User: Alwayslearningelec, Location: NJ
Asked on: Friday, October 17, 2025 at 8:04 am EDT
Answered on: Friday, October 17, 2025 at 8:05 am EDT
Question: Sorry for all the questions. So the 6P disconnect switch I asked about earlier makes sense as you can see the (6) #6's.1. If I have to replace fuses in this MCC there would be SIX fuses?2. How would I determine the size of the fuse? The disconnect switches at the units are 60A but I also see the Amps and MCA below for those same units. Assuming fuse ion MCC needs to be at least 60A?
No worries about the questions! It's good to be thorough, especially with electrical work. Let's break down the fuse situation in your MCC
1. Yes, you would have SIX fuses.
Since you saw six #6 wires going to the disconnect, that tells us each unit is wired for 3-phase power. 3-phase power requires three conductors per phase, so 2 Phases would require 6 fuses (3 fuses per phase).2. Determining Fuse Size
This is where it gets crucial to be precise. Never assume the fuse size based solely on the disconnect switch size. Here's how to determine the correct fuse size:
Find the Unit's Nameplate
The most reliable source of information is the equipment nameplate. Look for the following on the nameplate of each unit:
Minimum Circuit Ampacity (MCA)
This is the minimum ampacity the conductors feeding the unit need to have.
Maximum Overcurrent Protection (MOCP)
This is the maximum size fuse or circuit breaker allowed for that unit.
Rated Load Amps (RLA) or Full Load Amps (FLA)
The expected current draw of the unit under normal operation.
Important Considerations Based on Nameplate Information
Fuse Size CANNOT Exceed MOCP
The fuse size must be equal to or less than the Maximum Overcurrent Protection (MOCP) rating on the nameplate. This is a hard limit.
Fuse Size MUST Be Greater Than MCA
The fuse size must be equal to or greater than the Minimum Circuit Ampacity (MCA) rating on the nameplate.
Inrush Current
Some equipment (especially motors or equipment with large compressors) have a very high inrush current when starting. Time-delay fuses (like "dual-element" or "time-delay" fuses) are often used to handle these inrush currents without nuisance tripping. The equipment nameplate or the manufacturer's documentation will often specify if time-delay fuses are required.
Example Scenario
Let's say the nameplate on one of your units says: MCA = 45 Amps MOCP = 60 Amps RLA = 40 AmpsIn this case, you could use a 50A or 60A fuse. Always prefer the lowest rating you can use to provide proper protection.
How The 60A Disconnect Factors In
The 60A disconnect switch size tells you that the disconnect itself is rated to handle up to 60 Amps. This doesn't mean the fuse must be 60 Amps. If the MOCP is lower than 60A, you MUST use the lower value for the fuse.
Steps to Replace Fuses Safely & Correctly
De-energize
Completely de-energize the disconnect switch feeding the fuses you're replacing. Use a meter to verify that there is NO VOLTAGE present before touching anything. Lockout/Tagout procedures are essential.2.
Identify Correct Fuse Type
Look at the existing fuses (if they're intact) and note:
Voltage Rating
Make sure the replacement fuses have a voltage rating equal to or higher than the system voltage.
Ampere Rating
This is the most important - follow the nameplate information as described above.
Type
Is it a standard fuse, a time-delay fuse, or a special type? Make sure you replace it with the same type. Look at the label on the fuse itself. Fuses have markings such as "FRN" "KTK" and other markings. These markings are critical.3.
Replace Fuses
Use insulated fuse pullers or other appropriate tools to remove and replace the fuses.4.
Test
After replacing the fuses, close the disconnect switch and verify that the unit is operating correctly.
Important Warnings
Working with electricity is dangerous. If you are not a qualified electrician, do not attempt to replace the fuses yourself. Call a qualified professional. Never bypass or use a fuse with a higher amperage rating than the MOCP. This is a fire hazard and could seriously damage the equipment. Consult a qualified electrician if you have any doubts or questions.
In Summary:1. Yes, you will likely have six fuses in the MCC.
2. Determine the correct fuse size using the unit's nameplate (MOCP and MCA). The disconnect switch size is just a maximum rating; the fuse size might be smaller.3. Replace fuses with the exact same type and amperage rating.Safety first! Let me know if you have any more questions. Flag for review