Question: What is the size of a motor disconnect switch based off of? How would one calculate? Is it the breaker size feeding it?
The size of a motor disconnect switch is based on the horsepower (HP) rating of the motor it's disconnecting, and sometimes, the motor's full-load current (FLC). It is not simply based on the breaker size feeding it, although the breaker and disconnect are related.Here's a breakdown of how to determine the appropriate size
1. Motor Horsepower Rating (Most Common):
NEC (National Electrical Code) Table 430.251(A) or 430.251(B)
These tables list the minimum disconnect switch horsepower rating required based on the motor's horsepower. The tables are further divided based on voltage. Select the correct table (430.251(A) for single-phase motors, 430.251(B) for three-phase motors).
How to use the table
Locate the motor's HP rating in the table. The corresponding value in the "Maximum Horsepower Rating" column indicates the smallest HP-rated disconnect switch that can be used. You can use a disconnect with a higher HP rating, but never lower.
Example
A 5 HP, 230V, three-phase motor needs a disconnect rated for at least 5 HP.
Important Considerations
Dual-Element (Time-Delay) Fuses
If the disconnect switch is also designed to hold fuses, the horsepower rating is particularly important. The fuse size is determined separately (see below), but the disconnect must be rated for the motor's HP and voltage.
Manufacturer's Specifications
Always consult the disconnect switch manufacturer's specifications. They may have additional limitations or requirements.
2. Full-Load Current (FLC) Rating (Less Common, But Important)
When to use FLC
While horsepower rating is the primary method, the disconnect switch must also be rated to handle the motor's full-load current. This is particularly important for larger motors or when the disconnect is also used as a service switch.
NEC Table 430.248 or 430.250
These tables provide the Full-Load Current (FLC) for motors.
Calculate
The disconnect switch's ampere rating must be at least 115% of the motor's FLC. `Disconnect Ampere Rating >= 1.15 Motor FLC` If the FLC is not on the motor's nameplate then you must refer to the NEC table.
Example
A motor has an FLC of 20 amps. The disconnect switch must have an ampere rating of at least 23 amps (1.15 20).
3. Breaker Size (Related, but not the primary factor)
The breaker protects the motor circuit against overloads and short circuits. The size of the breaker feeding the motor is calculated based on the motor's FLC and the type of motor and its starting characteristics.
NEC 430.52
This section covers motor overload protection. It dictates how to determine the proper breaker or fuse size. This is often much larger than the motor's FLC to allow for inrush current during motor starting.
Relationship
The disconnect switch MUST be rated to handle the potential fault current that the breaker can deliver. If the breaker is very large (due to motor starting requirements), you may need a disconnect switch with a higher short-circuit current rating (SCCR) than would be dictated solely by the motor HP or FLC.
In Summary: Calculation Steps1. Determine the Motor's Horsepower (HP) and Voltage. This is found on the motor's nameplate.2. Determine the Motor's Full-Load Current (FLC). Look for the FLC on the motor's nameplate. If it's not there, use NEC Table 430.248 (single-phase) or 430.250 (three-phase).
3. Select the Disconnect Switch Horsepower Rating
Use NEC Table 430.251(A) or 430.251(B) to find the minimum HP rating of the disconnect switch based on the motor's HP and voltage.4.
Calculate Minimum Disconnect Ampere Rating (FLC)
Multiply the motor's FLC by 1.15 (115%). This gives you the minimum ampere rating the disconnect switch must be able to handle.5.
Compare Ratings
Choose a disconnect switch that meets both the horsepower rating from Step 3 and the ampere rating from Step 4. The higher of the two ratings will govern your selection.
6.
Consider SCCR
Ensure the disconnect switch's Short-Circuit Current Rating (SCCR) is sufficient for the available fault current at the installation location. This might require a disconnect with a higher ampere rating, or one specifically listed with suitable overcurrent protection.7.
Verify with Manufacturer's Specifications
Always check the manufacturer's specifications for the chosen disconnect switch to ensure it meets all requirements for the specific application.
Important Notes
Article 430 of the NEC
This article is the definitive resource for motor circuits. You should consult it directly for specific requirements and exceptions.
Local Codes
Be aware of any local electrical codes or regulations that may have additional requirements.
Qualified Electrician
Electrical work can be dangerous. These calculations are for informational purposes only and should not be a substitute for the advice of a qualified electrician. A qualified electrician can properly assess the installation and select the appropriate disconnect switch.
Example
Let's say you have a 10 HP, 460V, three-phase motor with a nameplate FLC of 14 amps.1. HP and Voltage
10 HP, 460V, three-phase.2.
FLC
14 amps.3.
Disconnect HP Rating (NEC 430.251(B))
Table indicates a minimum 10 HP disconnect.4.
Disconnect Ampere Rating
14 amps 1.15 = 16.1 amps. Therefore, a disconnect capable of handling at least 16.1 amps is needed.
5.
Comparison
You need a disconnect rated for at least* 10 HP and 16.1 amps. You would select a disconnect that meets or exceeds both of these ratings. It might be a 10 HP disconnect that is rated for at least 30 amps, for example.
6.
SCCR: You must also make sure that the disconnect you choose has an adequate SCCR for your situation.This is a simplified example. Always consult the NEC and a qualified electrician for accurate and safe installations. Flag for review