Topic: IR scan

User: mannyb, Location: Florida

Asked on: Monday, October 20, 2025 at 3:32 pm EDT
Answered on: Monday, October 20, 2025 at 3:43 pm EDT

Question: I have used a laser thermometer to check temp breakers to check amvmbient temp for breakers/equipment. I have been sucessful in the past but wanted to try this next IR scan device. The IR camera and Laser are is pretty close to each others temperature. My questlion is when using the devices. How much variance in temperature should one be looking for? If most of my breakers read 88degrees and 1 of the breakers read 110 degress is it safe to say theres a problem? In previous experience I have had YES but the camera makes me doubt. I always read ambient temperature of surrounding equipment and compare reading before making the decision. Any one share advice using camera....and dont get me started on the heat from sun. This does affect scan.

Okay, let's break down how to interpret temperature variances you see with an IR camera and laser thermometer when inspecting breakers, and address some common concerns.

Understanding Temperature Variance & What It Means It's Not Absolute Temperature, It's Relative Temperature. You're looking for significant differences compared to the surrounding components under similar load conditions. The absolute temperature readings (like 88°F or 110°F) are less important in isolation than the difference between them. Load is King. Breakers get warm because of the current flowing through them. If a breaker is carrying near its rated load, it will be warmer than breakers carrying little or no load. You need to have a reasonable understanding of the loads the breakers are supporting to make informed decisions. Ideally, compare breakers carrying similar loads. The 10°C (18°F) Rule of Thumb (and its limits)

A common guideline in electrical thermography is that a temperature difference of 10°C (18°F) or more compared to similar components
under similar load is worth investigating.

<10°C (18°F) Difference

Likely normal, or only a minor anomaly. Monitor, but probably no immediate action needed.

10°C - 20°C (18°F - 36°F) Difference

Investigate further. Check connections, look for loose wiring, signs of corrosion. This could indicate a developing problem.


>20°C (36°F) Difference

Serious problem. Shut down the circuit if possible, and investigate immediately. High risk of failure, potential fire hazard.

Your Example: 88°F vs. 110°F
You have a 22°F (approximately 12°C) difference. This is significant and warrants a full investigation. This is especially true if the breakers are supposedly carrying similar loads.

Why the Camera Might Make You Doubt (and how to use it effectively)
Higher Sensitivity

IR cameras are much more sensitive than laser thermometers. They can pick up subtle differences that a laser thermometer might miss or average out. This can lead to you seeing more variation. This isn't a bad thing, it's just a more detailed picture.

Emissivity

IR cameras measure infrared radiation. The
emissivity of a surface is how well it emits infrared radiation compared to a perfect blackbody. Different materials have different emissivities. Breakers often have varying surface finishes (plastic, metal, labels), which can affect the IR reading. Better cameras allow you to adjust emissivity settings, but for quick scans, focus on relative differences within the same material.

Reflected Heat

Shiny surfaces can reflect heat from other sources (like nearby equipment, sunlight through a window, or even yourself). This can give false readings. Try to position yourself so reflections are minimized.

Resolution & Distance

An IR camera's resolution determines how small an area it can accurately measure. At a distance, it might be averaging the temperature of a larger area than you think, blurring small hot spots. Get closer for more accurate readings, but maintain a safe distance.

Best Practices for Using an IR Camera for Breaker Inspections


Establish a Baseline

Before looking for problems, scan your entire panel when it's known to be operating under normal conditions. This creates a baseline for future comparisons.2.

Load Information

Document the load on each circuit you are scanning. Use an ammeter to measure the current. This is critical for accurate interpretation.3.

Consistent Distance

Maintain a consistent distance from the panel when scanning. This helps ensure comparable readings.4.

Multiple Angles

Scan from different angles to minimize reflections and shadows.5.

Focus

Make sure the image is in focus. Blurry images lead to inaccurate temperature readings.6.

Adjust Settings (if possible)

If your camera allows, set the emissivity appropriately for the materials you are scanning.7.

Look for Patterns

Are multiple breakers on the same phase running hotter than others? This could indicate a larger problem with the feeder.8.

Document Everything

Take thermal images and regular photos. Note the load on each circuit, the ambient temperature, and any other relevant observations.9.

Follow Up

If you find a hot spot, don't just assume the breaker is bad. Turn off the circuit (safely!), open the panel, and inspect the breaker terminals, wiring, and the busbar for signs of corrosion, loose connections, or damage. Use a torque wrench to ensure connections are properly tightened. Sometimes the problem is at the connection, not the breaker itself.

Addressing Specific Concerns



Sunlight

You are absolutely correct that sunlight will ruin your IR scans. Direct sunlight heats up components and makes it impossible to get reliable readings. Scan panels early in the morning or late in the afternoon, or when the panel is shaded.

Comparison to Laser Thermometer

The IR camera should be giving you
more* information than the laser thermometer, not less. Use the laser thermometer to confirm any hot spots you find with the IR camera, but trust the camera's ability to detect subtle differences. The laser thermometer can be useful for spot-checking and comparison, but the camera gives a much more comprehensive view.

In Summary:


That 110°F breaker reading compared to 88°F is a red flag. Don't ignore it just because you have a new tool. Use the IR camera to pinpoint the exact location of the heat, and then follow up with a thorough visual and mechanical inspection. Always prioritize safety! If you're not comfortable working on electrical equipment, call a qualified electrician.Let me know if you have any other questions. Good luck! Flag for review