Topic: Sizing a transformer

User: mike1061, Location: Chicago

Asked on: Monday, October 20, 2025 at 5:44 pm EDT
Answered on: Monday, October 20, 2025 at 5:44 pm EDT

Question: The first picture is an A/C compressor the customer has. The compressor is 480 and the service is 240. I said you need a step up transformer. The second is the label of a transformer he found. I determined he needed the 30 Kva transformer. A lower kva did not seem to be available. This is from memory. I said it needs to be sized to the “20 amp max fuse” the compressor says. Someone told him it needs to be sized to the LRA that he has circled. We are in Chicago, and both units will be mounted outside.Can I have some advice please. ThanksMike

Okay, Mike, this is a common situation, and getting the transformer sizing right is crucial. Let's break it down

Understanding the Problem
Mismatched Voltage

Your customer has a 480V compressor and only 240V service available. This
definitely requires a step-up transformer.

Transformer Sizing

The core question is how big of a transformer. You initially focused on the "20 amp max fuse," while someone else suggested using the Locked Rotor Amps (LRA). Both pieces of information are important, but

the LRA is more critical for sizing the transformer.
Why LRA Matters More Than Max Fuse LRA is a Momentary Spike

The LRA is the
instantaneous current draw when the compressor motor starts. It's a massive spike that lasts only for a fraction of a second, maybe a few seconds at most.

Max Fuse is for Continuous Running

The "Max Fuse" (or often the Minimum Circuit Ampacity (MCA)) is designed to protect the wiring and components from sustained overcurrents during normal operation. It's based on the Running Load Amps (RLA) plus a safety margin for other components.

Transformer Must Handle the Start-Up Surge

The transformer needs to be able to deliver the LRA without excessive voltage sag or damage. If the transformer is too small, the voltage will drop significantly during start-up, which can damage the compressor motor, shorten its life, or cause it to fail to start at all.

Analyzing the Compressor Label
480V, 3 Phase, 60Hz

This confirms the voltage requirement and the type of power.

20 Amp Max Fuse

This relates to the continuous operating current.


LRA: 107 Amps

This is the key number for transformer sizing. The customer circled it, which is correct.

RLA: 5.8 Amps

This is also needed, but secondary to the LRA.

Sizing the Transformer Correctly
1. Calculate KVA from LRA

You need to convert the 480V LRA to KVA using the following formula: KVA = (Volts x Amps x √3) / 1000 KVA = (480V x 107A x 1.732) / 1000 KVA = 89.12 KVA2.

Account for Oversizing

It's crucial to oversize the transformer to account for:

Voltage Sag

You want to minimize voltage drop during the LRA surge. A larger transformer will sag less.


Future Growth

Consider if the customer might add additional load in the future.

Transformer Efficiency

Transformers aren't 100% efficient.
A good rule of thumb is to add 25% to the LRA-derived KVA. 89.12 KVA 1.25 = 111.4 KVA.
3.


Look for the Next Standard Size

Standard transformer sizes typically come in increments. You'll want to choose the next largest standard KVA size above your calculated KVA. Common sizes are: 15, 30, 45, 75, 100, 112.5, 150, 225 KVA, and so on.
4.


Review Transformer Label Information



30 KVA Transformer
: Primary: 240 Delta

This matches your incoming service!


Secondary: 480Y/277

This is good! It provides the 480V you need.

Amps: 36 (Primary) / 36 (Secondary)
: Check these amperage ratings. 30,000 / (240 x 1.732) = 72 amps. 30,000 / (480 x 1.732) = 36 amps. Is that the right secondary voltage? Be sure it is designed to accept 240 VAC primary and supply 480 VAC secondary. THIS TRANSFORMER IS FAR TOO SMALL TO POWER THE COMPRESSOR5. Select the Proper Transformer Based on the calcations, you need a 112.5 KVA transformer at minimum. It is better to use a 150 KVA transformer.

Important Considerations 3-Phase Power

You must ensure that both the incoming 240V service
and the transformer are 3-phase. You cannot run a 3-phase compressor off a single-phase transformer or service.

Transformer Location (Outdoor)



Weather Rating

The transformer
must be rated for outdoor use (NEMA 3R or similar).

Mounting

Mount it properly and securely according to the manufacturer's instructions.

Clearance

Maintain proper clearances around the transformer for ventilation and maintenance.


Local Codes

Always check with your local electrical codes and permitting requirements. Chicago has very specific codes. An inspection is likely required.

Professional Installation

This is
not a DIY job for the homeowner. A qualified, licensed electrician must perform the installation.

Overcurrent Protection

Properly size the overcurrent protection (fuses or circuit breakers) on both the primary (240V) and secondary (480V) sides of the transformer. This should be based on the transformer's nameplate ratings. It does not have to match what the unit says.

In summary


You must calculate the LRA KVA and oversize it to account for voltage sag. The existing 30 KVA transformer that was found is too small and would likely lead to compressor failure. The correct transformer for the compressor should be a 150 KVA step up transformer rated for outdoor use. Flag for review