Question: Can you have two circuits that can't be put on a handle tie feed a quad receptacle? For instance ckt #1 feeds the left duplex and circuit #8 feeds the right duplex.
No, you cannot have two circuits that aren't handle-tied feeding a quad receptacle (or any multi-outlet receptacle, including a regular duplex) in a residential setting.
Why this is a problem and violates code (in the US, referring to the NEC)
Multi-wire Branch Circuits (MWBC)
This situation describes a potential multi-wire branch circuit. An MWBC shares a neutral conductor between two hot conductors. Without a handle tie, both circuits could be fed from the same phase of a split-phase system, which would overload the neutral. Even if they are on different phases, it creates a hazard during maintenance.
210.4(B) Disconnecting Means
The NEC requires that where two or more ungrounded conductors of a multi-wire branch circuit supply devices or equipment on the same yoke (like a duplex receptacle, or a quad), they must be provided with a means to simultaneously disconnect them. This means a handle tie, a 2-pole breaker, or a similar device.
Shock Hazard
If someone is working on one half of the quad receptacle and thinks they've turned off the power to the whole thing, but only one breaker is off, they could still be exposed to live voltage from the other circuit. A handle tie ensures both circuits are de-energized when one is turned off.
Arc Fault Circuit Interrupter (AFCI) and Ground Fault Circuit Interrupter (GFCI) Considerations
Modern codes often require AFCI and GFCI protection on receptacles in many locations. If each half of the quad receptacle is fed from a different circuit, it becomes very difficult, if not impossible, to properly provide this protection.
Exceptions/Clarifications (that don't typically apply to residential situations)
Dedicated Circuits
If each half of the quad is a dedicated circuit for a specific piece of equipment that requires a dedicated circuit, and the instructions allow, and the power requirements are within parameters, it can be different. However, this is not typical for general-purpose receptacles in a house. Also, the receptacle would have to be clearly marked to show which specific equipment it serves.
In summary, for almost all residential cases, using two separate circuits (without a handle tie or a 2-pole breaker) to feed a quad receptacle is a code violation and a safety hazard. You must use a handle tie or 2-pole breaker.Best Practice
If you need more capacity at a location, the proper way to handle it is to:1.
Run a dedicated circuit
A single 20-amp circuit to the quad receptacle.2.
Run a Multi-Wire Branch Circuit with a handle tie
Using a 2-pole breaker and ensuring the receptacle is correctly wired for the MWBC. This provides two 15 or 20 amp circuits sharing a neutral (safely).3.
Run two separate circuits to two* separate duplex receptacles. The receptacles cannot share a yoke (i.e. they must be individual units).Consult with a qualified electrician to determine the best and safest solution for your specific needs. Flag for review