Question: Hi just looking for insight here. Work seem pretty straight forward. This is how I see it regarding the two units I posted below.1. Disconnect power inside MCC and do the starter removal and wiring modification in MCC. MCC has fuses and not breaker.2. Disconnect conduit and wire at the motor factory mounted disconnect switch and secure in place so its ready for new motor.3. New VFD and motor/unit get delivered I reconnect the existing feed to the VFD and then run new from the VFD to disconnect switch.4. Power up MCC portion that feeds this unit. If there is no breaker in the MCC and its just fuses is there an "on/off" at the MCC for this circuit?Does this about sum up work involved. Anything else I need to consider? Thank you very much,
Yes, your summary generally captures the key steps involved in replacing a motor with a VFD-driven motor. However, let's break down each step with added considerations and potential pitfalls
1. MCC Disconnect and Starter Modification:
Your Description
"Disconnect power inside MCC and do the starter removal and wiring modification in MCC. MCC has fuses and not breaker."
Additional Considerations
Verify Isolation
Double and triple check that the power is absolutely off to the starter you're working on. Use a reliable voltage tester to confirm. Lockout/Tagout (LOTO) is paramount. Don't rely solely on the fuse removal.
Fuse Removal
Before removing the fuses, document which fuses correspond to which starter. Photographing the fuse arrangement is helpful. Keep the fuses in a safe place for possible future use.
MCC On/Off
If there's no breaker, and just fuses, there isn't a dedicated "on/off" switch for the entire circuit at the MCC. Removing the fuses is effectively your "off" position. Replacing them is your "on" position.
Starter Removal and Wiring Modifications
Thoroughly document the existing wiring before you disconnect anything. Take pictures, make diagrams, and label wires if necessary. This is crucial for potential troubleshooting or future maintenance. Ensure all wiring modifications comply with the VFD manufacturer's instructions and local electrical codes.
Grounding
Pay very close attention to grounding. VFDs are sensitive to proper grounding. Make sure your grounding system is robust and properly connected.
Arc Flash Hazard
Be aware of the potential arc flash hazard when working inside the MCC. Wear appropriate PPE.
Check control circuits
Consider the control wiring that feeds the starter. If your starter has any control wires tied into an external system, be sure to trace and document these wires. You may need to find a way to replace these signals coming from the VFD.
2. Motor Disconnect and Wiring
Your Description
"Disconnect conduit and wire at the motor factory mounted disconnect switch and secure in place so its ready for new motor."
Additional Considerations
Verify Disconnect Switch is OFF
Again, verify the disconnect switch is OFF and locked out/tagged out.
Condit Condition
Inspect the conduit and ensure it's in good condition. If there's any damage, corrosion, or the need for new seals, address it now.
Wire Labeling
Label the wires at the disconnect switch before disconnecting them. This will make reconnection to the new motor much easier. Even if they are color coded.
Wire Securing
Protect the exposed wires from the elements and accidental damage. Use wire nuts and tape to insulate the ends. Secure the wires inside the disconnect box.
Inspect the Disconnect
Is the existing disconnect suitable for the VFD output? VFDs can generate harmonics and voltage spikes. Consider upgrading the disconnect to a VFD-rated one, if necessary, and consult with the VFD manufacturer's recommendation.
Physical fit
Make sure new motor will physically fit.
3. VFD and Motor Installation and Wiring
Your Description
"New VFD and motor/unit get delivered I reconnect the existing feed to the VFD and then run new from the VFD to disconnect switch."
Additional Considerations
VFD Location
Consider the environment where the VFD will be installed. Is it adequately protected from dust, moisture, and temperature extremes? VFDs have specific environmental requirements.
VFD Input Wiring
Ensure the input wiring to the VFD is properly sized for the VFD's input current requirements. Consider the VFD's power factor.
VFD Output Wiring
Use VFD-rated cable for the output wiring from the VFD to the motor. This cable is designed to withstand the voltage spikes and harmonics generated by the VFD. Ensure the cable is properly shielded and grounded to minimize noise.
Motor Overload Protection
VFDs provide electronic overload protection for the motor. Make sure this protection is properly programmed and configured according to the motor's nameplate data. Disable any overload protection built into the motor starter (which you have already removed).
Motor Connections
Connect the motor wiring to the disconnect switch correctly, following the motor nameplate and wiring diagram.
VFD Programming
This is a critical step. Carefully program the VFD according to the motor's nameplate data (voltage, current, frequency, speed, etc.). Set up any necessary control parameters and safety features.
Brake Resistor
If the application requires rapid deceleration, consider installing a brake resistor for the VFD.
Input filter
If required, install an input filter.
4. Power Up and Testing
Your Description
"Power up MCC portion that feeds this unit. If there is no breaker in the MCC and its just fuses is there an "on/off" at the MCC for this circuit?"
Additional Considerations
Pre-Power Checks
Before energizing anything, double-check all wiring connections, grounding, and VFD programming.
Gradual Power Up
Start by powering up the VFD only. Verify that the VFD powers on correctly and that there are no error messages.
Motor Rotation
Before connecting the motor to the load, "jog" the motor to verify correct rotation. If the rotation is incorrect, swap two of the motor leads at the disconnect switch.
Monitor Motor Current and Voltage
Use a multimeter or clamp meter to monitor the motor current and voltage while the motor is running. Ensure that the motor is operating within its nameplate ratings.
Test with Load
Gradually increase the load on the motor and monitor its performance. Look for any signs of overheating, vibration, or unusual noise.
Document Settings
Record all VFD programming settings and motor performance data for future reference.
Commissioning Report
Generate a commissioning report detailing the installation, wiring, programming, and testing of the VFD and motor.
Fuse Selection
Be certain that the fuses are of the proper rating. A VFD will generally require fast acting fuses.
Additional Considerations
Electrical Codes
Ensure all work complies with local electrical codes and regulations (NEC in the US, CEC in Canada, etc.).
VFD and Motor Compatibility
Ensure the VFD and motor are compatible in terms of voltage, current, and horsepower.
Training
Ensure that personnel involved in the installation and programming of the VFD are properly trained.
Commissioning Support
Consider getting commissioning support from the VFD manufacturer or a qualified technician.
Documentation
Maintain detailed documentation of all work performed, including wiring diagrams, VFD programming settings, and test results.
Communication
Communicate with all relevant stakeholders (plant operations, maintenance, etc.) throughout the process.
EMC/RFI
VFDs can generate electromagnetic interference (EMI) and radio frequency interference (RFI). Take steps to minimize interference, such as using shielded cables, grounding properly, and installing filters.
In summary: Your high-level outline is accurate, but the devil is in the details. Meticulous planning, thorough documentation, and strict adherence to safety protocols are crucial for a successful VFD installation. Good luck! Flag for review