Question: Im replacing a 400amp interior panel which is currently fed with a 400amp breaker from an 800amp switch gear. Customers load has reduced to the point where a 400a panel isnt needed, so im replacing with a 200a. Why can i not feed the 200a with 200a feeders fed off the 400a main breaker? I get the feeders are undersized for the 400amp but they are then fused at the sub panel, so it would be the same as using a 400a disconnect with 200a feeders going to the sub panel (which the inspector said would be acceptable). I dont see the difference between using the breaker and the disconnect? Any help would be appreciated.
You've hit on a point of contention that often comes up, and you're right to question it. Here's a breakdown of the reasons why an inspector might reject your proposal, and the NEC articles they are likely referencing: Overcurrent Protection at the Point of Supply
The primary argument against your setup is the NEC's requirement for overcurrent protection to be sized at the amperage of the conductors supplying the load.
NEC 240.21(B)(1) - Feeder Taps
This section allows for taps (reduced size conductors) if they meet specific requirements, most of which you won't likely meet in your situation. These requirements are stringent and are designed to prevent overloading the smaller conductors. Key considerations include:
Tap Length
The tap length is severely restricted. In most scenarios, you'd likely be too far away to meet those limitations.
Overcurrent Protection
The tap conductors need to be protected by an overcurrent device at the point where they receive their supply, unless the tap length meets the requirements of 240.21(B)(2), (3), or (4). These exceptions have stringent rules for length, and the load size must be less than the ampacity of the feeder.
In essence, the inspector is interpreting that the 400A breaker upstream is designed to protect the 400A conductors, not the smaller 200A conductors you intend to tap. Misapplication of Equipment
A breaker is designed to protect the wiring downstream of it. Using a 400A breaker to protect 200A conductors goes against this fundamental principle, regardless of the downstream panel's main breaker.
Potential for Overloading the Conductors
Even if the 200A breaker in the new panel should trip before the 200A conductors overheat, there's a perceived risk that a sustained overload below 400A but above 200A could damage the conductors before the upstream breaker trips. This is a theoretical risk that's addressed with NEC rules.
Why the Inspector Might Accept a Disconnect
The situation with a disconnect is different because a disconnect doesn't provide overcurrent protection. The disconnect simply provides a means to de-energize the circuit. With a disconnect, you would need a separate overcurrent protective device, such as fuses or a breaker, at the point where the 200A conductors are connected to the 400A conductors.
The Key Difference
Breaker
Is both a disconnecting means and an overcurrent protective device. Using an oversized breaker in place of an appropriately sized one defeats the overcurrent protection purpose.
Disconnect
Is only a disconnecting means. It doesn't inherently provide overcurrent protection.
Your Argument (and why it might not win)
You're right to point out that the 200A breaker in the new panel provides overcurrent protection at that point. In your mind, it's functionally the same as using a fused disconnect. However, the NEC prioritizes protection at the source of the conductors, and the inspector's interpretation is likely aligned with that principle.
Possible Solutions (Discuss with the Inspector First!)
Replace the 400A Breaker with a 200A Breaker
This is the most straightforward and compliant solution. Since the load is now only 200A, replace the 400A breaker in the 800A switchgear with a 200A breaker. This provides the correct overcurrent protection for the 200A conductors.2.
Fused Disconnect
Use a 400A rated disconnect switch directly off the switchgear bus. Then, you would feed to a fuse block and then your 200A wires. This configuration would be compliant as the fuses would be your overcurrent protection, sized for the wiring.3.
Tap Rules Compliance (Highly Unlikely)
Attempt to comply with the very specific requirements of NEC 240.21(B) regarding feeder taps. This is often impractical due to the distance and physical constraints involved.
4.
Appeal
If you strongly believe in your interpretation and have a very good understanding of the NEC, you could appeal the inspector's decision. However, this can be a lengthy and confrontational process.
Before Proceeding
Talk to the Inspector
Discuss your proposed solution and their reasons for rejecting it. Understand their interpretation of the NEC. Open communication is key.
Document Everything
Keep detailed records of your conversations, the inspector's feedback, and the specific NEC articles they cite.
Consider a Second Opinion: If you're still unsure, consult with another qualified electrician or electrical engineer for a second opinion.In summary, while your logic has merit, the inspector is likely basing their decision on a strict interpretation of the NEC's overcurrent protection requirements, particularly the need for protection at the source of the conductors. The easiest solution is to simply replace the breaker with one of the correct size. Flag for review