Topic: Feeder Neutral sizing

User: Hvactrician, Location: Walworth Cty Wisconsin

Asked on: Thursday, October 16, 2025 at 12:01 pm EDT
Answered on: Thursday, October 16, 2025 at 12:02 pm EDT

Question: I currently have a building that is being fed with a 400 amp 480/277 service. We are running new feeders from a different service in a connected buildingto the building to allow for excavation and construction. We are running a four wire circuit of 480/277 and changing the fuses to 200 amp. The only thing that the service is feeding is a 277 V lighting panel with balanced lighting loads and two 480v -120/208 transformers. our current carrying conductors are 4/0 what size do I need for my neutral?

Okay, let's break down the neutral conductor sizing for your temporary 200A, 480/277V feeder to the existing building.

Understanding the Requirements

The NEC (National Electrical Code) dictates the sizing of neutral conductors. The basic principle is that the neutral conductor must be large enough to carry the maximum possible unbalanced load. However, there are specific rules and allowances that can reduce the required size in certain situations, particularly for 4-wire, wye-connected systems.

Your Specific Situation 480/277V, 4-Wire Wye System

This is a key point. In a 4-wire wye system, the neutral carries the unbalanced load between the phases.


200A Feeder

This is your maximum ampacity for the feeder.

Balanced Lighting Load

This is critical. You stated that you have a balanced lighting load on your 277V panel. With a perfectly balanced lighting load, theoretically, no current would flow on the neutral.


480V-120/208V Transformers

These are also important to consider. If these transformers are mainly supplying linear loads and are balanced (which is often the case), the contribution of harmonic currents (especially the 3rd harmonic) to the neutral current should be minimal.

NEC Guidelines
1. NEC 220.61 (Neutral Conductor) This Section of the NEC provides the requirements for the Sizing of the neutral conductors.2. NEC 220.61(C)(1) - Feeder or Service Neutral Load (1) A feeder or service supplying household cooking appliances shall have an additional demand factor of 70 percent applied to the amount of the unbalanced load. This does not apply to your situation. (2) For feeders or services supplying electric ranges, wall-mounted ovens, counter-mounted cooking units, and electric dryers as specified in Table 220.55, the maximum unbalanced load shall be assumed to be 70 percent of the load on the ungrounded conductors. This does not apply to your situation. (3) For 3-wire dc or single-phase ac; 4-wire, 3-phase; or 5-wire, 3-phase systems, a further demand factor of 70 percent shall be permitted for that portion of the unbalanced load in excess of 200 amperes. This provision would apply if the unbalanced load exceeds 200A.Calculations and Considerations Calculate the Expected Unbalanced Load

This is the most important step. Even with balanced lighting, there will always be some imbalance. The transformers' loading will also contribute to the imbalance. You can't assume a perfectly balanced load. The easiest way to measure the load is to use a clamp meter on your existing neutral conductor.

Apply Demand Factors (if applicable)

You may be able to apply a demand factor of 70% for that portion of the neutral load over 200A as mentioned in section 220.61(C)(3).


Minimum Neutral Size

The NEC also has minimum sizes for neutral conductors, typically based on the size of the phase conductors. Because the system is 480/277, the neutral would be able to be sized smaller than the phase conductors.

Based on the information given, here is my professional opinion

Given that you're using 4/0 AWG for the phase conductors, the minimum size you'd likely be allowed, per code, is

#2 AWG copper.
Since you stated that the loads are balanced, you can use #2 AWG copper. However, since the run is temporary, using the existing 4/0 AWG conductor you are using for your phases may be more cost effective.

Important Notes and Recommendations



Harmonic Currents

While you mentioned the loads being mostly linear, if you have any significant non-linear loads (e.g., some types of electronic ballasts, variable frequency drives, etc.), the neutral conductor can carry a substantial amount of harmonic current (especially the 3rd harmonic, which adds arithmetically in the neutral of a 3-phase system). If you suspect significant harmonic content, you MUST upsize the neutral conductor and consider using an oversized neutral reactor.


Local Codes and AHJ (Authority Having Jurisdiction)

Always check with your local electrical inspector (AHJ) for any specific requirements or interpretations of the NEC that may apply in your area. They have the final say on what is acceptable.

Voltage Drop

Consider voltage drop on the neutral, especially if the feeder run is long. An undersized neutral can exacerbate voltage drop issues.


Future Expansion

If there's any possibility of future load growth or changes in load characteristics (e.g., adding more non-linear loads), it's always wise to upsize the neutral conductor to accommodate those changes.

Disclaimer:
I am an AI chatbot and cannot provide legally binding electrical advice. This information is for general guidance only. A qualified and licensed electrical engineer or electrician should perform the actual calculations and design for your electrical system to ensure safety and code compliance. Flag for review