Question: I have a scenario where we are replacing VAV with heaters. The existing wiring is #12AWG. The kw load of the new heaters went up to 5KW @ 277 = 18Amp FLA for the new heaters. We are replacing existing 20Amp breakers with 25Amp breakers to accommodate this upsized load.To save cost, are we able to utilize the existing #12AWG wire? I understand for loads under 100Amp to assume using the 60C ampacity table unless terminations are marked for 75C. The VAV has a label that says "Use wire suitable for at least 75C" that is not really stating the termination if rated for 75C. Has anyone ran into this? It is a lot of VAV units and could save a decent bit if existing #12AWG wire can be used vs installing new #10Awg to each new unit. Check the O&M and it does not state electrical termination temp ratings.The Sqaure D circuit breaker is rated for 75C so good on that end of the circuit.
Okay, let's break this down thoroughly and address the code implications. You're right to be concerned and carefully evaluate this.
The Core Problem: Overcurrent Protection and Conductor Ampacity
The fundamental issue is whether you can safely and legally increase the overcurrent protection (breaker size) on an existing #12 AWG circuit to accommodate a higher load. The answer is almost certainly no, based on the information you've provided.
Here's a detailed breakdown
Conductor Ampacity (#12 AWG)
#12 AWG copper wire, according to NEC Table 310.16 (using the 60°C column since you don't have a definitive 75°C termination rating), is typically rated for
20 amps. Even if you assumed 75°C, it's generally only rated for 25A, which is not enough ampacity for 18A heaters with a required 125% ampacity adjustment. Termination Temperature is Critical
You are correct. Even if the wire insulation is rated for 75°C or 90°C, the termination (the point where the wire connects to the breaker, heater, or other equipment) is what matters most. Unless you have documentation specifically stating that the terminations at both ends of the circuit are rated for 75°C, you must use the 60°C column. The vague label on the VAV saying "Use wire suitable for at least 75C" is not sufficient. It's merely telling the installer what the wire insulation must be capable of, not the termination rating. You've checked the Square D breaker is rated for 75C which is good, but you need to know about the heater terminations.
Important Note
The NEC specifically addresses this in
110.14(C)(1)
"Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both. Where equipment terminations are used with conductors rated for higher temperatures, the ampacity shall be determined from the lowest temperature rating of the equipment terminals, conductors, or devices."
This means that you CAN use the 90 degree ampacity for derating in situations where there are other conditions that affect the ampacity (like more than 3 current carrying conductors in a conduit, or high ambient temperatures). BUT, you can NEVER upsize the breaker based on the 90 degree ampacity if the termination point is only rated for 60 degrees.2. Overcurrent Protection (Breaker Size)
The fundamental principle of overcurrent protection is to protect the conductor from overheating and potential fire. The breaker's job is to trip before the wire's ampacity is exceeded. NEC 240.4(D) states (in summary) that you cannot use an overcurrent protection device rated higher than the ampacity of the conductors. (There are exceptions, but none apply here)
Increasing the breaker to 25 amps on a circuit wired with #12 AWG (rated for 20 amps in most cases) is a violation of the NEC and creates a significant fire hazard.3. Heater Load Calculation and Overcurrent Protection
5kW at 277V = 18 amps. NEC requires you to calculate the heater load at 125% (NEC 424.3(B)). 18 amps x 1.25 = 22.5 amps. Even if you had 75°C terminations, and rated the #12 AWG at 25 amps, you still can't use a 25-amp breaker. NEC 240.4(B) states that you can use the next higher standard overcurrent device rating if the calculated load does not match the standard breaker size. The next higher standard breaker size from 22.5 amps is a 25 amp breaker. BUT, you cannot exceed the ampacity of the conductors.
4.
Code Violations and Safety
NEC Article 240.4
Specifically prohibits overcurrent protection exceeding the conductor's ampacity.
NEC Article 110.3(B)
Requires equipment to be installed according to its listing and labeling. If the heater requires a specific wire gauge and overcurrent protection, you must follow it.
Fire Hazard
Overloading the #12 AWG wire will cause it to overheat, potentially melting the insulation and causing a short circuit, resulting in a fire.
What You Need to Do
Verify Heater Termination Ratings
This is your FIRST and most important step. Contact the heater manufacturer and get documented proof of the termination temperature rating. The heater's installation instructions must* specify the wire gauge and overcurrent protection requirements. If the heater says 75C or 90C rating then you can consider 2.2.
Verify the breaker termination temp rating. Typically circuit breakers terminations are rated for 75C.3. Replace the Wiring
If the heater is rated at 75C and the Breaker is rated at 75C, then the weak spot could be the wire ampacity itself. You must replace the #12 AWG with #10 AWG copper wire (rated for 30 amps at 60°C or 35 amps at 75°C) and change to a 25 amp breaker. This is the safest and most compliant solution.4.
Document Everything
Keep all documentation related to the heater specifications, termination ratings, and any calculations performed.
Cost Considerations
While replacing the wiring is a significant cost, the risk of a fire and the liability associated with code violations far outweigh the savings. It's crucial to prioritize safety and compliance with the NEC.
In summary, upgrading the breaker size without upgrading the wiring is not a viable or safe solution. You must replace the wiring with the appropriate gauge wire to handle the increased load and maintain compliance with the NEC. Flag for review