User: marmathsen, Location: Seattle, Washington ...ish
Asked on: Friday, October 17, 2025 at 2:01 pm EDT
Answered on: Friday, October 17, 2025 at 2:02 pm EDT
Question: I have a small back yard ADU project that was finished a few months ago. It has a new 200A service that shares an overhead drop from the utility that feeds both the main house (200A) and the ADU (200A).They have had issues with the heat pump circuit tripping about once per week on Sunday night/Monday morning.As a first attempt we swapped out the GFCI breaker (HOM230GFI). The install instructions require GFCI protection and no one is willing to OK installing a standard breaker.We also setup new (temporary) wiring from the panel all the way to the unit including a new fused disconnect.The equipment rep for Mitzubishi came out and logged the heat pump during operations and stated""you have installed a fresh breaker and a new circuit. And it all appears to be more than sufficient to handle this load.The equipment has been thoroughly tested and has no shorts. I ran the system through an entire test mode while testing inrush, average and maximum amp draw. Inrush was 1.6 amps, dropping to 1.3 amps. Maximum draw at high call from all 3 zones was 7.9 amps"
This is a frustrating situation! You've taken some good first steps in troubleshooting, but the problem persists. Let's break down the information and explore potential causes and solutions
Understanding the Problem
Heat Pump Circuit Tripping
The core issue is the 30A GFCI breaker for the heat pump tripping, typically on Sunday nights/Monday mornings. This suggests a possible pattern.
New Dedicated Circuit
Replacing the breaker, running a new circuit, and installing a fused disconnect eliminates many wiring issues as potential causes.
Mitsubishi Tech Inspection
The Mitsubishi rep's testing is crucial. The low inrush and running amperage readings indicate the heat pump itself isn't the problem.
Shared Overhead Drop
Both the house and ADU share the same power drop from the utility. This shared connection is a critical point to consider.
Possible Causes and Troubleshooting Steps1. GFCI Sensitivity/Nuisance Tripping
Higher Quality GFCI
Even though you replaced the breaker, some GFCI breakers are more sensitive than others. Consider trying a different brand or model of GFCI. Ask your electrician for recommendations. A commercial grade GFCI may have a different trip curve that would be less sensitive to nuisance tripping.
Wiring Installation
Verify the correct installation of the new wiring and all connections. Loose neutrals can cause GFCI trips.
Grounding Problems
Ensure proper grounding throughout the ADU, particularly for the heat pump. A poor ground can cause small leakage currents that trigger the GFCI. Test ground resistance.2.
Voltage Fluctuations/Power Quality
Utility Grid Issues
Sunday night/Monday morning could be a time of higher grid load, leading to voltage fluctuations (sags, swells, or spikes) on the shared overhead drop. GFCI breakers can trip on these fluctuations. This is a strong possibility given the consistent timing of the trips.
Monitor Voltage
Use a power quality meter to monitor voltage at the ADU panel over a 24-hour period, especially around the time the breaker typically trips. This will reveal if there are voltage anomalies.
Call the Utility
Contact your local utility company and inquire about voltage stability in your area, especially during peak demand times. Report your breaker tripping issue and ask if they have any known voltage problems.
Load Imbalance
If the main house is drawing a significantly different load on each leg of the 240V service, it can create imbalances that affect the ADU's voltage.
Measure Load
Use a clamp meter to measure the current on each leg of the main house panel and the ADU panel during the times when the breaker trips. Look for significant imbalances.3.
Harmonic Distortion
Other Devices
Harmonic distortion introduced by other electronic devices in the house or ADU (LED lights, computers, inverters, etc.) can interfere with the GFCI breaker.
Test Without Other Loads
Try turning off as many other electrical devices as possible in both the house and ADU around the time the breaker typically trips to see if it stops the tripping.
Harmonic Filter
If harmonic distortion is suspected, a qualified electrician can install a harmonic filter to mitigate the issue.4.
Shared Neutral (Highly Unlikely, but Worth Checking)
Neutral Wire Check
While unlikely with a new dedicated circuit, double-check to ensure the neutral wire for the heat pump circuit is dedicated and not shared with any other circuits in the ADU or house. Shared neutrals can cause GFCI tripping. This is a major code violation.5.
Heat Pump Itself (Less Likely, but Re-evaluate)
Component Failure Over Time
Even though the tech tested the heat pump, a component could be starting to fail intermittently, causing a small ground fault that the GFCI is detecting.
Condensation/Moisture
Check for any condensation or moisture inside the heat pump unit, especially near electrical connections. Moisture can create a path to ground and cause a trip.
Wiring Inside the Unit
Inspect the wiring inside the heat pump unit itself for any signs of damage, loose connections, or rubbing against metal parts.
Action Plan1. Power Quality Monitoring (CRITICAL)
Invest in monitoring the voltage at the ADU panel around the time the breaker trips to rule out voltage fluctuations. This is the most likely cause based on your description.2.
Call the Utility Company
Report the consistent tripping and ask about voltage stability in your area, especially during peak demand.3.
Check the Dedicated Circuit Again
Re-verify the wiring of the heat pump circuit, especially the neutral and ground connections. Make sure they are tight and properly terminated.4.
Test With Minimal Load
Try to reduce the electrical load in both the house and ADU around the time the breaker trips to see if it prevents the tripping.5.
Advanced Testing
If the problem persists, hire a qualified electrician who specializes in troubleshooting electrical issues. They can use advanced testing equipment to pinpoint the source of the ground fault.
Important Considerations Safety First
Always work with a qualified electrician for any electrical work.
Documentation
Keep detailed records of all troubleshooting steps, tests, and results.
Communicate: Stay in close communication with your electrician and the Mitsubishi rep.This is a process of elimination. By systematically ruling out potential causes, you should eventually find the source of the problem and implement a solution. Good luck! Flag for review