Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Question about proper cable for 48 VDC 5 to 10 A

User: Installer, Location: DesMoines, Washington

Asked on: Monday, October 20, 2025 at 9:01 pm EDT
Answered on: Monday, October 20, 2025 at 9:01 pm EDT

Question: A vendor is selling us a system sending 48 VDC ranging from 5A to 10 A from a DC converter in an Equipment Rack up seven floors in a cable shaft to power Communications Processors.The Amps would vary with the number of Communication Processors. This would be a Class 3 application since its greater than 100VA. The vendor is using 10 AWG 2 conductor stranded cable.The cable shaft contains Communications cabling as well as 120 VAC AC circuits in conduit.The vendor is using Plenum Cable.We’re trying to verify the vendor’s cable selectionArticle 725 says CL3R applies.We can’t locate 10 AWG-2 CL3R cable anywhere. We can find it in smaller gauges, around 12 to 18 AWG.What make us feel queasy is the insulation is usually a thin PVC jacket and is minimal.Also its always called "remote control and alarm cable"48 VDC at 10 A seems substantial.Is there anyway we can require the vendor to use 10 AWG/2 MC cable in this application?

You're right to be cautious. Let's break down the situation and analyze the code requirements, available options, and potential solutions.

Understanding the Problem Power Levels

48VDC at 5-10A translates to 240-480 Watts. This is definitely a significant amount of power.


Class 3 Circuits

Exceeding 100VA (Volt-Amps) firmly places this in Class 3 territory according to NEC Article 725.

Cable Shaft Environment

The presence of communications cabling, 120VAC circuits in conduit, and the multi-story run create a challenging environment requiring careful cable selection.


Code Compliance

You're correctly focusing on NEC Article 725, specifically Class 3 Remote-Control, Signaling, and Power-Limited Circuits.

Availability Issues

The difficulty finding 10 AWG CL3R cable is a significant red flag.

Analysis of NEC Article 725 and Other Relevant Codes
725.3(A) Classifications

725.3(A) defines class 1, 2, and 3 circuits.

725.15 Allowable Voltage and Current Combinations

This details the VA and current limits. You are exceeding the limits for class 2.


725.43 Class 3 Wiring Methods and Materials on Supply Side

You are on the supply side.

725.48 Class 3 Cable Uses and Permitted Substitutions

This is the crux of your issue. CL3R (riser rated) cable is the minimum you'd want in a cable shaft.
However, the key question is whether CL3R is the only acceptable cable.
Here's where the NEC provides some flexibility. You are permitted to use any cable permitted in Chapter 3 of the NEC, or other listed Class 3 cable
Chapter 3 Wiring Methods

This is where you'll find options like MC cable (Metal-Clad Cable), which is available in 10 AWG.

Why MC Cable is a Good Choice
Physical Protection

MC cable provides robust physical protection against damage, which is crucial in a cable shaft environment. It's far more resistant to crushing, abrasion, and other physical hazards than typical CL3R cable.


Grounding

MC cable inherently provides a grounding path via the metal sheath, which can be important for safety and reducing noise.

Higher Voltage/Current Ratings

MC cable is generally rated for higher voltage and current levels than standard CL3R cable, offering a safety margin.


Availability

MC cable is readily available in 10 AWG and with multiple conductors.

NEC 725.136(D) states "Class 3 circuit conductors shall be separated from conductors of electric light, power, Class 1, non-power-limited fire alarm, and medium power network-powered broadband communications circuits unless installed in a raceway, cable tray, a box, or a similar enclosure." Using a cable such as MC, you can run it in the same shaft.


Addressing the Plenum Requirement


Plenum vs. Riser

Plenum spaces (used for environmental air) have more stringent fire safety requirements. Riser spaces (vertical shafts connecting floors) also have specific fire safety requirements.

MC Cable Options

You can specify MC cable that is
also plenum-rated (CMP). This will ensure compliance with both riser and plenum requirements if you need to run the cable through a plenum space at any point.

Vendor's Plenum Cable

The vendor's choice of plenum cable might be based on a misunderstanding of where the cable actually runs. Double-check the entire cable route to confirm whether any portion passes through a true plenum space. If it doesn't, riser-rated MC cable is sufficient.

Your Action Plan1.

Clarify the Cable Route

Absolutely confirm the exact cable route. Does it pass through a true plenum space at any point? If not, you can focus on riser-rated (CMR) or general-purpose (CM) cable.2.

Specify MC Cable

Inform the vendor that you require 10 AWG MC cable (with the appropriate number of conductors) for the 48VDC power supply.3.

Specify Plenum Rating (If Necessary)

If the cable does pass through a plenum, specify 10 AWG plenum-rated (CMP) MC cable.4.

Request Documentation

Ask the vendor to provide documentation showing that the MC cable they propose meets or exceeds the NEC requirements for your application. This should include the cable's voltage/current ratings, fire rating (CMR or CMP), and listing information.5.

Consult with an Electrical Engineer

If you have any doubts or concerns, it's always best to consult with a qualified electrical engineer. They can perform a load calculation, verify the cable sizing, and ensure that the installation meets all applicable code requirements.6.

Consider Voltage Drop

A long cable run at 48VDC can experience significant voltage drop, especially at 10A. Ensure the vendor has accounted for voltage drop in their cable sizing calculations. You may need to increase the wire gauge to compensate.

Example Specification

"The 48VDC power supply cable shall be 10 AWG, 2-conductor Metal-Clad (MC) cable. The cable shall be listed and labeled for its intended use and meet or exceed the requirements of NEC Article 725 and Chapter 3. If any portion of the cable run passes through a plenum space, the MC cable shall also be plenum-rated (CMP). The vendor shall provide documentation verifying compliance with all applicable codes and standards."

In summary, requiring MC cable is a perfectly legitimate and often superior solution for this application. It provides better physical protection, inherent grounding, and is readily available in the necessary gauge. Just be sure to address the plenum rating if required by the specific installation. Flag for review

Previous Question Next Question