Question: The first picture is an A/C compressor the customer has. The compressor is 480 and the service is 240. I said you need a step up transformer. The second is the label of a transformer he found. I determined he needed the 30 Kva transformer. A lower kva did not seem to be available. This is from memory. I said it needs to be sized to the “20 amp max fuse” the compressor says. Someone told him it needs to be sized to the LRA that he has circled. We are in Chicago, and both units will be mounted outside.Can I have some advice please. ThanksMike
Okay, Mike, this is a common situation, and getting the transformer sizing right is crucial. Let's break it down
Understanding the Problem
Mismatched Voltage
Your customer has a 480V compressor and only 240V service available. This definitely requires a step-up transformer.
Transformer Sizing
The core question is how big of a transformer. You initially focused on the "20 amp max fuse," while someone else suggested using the Locked Rotor Amps (LRA). Both pieces of information are important, but
the LRA is more critical for sizing the transformer.Why LRA Matters More Than Max Fuse LRA is a Momentary Spike
The LRA is the instantaneous current draw when the compressor motor starts. It's a massive spike that lasts only for a fraction of a second, maybe a few seconds at most.
Max Fuse is for Continuous Running
The "Max Fuse" (or often the Minimum Circuit Ampacity (MCA)) is designed to protect the wiring and components from sustained overcurrents during normal operation. It's based on the Running Load Amps (RLA) plus a safety margin for other components.
Transformer Must Handle the Start-Up Surge
The transformer needs to be able to deliver the LRA without excessive voltage sag or damage. If the transformer is too small, the voltage will drop significantly during start-up, which can damage the compressor motor, shorten its life, or cause it to fail to start at all.
Analyzing the Compressor Label 480V, 3 Phase, 60Hz
This confirms the voltage requirement and the type of power.
20 Amp Max Fuse
This relates to the continuous operating current.
LRA: 107 Amps
This is the key number for transformer sizing. The customer circled it, which is correct.
RLA: 5.8 Amps
This is also needed, but secondary to the LRA.
Sizing the Transformer Correctly1. Calculate KVA from LRA
You need to convert the 480V LRA to KVA using the following formula: KVA = (Volts x Amps x √3) / 1000 KVA = (480V x 107A x 1.732) / 1000 KVA = 89.12 KVA2.
Account for Oversizing
It's crucial to oversize the transformer to account for:
Voltage Sag
You want to minimize voltage drop during the LRA surge. A larger transformer will sag less.
Future Growth
Consider if the customer might add additional load in the future.
Transformer Efficiency
Transformers aren't 100% efficient. A good rule of thumb is to add 25% to the LRA-derived KVA. 89.12 KVA 1.25 = 111.4 KVA.
3.
Look for the Next Standard Size
Standard transformer sizes typically come in increments. You'll want to choose the next largest standard KVA size above your calculated KVA. Common sizes are: 15, 30, 45, 75, 100, 112.5, 150, 225 KVA, and so on.
4.
Review Transformer Label Information
30 KVA Transformer: Primary: 240 Delta
This matches your incoming service!
Secondary: 480Y/277
This is good! It provides the 480V you need.
Amps: 36 (Primary) / 36 (Secondary): Check these amperage ratings. 30,000 / (240 x 1.732) = 72 amps. 30,000 / (480 x 1.732) = 36 amps. Is that the right secondary voltage? Be sure it is designed to accept 240 VAC primary and supply 480 VAC secondary. THIS TRANSFORMER IS FAR TOO SMALL TO POWER THE COMPRESSOR5. Select the Proper Transformer Based on the calcations, you need a 112.5 KVA transformer at minimum. It is better to use a 150 KVA transformer.
Important Considerations 3-Phase Power
You must ensure that both the incoming 240V service and the transformer are 3-phase. You cannot run a 3-phase compressor off a single-phase transformer or service.
Transformer Location (Outdoor)
Weather Rating
The transformer must be rated for outdoor use (NEMA 3R or similar).
Mounting
Mount it properly and securely according to the manufacturer's instructions.
Clearance
Maintain proper clearances around the transformer for ventilation and maintenance.
Local Codes
Always check with your local electrical codes and permitting requirements. Chicago has very specific codes. An inspection is likely required.
Professional Installation
This is not a DIY job for the homeowner. A qualified, licensed electrician must perform the installation.
Overcurrent Protection
Properly size the overcurrent protection (fuses or circuit breakers) on both the primary (240V) and secondary (480V) sides of the transformer. This should be based on the transformer's nameplate ratings. It does not have to match what the unit says.
In summary
You must calculate the LRA KVA and oversize it to account for voltage sag. The existing 30 KVA transformer that was found is too small and would likely lead to compressor failure. The correct transformer for the compressor should be a 150 KVA step up transformer rated for outdoor use. Flag for review