Topic: Voltage drop

User: Maine Bassin', Location: Boston

Asked on: Wednesday, October 15, 2025 at 8:18 pm EDT
Answered on: Wednesday, October 15, 2025 at 8:35 pm EDT

Question: I need to run an underground service from a transformer pad to an installed hand hole. The distance is about 275' , my calculations put me at 600kcmil aluminum, which is huge, but does that sound right . I would like to use the smallest wire possible ,obviously. Thanks

Okay, let's break down the factors involved in sizing underground aluminum conductors and see if 600 kcmil sounds reasonable and how we might optimize. We need to consider:1. Load (Amps)

What's the actual load you're serving? This is the most critical factor. If you can provide the exact amperage of the load, we can be much more precise. This load needs to be on the name plate.2.

Voltage

What is the supply Voltage? 480, 240, 120v3.

Voltage Drop

Acceptable voltage drop is crucial for equipment performance and code compliance. Typically, a maximum of 3% voltage drop is recommended for feeders and 5% overall (feeder + branch circuit). What is the requirement?4.

Installation Method

Direct burial? In conduit? This affects the ampacity.5.

Soil Conditions & Ambient Temperature

These affect the ampacity of the cable.6.

Code Requirements (NEC)

The National Electrical Code (NEC) has tables and requirements for ampacity and voltage drop.7.

Number of Conductors in a raceway/ or direct burial

This affects the ampacity.

Here's a breakdown of why 600 kcmil might be necessary (or not)



Long Distance

At 275 feet, voltage drop becomes a significant factor. Smaller wires will result in a greater percentage of voltage drop.


High Current

If you're carrying a substantial current (hundreds of amps), you'll need larger conductors to handle the ampacity and minimize voltage drop.

Here's a step-by-step approach to verify and potentially reduce the conductor size


Determine the Actual Load (Amps)

This is absolutely the starting point. What equipment are you powering? What is the FLA (Full Load Amps) of that equipment? If it's a panelboard, what's the total connected load (after demand factors)? If it's a motor, what's the motor's HP and voltage? Provide this information! Without it, we're just guessing.2.

Calculate the Minimum Ampacity Required (NEC 310.15)

The NEC requires you to size conductors to carry at least 125% of the continuous load. Continuous load is defined as a load that operates for 3 hours or more. If your load is 100 amps and is continuous, you'll need to size the conductor for at least 125 amps.3.

Choose an Insulation Type

Common underground insulation types include THHN/THWN-2 (in conduit), USE-2, and RHW-2. The insulation temperature rating impacts the ampacity (90°C is generally desirable for its higher ampacity). Most underground installations require wet-rated conductors (THWN-2, USE-2, RHW-2).4.

Determine Installation Method (NEC Table 310.15(B)(16) & 310.15(B)(3))

Direct burial requires different ampacity ratings than conductors in conduit. Also how many other conductors are in the same trench or conduit. This table provides ampacity values for different wire sizes and insulation types, assuming specific conditions (e.g., 3 current-carrying conductors in a raceway or cable).5.

Apply Ampacity Correction Factors (NEC 310.15(B)(2) & 310.15(B)(3))

If the ambient temperature is higher than 30°C (86°F), you need to derate the ampacity. If you have more than three current-carrying conductors in a raceway or cable, you need to apply a derating factor (NEC Table 310.15(C)(1)).
6.


Calculate Voltage Drop (NEC Chapter 9, Informative Annex C)

Use a voltage drop calculator or the formulas in Annex C of the NEC. The NEC recommends a maximum of 3% voltage drop for feeders. For a 275-foot run, voltage drop is critical. The formula for voltage drop (simplified, for single-phase or balanced three-phase) is: VD = (2 K I D) / CM (Single Phase) VD = (1.732 K I D) / CM (Three Phase) Where: VD = Voltage Drop (Volts) K = Resistance factor of conductor material (Aluminum is approx. 17 ohms per mil-foot) I = Current (Amps) D = Distance (One-way, in feet) CM = Circular Mils (Cross-sectional area of the conductor)7.

Choose the Larger Wire Size

Select the conductor size that meets both the ampacity requirements (after derating) and the voltage drop requirements.

Possible Ways to Reduce Conductor Size (Consider these
after accurately determining the load)



Increase the Voltage

If possible, increasing the voltage reduces the current required for the same power, which allows for smaller conductors. This isn't always feasible but is the most effective way.

Minimize the Load

Are you overestimating the load? Are you including non-essential loads?


Optimize the Installation

Ensure proper burial depth and backfill to improve heat dissipation.

Parallel Conductors (NEC 310.10(H))

In some cases, you can run two or more smaller conductors in parallel instead of one very large conductor. This requires careful consideration of termination and equal length conductors. This may require larger conduit.

Example Scenario (Illustrative -
You MUST provide your actual load information)

Let's say you have a 480V, 3-phase load that draws 200 amps continuously. You're running it in conduit underground, and the ambient temperature is 35°C.1.

Minimum Ampacity

200 amps
1.25 = 250 amps.
2.


Choose Insulation

USE-2 (90°C rated)3.

NEC Table 310.15(B)(16)

A 250 kcmil aluminum conductor (USE-2) is rated for 255 amps at 90°C.4.

Temperature Correction (NEC 310.15(B)(2))

For 35°C ambient, the correction factor is approximately 0.91 (check the table). 255 amps 0.91 = 232 amps. This is not enough, so we need to move up in wire size. A 300 kcmil aluminum conductor (USE-2) is rated for 280 amps at 90°C. 280 amps 0.91 = 255 amps after derating.
5.


Voltage Drop Calculation

Use the formula from above. Assume that the voltage drop limit is 3% (480v 0.03 = 14.4 volts). Then use the equation above and solve for CM (Circular Mils)CM= (1.732 K I D) / VDCM= (1.732 17 200 275) / 14.4CM = 1,106,885 / 14.4CM = 76,867This means that you need a 300 kcmil (300,000 CM) to be able to carry the required load based on ampacity, you would need to check the voltage drop, but based on this calculation, you would need about a 800 kcmil to be able to meet the voltage drop requirements.

Important Considerations



Consult a Qualified Electrician or Engineer

This is critical. These calculations are simplified for illustrative purposes. A professional can perform accurate load calculations, consider all applicable codes, and ensure a safe and compliant installation. Do not rely solely on this information for your actual installation.



Permitting and Inspection

Most jurisdictions require permits and inspections for electrical work.

In summary, provide the load amperage, voltage, and desired voltage drop, and we can give you a more specific recommendation. But based on a long run and an unknown load, 600 kcmil aluminum is plausible but could potentially be reduced with more accurate information.