Question: We have multiple parallel runs of #350 MCM / 1C mineral insulated (MI) cables. The longest run without a field splice will be around 310 feet. We will use 24"/36" pulleys (roller/sheave) for every turn in the path of the cable. Each of the pullies will be mounted appropriately at the adjacent structure. We have done many of these kind of jobs in the past. This peculiar job, the client is asking us (EC) to provide (point force) calculations for the mounting location of the pulley, and if the structure there would be able to withstand it or not. We assume it is the sidewall pressure for each of the turning points. In normal scenarios where we use THHN/XHHW, etc. cable in conduit, we use SIMpull (Southwire) cable pull calculation sheets. Southwire does not make solid copper MI-cables. nVent is the only one who makes it and they do not have pulling calculator. We could not find any other information we could use for calculation for MI-cables. Or we are not sure how to use it for MI-cable calculations.#350MCM/1C cable is 1.625 lbs./ft., O.D. 0.834", Solid Copper, manufacturer recommended max pulling pressure 3,000 lbs, not to exceed 8,800 lbs.Any help is appreciated. Please let me know if you need any more information. Thank you.
Okay, this is a classic problem with specialty cable installations. You're being asked to provide engineering validation for your installation methods, which is a good practice, especially with heavier and less flexible cable like MI. Let's break down how to approach this force calculation.
Understanding Sidewall Pressure (SWP) and Point Force at the Pulley
Sidewall pressure, while relevant for conduit bending calculations, isn't directly what you need to calculate the point force on the pulley's mounting structure. Think of it this way: Sidewall Pressure
This is the force exerted by the cable per unit length against the inside of a bend in a conduit. It's important for conduit integrity.
Point Force on Pulley
This is the total force exerted at a single point on the pulley and, therefore, on its mounting structure. This force is the vector sum of the tension in the cable on either side of the pulley.
Calculating the Point Force on the Pulley
Here's the general approach:1. Estimate Maximum Cable Tension (T)
This is the most critical factor. You need to estimate the maximum tension that will be applied to the cable during the pull. You have two limits:
Manufacturer's Recommended Max Pulling Pressure
3,000 lbs (this is your working limit).
Not to Exceed Limit
8,800 lbs (this is your absolute maximum).You should aim to stay well below the 3,000 lb recommended limit to provide a safety factor and account for any unforeseen issues during the pull. Consider that a 310-foot pull, even with pulleys, is going to generate significant friction. A good starting estimate for maximum pulling tension (T) would be around
2,000 lbs. It's prudent to aim for this value until you can refine it with a more precise friction estimate.2. Determine the Angle (θ)
This is the angle of the cable deflection around the pulley. For example, if the cable makes a 90-degree turn around the pulley, θ = 90 degrees. If the cable goes straight (no turn) around the pulley, θ = 0 degrees.3.
Calculate the Point Force (F)
The point force on the pulley is determined by the following formula:
F = 2 T sin(θ / 2)
Where: F = Point Force on Pulley (lbs) T = Estimated Maximum Cable Tension (lbs) θ = Angle of Cable Deflection (degrees)4. Calculate Safety Factor
Since the cable is heavy and the run is long, a safety factor of 2 or more is recommended. Multiply the Force calculated above by 2. This will ensure that the mounting structure is strong enough to withstand the force.
Example Calculation
Let's assume: T = 2,000 lbs (estimated max tension) θ = 90 degrees (right angle turn)Then: F = 2 2,000 lbs sin(90°/2) F = 4,000 lbs sin(45°) F = 4,000 lbs 0.707 F = 2,828 lbs. With Safety factor: 2828 x 2 = 5,656 lbs
Therefore, the point force on the pulley's mounting structure for a 90-degree turn, with an estimated maximum tension of 2,000 lbs and a safety factor of 2, would be approximately 5,656 lbs.
Key Considerations and Refinements Friction
This is the biggest uncertainty. The longer the pull, the more friction matters. Here are ways to estimate (or at least consider) friction:
Past Experience
You mentioned having done similar jobs. Review the pulling tensions experienced in those projects. Did you measure them? Can you extrapolate?
Lubrication
What type of lubricant will you use on the cable? A good lubricant will significantly reduce friction. Check the lubricant's specifications.
Pulley Friction
Assume a small coefficient of friction for the pulley itself (e.g., 0.05 to 0.1). This contributes to the overall tension.
Vertical vs. Horizontal Runs
Vertical runs will have significantly higher tension due to the weight of the cable hanging vertically.
Pulley Size
While 24"/36" pulleys are good for minimizing cable bending stress, they don't directly affect the point force calculation as long as the cable smoothly transitions around the pulley.
Dynamic Loading
The calculations above assume a static load. During the pull, there will be dynamic loading (jerks, stops, starts). This is another reason to use a good safety factor.
Worst-Case Scenarios
Consider the turn that will experience the highest tension. This is likely the turn closest to the pulling winch.
Documentation
Document all your assumptions, calculations, and safety factors clearly. This is what the client is paying for.
How to Present This to Your Client1. State Your Assumptions
Be upfront about your assumptions, especially regarding the estimated maximum cable tension and friction. Explain the rationale behind your choices.2.
Show Your Calculations
Present the calculations clearly and concisely.3.
Provide the Point Force
Clearly state the calculated point force for each turning point (or the worst-case turning point) including the safety factor.4.
Highlight Structural Assessment
Emphasize that it's the client's responsibility to have their structural engineer verify that the mounting locations can withstand the calculated point forces with the appropriate safety factor. You are providing the load, not the structural analysis.5.
Contingency Plan
Suggest that you be present during the initial pull to monitor cable tension and make adjustments if necessary. This demonstrates a commitment to a successful and safe installation.
In Summary
While you can't find a dedicated MI cable pulling calculator, you can use the principles of force vector analysis and friction estimation to calculate the point forces on the pulley mounting structures. Accurate tension estimation, a generous safety factor, and clear communication with your client are key to a successful project. Flag for review