Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 75C ampacity rating for MV-90 cables

User: SR_100, Location: Canada

Asked on: Wednesday, October 15, 2025 at 5:45 pm EDT
Answered on: Wednesday, October 15, 2025 at 6:23 pm EDT

Question: Hello, in the Canadian Electrical Code there is rule 28-104(1)(c) which requires motor feeder cables to be sized based on 75C ampacity values. Is there an equivalent rule in the NEC? Is there a derating factor to apply to the values in the 315.60(C) tables to get a 75 C ampacity value? For example, the corresponding table for shielded 5 kV cables in the Canadian code uses a 0.886 factor to convert from 90 C to 75 C values.Thanks.

You're asking about a common point of confusion when comparing the CEC and the NEC. Here's a breakdown of the NEC rules and how they relate to your question about 75°C ampacities for motor feeders

NEC Requirement for Motor Feeder Ampacity

The NEC does not explicitly mandate using 75°C ampacity values solely for motor feeders in the same direct way the CEC 28-104(1)(c) does. However, the NEC's approach accomplishes a similar result through a combination of requirements:1. NEC 430.22(A) Motor feeder conductor ampacity. Conductors supplying a single motor shall have an ampacity not less than 125% of the motor's full-load current rating as determined by 430.6(A)(1).
2. NEC 110.14(C) Termination Temperature Limitations

This is the key section. It states: "(1) Equipment for use at 100 amperes or less, and marked for use with 14 AWG through 1 AWG conductors, shall be limited to use with conductors rated 60°C (140°F)." "(2) Equipment for use at over 100 amperes, and marked for use with 14 AWG through 1 AWG conductors, shall be permitted to be used with conductors rated higher than 60°C (140°F), provided the ampacity of such conductors is determined based on the 60°C (140°F) ampacity of the conductor size used." "(3) Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both."

How this effectively requires 75°C or lower ampacities in many cases



Termination Temperature Ratings Drive the Requirement

The vast majority of motor control centers (MCCs), disconnect switches, circuit breakers, and contactors are marked with termination temperature ratings. The most common rating is 75°C. Some (especially older or lower-cost equipment) are only rated for 60°C terminations.

You
must use the lowest temperature rating

You have to use the
lowest temperature rating of any of the termination points in the circuit (breaker, disconnect, motor terminals, etc.).

The Result

If any of the termination points are rated for 75°C (which is very common), you must use the 75°C ampacity column from Table 310.16 (or the ampacity based on engineering calculations). If any termination point is 60°C, you must use the 60°C ampacity.

Therefore, while the NEC doesn't explicitly say "use 75°C for motor feeders," the practical effect is that, due to termination temperature ratings, 75°C ampacities are almost always required, especially for larger motors.
Specifically Addressing your Questions



Equivalent to CEC 28-104(1)(c)?
No direct rule that mirrors it exactly. However, 110.14(C) combined with the nature of termination ratings on equipment serves the same purpose. Derating factor for 315.60(C) tables? No. Table 315.60(C) is for cables installed in cable trays, and specifically references conductor's temperature rating. However, just like conductors listed in Table 310.16, the ampacity in Table 315.60(C) could be limited by 110.14(C) due to the termination points. Important: You wouldn't "derate" from the 90°C column to a 75°C value. Instead, you would select your conductor size based on the 75°C ampacity directly from Table 310.16 (or use the 60°C column if that's the limitation). If Table 315.60(C) is used, then you would select your conductor based on the table's ampacity.

In summary: The NEC achieves a similar goal as the CEC's explicit 75°C rule for motor feeders, but through a different mechanism centered on termination temperature limitations. You
always need to consider the temperature rating of your terminations and use the appropriate ampacity table column based on the lowest* rated termination in the circuit. Flag for review

Previous Question Next Question