User: philly
Asked on: Wednesday, October 15, 2025 at 10:37 am EDT
Answered on: Wednesday, October 15, 2025 at 10:43 am EDT
Question: I'm involved in rebuild of a customer owned industrial sub that has a 13.2kV feeder from secondary of substation down to the plant's main incoming switchgear. Utility metering is on primary of substation transformer so everything from transformer down falls under NEC purview in my opinion.The 13.2kV feeder from the sub will be underground cable before it transitions to a new short overhead line to join an existing overhead (ASCR cable) line that is run into the existing facility.Am I correct in understanding that the NEC requires a separate EGC and thus my new OH line portion will need to have a ground wire (UG portion of cable will have an EGC run up to pole)? In these cases is the OH ground typically installed as a shield above ASCR phase conductors, or below it similar to a utility Distibution neutral?It also appears that the existing OH line going into the plant does not have any sort of separate EGC? This was a much older installation and at one point in time looks like system may have been LRG grounded (its solidly grounded now). Is there any sort of exception in NEC for older installations that did not have an EGC? Is there an approach to a situation like there where one does not exist for OH cables traversing several hundred yards before getting to facility?
You've hit on some important points and complexities. Let's break down the NEC requirements and best practices for this situation.
Your Understanding of NEC Applicability
You are correct. Because the utility metering is on the primary side of the substation transformer, everything on the secondary side (including the 13.2kV feeder to the plant) falls under the NEC. This includes the underground cable, the new overhead line, and the connection to the existing overhead line.
NEC and EGC Requirements for 13.2kV Systems
The NEC generally requires an equipment grounding conductor (EGC) to be run with the circuit conductors. Specifically: NEC 250.4(A)(5)
"Electrical equipment that is required to be connected to a system grounding electrode and is likely to become energized shall be connected in a manner that creates a low-impedance ground-fault current path that facilitates the operation of the overcurrent protective devices."
NEC 250.184(A)
"High-impedance grounded neutral systems shall not be used for portable equipment." (Since you mentioned it's now solidly grounded, this is relevant in ruling out high-impedance grounding as an option)
Article 399, Engineered Optimal Grounding. This section of the NEC is relatively new and could potentially be applicable to your installation. This is an alternative method to establish effective ground-fault current path for your electrical equipment.
Overhead EGC Placement
Shield Wire (Above the Phase Conductors)
This is more common on transmission lines (higher voltages, longer distances). It primarily serves as a lightning shield to intercept direct strikes and protect the phase conductors. While it can contribute to the ground fault current path, it's not typically sized or installed solely for that purpose on distribution feeders.
Underneath Phase Conductors (Distribution Neutral)
This is the more common configuration for distribution lines. While often referred to as the "neutral," it's actually a multi-function conductor. It serves as the neutral for single-phase loads, and it acts as the Equipment Grounding Conductor (EGC). It is directly bonded to ground at multiple points along the line.
NEC Compliance and EGC Concerns
Yes, the NEC generally requires an EGC with your 13.2kV feeder. However, there are nuances to how this is achieved and enforced at these voltages.Here's the breakdown for each section of your feeder, and some options:
Underground Cable
You are correct. Your new underground cable should have an EGC that is properly sized and terminated at both ends. The EGC needs to be brought up to the pole to connect to the overhead portion.
New Overhead Line Section
Since this is a new install section of overhead conductor, it will need an EGC installed with the phase conductors to remain code compliant. You have a few options:
Install a separate ground wire. Run a bare copper or aluminum conductor parallel to the phase conductors, ensuring it's bonded to the EGC at the transition point from the underground cable and connected to the switchgear grounding system. This is likely the most straightforward and compliant approach. Place this below the phase conductors similar to a utility distribution neutral. Install a grounding conductor separate from the overhead line. This would involve burying a conductor between the substation and facility. This can be a solid wire, but a ground grid or ground ring with ground rods may be required to lower impedance to ground, especially if there is a concern of short circuit faults. Shield Wire
While you could use a shield wire, it likely will not meet NEC requirements for fault current carrying capacity. It is also more expensive and difficult to install.
Existing Overhead Line (No EGC)
This is where it gets tricky.
"Grandfathering" / Existing Installations
The NEC generally doesn't require you to bring existing installations up to current code unless you are making significant modifications or expansions (NEC 90.4). The addition of the new underground cable and short overhead section could be considered a modification that triggers the need to address the entire feeder.
Safety and Mitigation
Even if not strictly required by the NEC to upgrade the entire existing overhead line, it's prudent to evaluate the safety implications and explore mitigation options:
Grounding Impedance
Carefully measure the impedance to ground of the existing overhead line and the equipment it serves. High impedance can lead to elevated touch potentials during ground faults.
Supplemental Grounding
Consider adding supplemental grounding electrodes (ground rods) at the base of poles along the existing overhead line, especially near the facility entrance. This can help lower the overall impedance to ground and improve safety.
Equipotential Bonding
At the facility entrance, ensure that all metallic structures (fences, pipes, building steel) are effectively bonded together to create an equipotential plane. This minimizes the risk of voltage differences during ground faults.
Ground Fault Protection
Install sensitive ground fault protection (e.g., ground fault relays) at the main switchgear to quickly detect and isolate ground faults. This is crucial, especially if the ground fault current path is not as robust as desired.
Consider Engineering Analysis
Engage a qualified electrical engineer to perform a detailed study of the grounding system. They can model the ground fault current distribution and identify areas of concern.
Addressing the Existing Overhead Line
Because the existing overhead line is an existing install, the best advice is to contact the local AHJ (Authority Having Jurisdiction) to discuss potential upgrades. This may allow you to perform an upgrade specific to the underground installation to the existing overhead without replacing the entire system.If the cost of replacing the entire overhead system is beyond budget, then perform due diligence by focusing on the following:
Documentation
Document the existing conditions thoroughly. Include photographs, measurements (impedance to ground, etc.), and a description of the grounding system.
Risk Assessment
Perform a formal risk assessment that considers the potential hazards associated with the existing grounding system and the proposed modifications.
Mitigation Plan
Develop a mitigation plan that outlines the steps you will take to improve safety, even if full compliance with the latest NEC isn't feasible.
AHJ Consultation
Discuss your findings and mitigation plan with the AHJ. Obtain their approval for your approach.
In summary
New Portions
The new underground cable and overhead line must comply with the NEC and have a properly sized EGC.2.
Existing Line
The existing overhead line is a more complex issue. Aim to improve safety through grounding enhancements, equipotential bonding, and ground fault protection. Consult with the AHJ and document everything.3.
Engineering is Key: This is a complex situation. Involving a qualified electrical engineer experienced in medium-voltage distribution and grounding is highly recommended. They can perform the necessary studies, recommend appropriate solutions, and ensure compliance with the NEC and other applicable standards.This information is for guidance only and should not be considered a substitute for professional engineering advice. Always consult with qualified professionals and the local AHJ before making any electrical modifications. Flag for review