Question: They’ve installed a 16” wire gutter below a group of 5, 480V disconnect switches that extends approximately 10” begin the front of the switches which is violation of working access NEC 110.26. Is there any “work-around” this so they don’t have to tear it out ?Enviado desde mi iPhone utilizando Tapatalk
You're right, a 16" wireway protruding 10" out from the front of 480V disconnects is a major working space violation. NEC 110.26(A) specifies minimum working clearances around electrical equipment operating at 600 volts, nominal, or less. Here's a breakdown of potential workarounds and considerations, keeping safety the top priority
Understanding the Violation:
Hazard
Obstructions in the working space create a significant arc-flash and electrocution hazard. Technicians need clear access for safe operation and maintenance. Restricted movement hinders quick egress in an emergency.
NEC 110.26(A)(1)
Requires clear working space dimensions for equipment operating at 600V or less. The exact depth requirement depends on the voltage to ground and conditions. At 480V (likely 277V to ground), you'll need to consult Table 110.26(A)(1) in the NEC. The minimum depth is often 3 feet, and can be more depending on if there's exposed live parts on the opposite side, or an insulated wall (see conditions 1, 2, and 3 in the table). The 10" protrusion likely eats significantly into this required space.
Potential "Workarounds" (Listed in Order of Preference - Least to Most Desirable)
Relocate the Disconnect Switches
Best Option
If feasible, the ideal solution is to move the disconnect switches to a new location that provides the required working clearances without needing the wireway in front of them. This eliminates the problem entirely.2.
Replace the Wireway with a Shallower Solution
Reduce Depth
Can the 16" wireway be replaced with a narrower one (e.g., 6" or 8") that provides the necessary wiring capacity while significantly reducing the encroachment into the working space? The key is to meet NEC fill requirements for wireways (376.22) and ampacity derating if applicable.
Conduit Runs
Instead of a continuous wireway, could individual conduit runs from each disconnect be used? This might allow for a tighter overall profile.3.
Recess the Disconnects (If Possible)
Consider Wall Modification
Could the disconnect switches be recessed into the wall to gain some of the working space back? This might involve structural modifications and would depend on the wall type and depth available. This is likely a costly and difficult option.4.
Warning Signage & Barriers (Least Desirable - Likely Not Acceptable Alone)
Not a Real Solution
While NEC 110.26(C)(2) allows for dedicated equipment space, this typically applies to spaces above or adjacent to the equipment, not directly in front of it, blocking access.
Supplemental Approach Only
As a supplement to another solution (e.g., after reducing the wireway depth as much as possible), very prominent warning signs could be used. These signs must clearly and unequivocally state the hazard and any specific precautions required.
Physical Barriers (Temporary)
Consider installing temporary barriers (e.g., stanchions with caution tape) during maintenance to prevent inadvertent contact with the wireway. This is only a temporary solution and not a replacement for proper clearances.
Important Considerations
Local Codes and Inspector
Consult with the local electrical inspector before implementing any changes. They have the final say on what is acceptable. Show them your proposed solutions.
Documentation
Thoroughly document any changes made, including drawings, calculations, and photos.
Safety First
Do not compromise safety to avoid rework. The cost of an injury or fatality far outweighs the cost of correcting the violation.
Engineering Review
Have a qualified electrical engineer review any proposed modifications, especially if it involves changing wireway sizes, conduit runs, or equipment locations.
Maintenance Accessibility
Ensure that the disconnects can be easily accessed for maintenance and repair.
Why Some "Solutions" Are Unlikely to Work
Painting Yellow Stripes
Painting the wireway won't change the physical obstruction it presents.
Relying on "Qualified Persons Only"
Even qualified persons need adequate working space for safety. The presence of the wireway still poses a hazard.
In summary, the best approach is to either relocate the disconnects or reduce the size/depth of the wireway. Warning signs and barriers should only be considered as a supplementary measure after other options have been exhausted, and only with the approval of the local electrical inspector. Flag for review