Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Smoke Control power monitoring

User: Kingswillfall, Location: Atlanta

Asked on: Monday, October 20, 2025 at 2:29 pm EDT
Answered on: Monday, October 20, 2025 at 3:06 pm EDT

Question: I have to provide “positive confirmation” according to NFPA92 sec 6.4.8.2. The presence of power for a dual zone smoke control system. VFDs are housed inside with local disconnects at the fans (outside). Power monitoring must be downstream of all circuit disconnects. This means load side of the last disco and the fan motor. My dilemma is that the system is only powered when commanded by Fire Alarm input to the VFDs. How do I show status without power downstream of the disco and still meet the requirement?

This is a tricky situation, but you're right in identifying the core problem: demonstrating power without continuously powering the system, especially since it's designed to only power up on a fire alarm activation. Here's a breakdown of possible solutions and approaches, focusing on meeting the intent of NFPA 92 Sec 6.4.
8.2 while working within the constraints of your system

Understanding NFPA 92 Sec 6.4.
8.2


Before diving into solutions, let's be clear on the intent. NFPA 92, section 6.4.
8.2 likely requires positive confirmation of power presence to ensure that the smoke control system is ready and capable of operating in an emergency. The reasoning is to identify power failures (blown fuses, tripped breakers) before a fire occurs, preventing system failure when it's needed most. It's not solely about the fan running, but about the availability of the power supply.

Possible Solutions (Prioritized by Feasibility and Compliance)1. Pilot Circuit (Recommended and Best Practice) Concept

Create a separate,
always-on low-voltage pilot circuit that monitors the main power circuit downstream of the final disconnect.

Implementation

Install a small, dedicated low-voltage power supply (e.g., 24VDC) wired before the local disconnect on the line side of the VFD. Run this low-voltage power to a relay (or a voltage monitor/sensor) on the load side of the disconnect (and ideally, as close to the motor terminals as practically feasible). The relay/sensor is energized when the main power is present on the load side. If power is lost (due to a tripped breaker, open disconnect, or any other fault), the relay de-energizes. Connect the relay contacts to the fire alarm panel's monitoring input. This gives you a continuous "power available" signal.

Benefits

Meets the intent of continuous power monitoring without constantly running the high-voltage system. Provides clear and reliable indication of power loss. Relatively easy to implement. Provides continuous monitoring and alarm if the disconnect is turned off.

Documentation

Crucially, document this setup thoroughly in the system's operating and maintenance manuals.2.

Automated Periodic Power Confirmation Test
Concept

Program the Fire Alarm Control Panel (FACP) and/or the VFDs to perform a brief, automated power confirmation test at regular intervals (e.g., weekly, monthly).


Implementation

The FACP sends a signal to the VFD to initiate a short test run (a few seconds) of the fan at a very low speed. The VFD monitors current and voltage on its output. If the VFD sees the expected electrical parameters, it sends a "power OK" signal back to the FACP. If the parameters are not met (due to power loss), the VFD sends a "power failure" signal. The FACP logs the test results and generates an alarm if a failure is detected. Consider a test period within 24 hours of each activation.

Considerations

Requires close coordination between the FACP and VFD programming. The short test run shouldn't significantly impact the lifespan of the motor or bearings. A soft start is essential. This test should be designed with a reduced speed that minimizes strain. This needs to be documented in a testing plan to meet NFPA 92 requirements.

Documentation

Detailed documentation of the testing procedure, frequency, acceptance criteria, and reporting mechanisms is absolutely essential for code compliance.3.

Load Side Voltage Monitoring of FACP Signal
Concept: If the system is designed to fail safe, you could monitor the output of the signal from the FACP to the VFD when the fire alarm system is inactive. The intent here is that the failure of this signal would constitute an alarm state. Implementation: The FACP provides a voltage signal (ex. 24VDC) to the VFD to engage the fan on alarm. A relay is placed downstream of the FACP to monitor the voltage signal. When voltage is present, the relay indicates normal. If the voltage drops, the relay de-energizes and shows failure. If the signal fails, the assumption is that the VFD is unavailable on system demand and therefore constitutes an alarm state. Considerations: Requires close coordination between the FACP and the VFD. Assumes that any wire break is a failure state This needs to be documented in a testing plan to meet NFPA 92 requirements. Documentation: Detailed documentation of the testing procedure, frequency, acceptance criteria, and reporting mechanisms is absolutely essential for code compliance.4. Smart Motor Controller with Power Monitoring Concept

Replace the standard motor with a smart motor controller that has built-in power monitoring capabilities.


Implementation

The smart motor controller continuously monitors voltage, current, and power factor. It can be configured to send an alarm signal to the FACP if any of these parameters fall outside acceptable limits (indicating a power problem).

Benefits

Provides continuous power monitoring and detailed diagnostic information.


Drawbacks

Higher initial cost. May require significant system modifications.

Important Considerations for All Solutions
Coordination with the AHJ (Authority Having Jurisdiction)

Crucially, discuss your proposed solution with the local fire marshal or building inspector before implementing anything. They have the final say on whether your approach meets the intent of the code. Get their approval in writing if possible.

Fail-Safe Design

Ensure that any monitoring system is designed to be "fail-safe." Meaning that if the monitoring system itself fails, it should trigger an alarm, rather than falsely indicating that power is available.

Clear Labeling

Clearly label all components of the power monitoring system, including the power supply, relays, and wiring.


Comprehensive Documentation

Thoroughly document the power monitoring system in the operating and maintenance manuals, including wiring diagrams, test procedures, and troubleshooting information. This is critical for future maintenance and inspections.*

Testing and Commissioning

Rigorous testing is essential to ensure that the power monitoring system is functioning correctly and that it provides accurate and reliable indications of power availability. Test under various failure conditions (e.g., open disconnect, tripped breaker).

Example Documentation Excerpt (for Pilot Circuit Solution)
"The smoke control system's fans are equipped with a dedicated power monitoring circuit to ensure power availability prior to fire alarm activation, as required by NFPA 92 Sec 6.4.
8.2. This circuit consists of a [Voltage]VDC power supply located in the [Location] panel, wired on the line side of the fan's local disconnect switch. The [Voltage]VDC power is fed to a [Relay Model] relay, located in the [Location - near Fan Motor] enclosure, on the load side of the disconnect. The relay is configured with normally closed contacts. Loss of power on the load side of the disconnect will de-energize the relay, closing the contacts and signaling a 'Power Unavailable' alarm to the Fire Alarm Control Panel, input [Input Number/Description]. See wiring diagram [Diagram Number] for details."In summary, prioritize the pilot circuit solution or the automated periodic test approach, and always coordinate closely with the AHJ to ensure compliance. Good luck! Flag for review

Previous Question Next Question