Question: Hello,I am an electrician for 5 years working towards my journeyman's now.Currently my brother is installing a new shed that he want power run to. He wants a small a/c mini split, a mini fridge, some outlets for his office set up, and led lights.I do not have any wattage or amp specifics for the a/c or fridge but I assume that a 50 amp sub panel would be sufficient.Of course I'm trying to keep costs down and not have to get a bigger panel and thus bigger wire and bigger conduit etc.After some initial research I am not able to find a 50amp sub panel that has at least 8 breaker slots. Does such a sub panel even exist and where can I get it?Or, do I have to use a higher amount sub panel?Thank you.

You're on the right track planning this out, and wanting to keep costs down is smart. Let's break down the 50A subpanel and your options.

Yes, a 50A Subpanel with 8 Circuits Does Exist

While it might not be readily available at big box stores, a 50A subpanel with 8 or more circuit spaces absolutely exists. You're looking for something commonly referred to as a "load center" or "breaker box." The number of spaces (where breakers plug in) is independent of the amperage of the main breaker feeding the panel.

Where to Find a 50A, 8+ Space Subpanel



Electrical Supply Houses

This is your best bet. Local electrical supply houses are the go-to for electricians because they carry a wider variety of panels and components than big box stores. Tell them what you're doing, and they can guide you to the right panel. They can also advise on brand reputations and what's in stock.


Online Retailers (Be Careful)

You can find them online, but verify the specifications. Check the amperage rating and the number of available spaces very carefully. Look for reputable brands like Square D, Eaton, Siemens, and GE. Don't go with off-brand or unknown manufacturers for critical electrical components.

Why You Might Be Having Trouble Finding One Easily



Big Box Stores Focus on Common Sizes

Big box stores cater to a broad homeowner market. They stock the most common panel sizes, which might be a 60A, 100A, or 200A main panel for a house, or smaller 30A/6 space for a hot tub. A 50A subpanel is a bit less common.

50A Might Be
Cutting It Close - Do Load Calculations

Before you commit to 50A,
strongly consider doing a proper load calculation. This is critical for safety and ensuring your brother doesn't trip breakers all the time. Here's why:1.

Mini-Split

Mini-splits can have a decent inrush current on startup, and their running amperage varies. Look at the
nameplate on the unit (or the installation manual) to find the Minimum Circuit Ampacity (MCA) and the Maximum Overcurrent Protection (MOCP). The MCA is the minimum ampacity the circuit needs to handle, and the MOCP is the largest breaker you're allowed to use. You'll want to plan your circuit based on these ratings.2.

Mini-Fridge

Again, look at the nameplate. Find the running amperage.3.

Outlets for Office

Here's where it gets tricky. You can't just assume each outlet is insignificant. Think about what might be plugged in at the
same time: computer, monitor, printer, phone charger, maybe a small space heater, etc. A good rule of thumb for general-purpose outlets is to assume a load of 1.5 amps per outlet (180 watts at 120V).
4.


LED Lights

LED lights are efficient, but add up the wattage of all the lights and divide by the voltage (120V) to get the amperage.

How to Do a Basic Load Calculation


List everything

List everything that will be running
simultaneously in the shed: mini-split (use MCA), mini-fridge, outlets (multiply the number of outlets by 1.5 amps to get total amperage), LED lights.
2.


Add up the Amps

Add up all the amperage values from step 1.3.

Factor in Future Expansion

It's wise to add a buffer of 20% to your calculated amperage to account for potential future expansion or things your brother might add later.

Example

Mini-split (MCA): 15 amps Mini-fridge: 2 amps Outlets (6 x 1.5 amps): 9 amps LED lights: 1 amp

Total

27 amps

Plus 20%

32.4 ampsIn this example, 32.4 amps is well within the 50A, but this is a
simplified example. A more powerful mini-split, more outlets, or other appliances could easily push you over.

Upsizing Might Be Necessary

If your load calculation comes close to 50A,
seriously consider bumping up to a 60A or even a 70A subpanel. Yes, it will cost a bit more for the panel, wire, and conduit, but:

Headroom

It gives you much more breathing room and avoids nuisance tripping.

Future-Proofing

It allows for future expansion without having to replace the entire subpanel and wiring.


Safety

Running a panel consistently near its maximum capacity is not ideal and can shorten the lifespan of components.

Wiring



Wire Size

Remember to use the correct wire size for the amperage of the breaker feeding the subpanel. Consult a wire ampacity chart for your type of wire (THHN, etc.) and the installation method (in conduit, etc.). Using undersized wire is a
major fire hazard. For a 50 amp feed you will need a minimum of #6 AWG copper wire. For a 60 or 70 amp feed, you will need a minimum of #4 AWG copper wire.

Grounding

Ensure proper grounding.

Conduit

Use the correct size and type of conduit for your wire and location (underground, exposed, etc.).

Recommendations


Perform a Detailed Load Calculation

Get the exact wattage/amperage information for the mini-split and fridge. Be realistic about the usage of the outlets.2.

Consult with a Local Electrical Inspector

They can give you specific advice based on your local codes and requirements.3.

Visit an Electrical Supply House

Tell them what you're doing, and they can show you the available 50A+ subpanels with the required number of spaces, as well as the correct wiring and conduit.4.

Consider Upsizing to 60A or 70A

It might be a worthwhile investment for long-term reliability and future expansion.

Important Safety Notes



If you're not comfortable working with electricity, hire a qualified electrician.
Electrical work can be dangerous. Always de-energize the circuit before working on it. Follow all local electrical codes.

Good luck with your project! Doing the planning upfront will save you headaches (and money) down the road. Flag for review