User: zooby, Location: Indiana
Asked on: Wednesday, October 22, 2025 at 6:24 am EDT
Answered on: Wednesday, October 22, 2025 at 6:25 am EDT
Question: "Therefore, 380 amps at 13,200 volts is equal to 10,450 amps at 480 volts". Would this be a a real world scenario or just how the math works out? I am trying to gain some insight as to what is actually "available" on our campus loop. Let me try to ask this way...... If all 22 xfmrs were 13,2 to 480V and all xfmrs were the same kVA and fused the same AND equal loads at each, would that 10,450 amps "be available" to divy up between them all?I am sure there is a lot more to this crappy question than I realize but never know how one might learn something.
Okay, let's break this down.
The Math
The core calculation you're presenting is based on the principle of conservation of power. Power (measured in kVA or MVA) is roughly constant through a transformer (minus some losses, which we'll ignore for simplicity). Power (kVA) = Voltage (kV) x Current (Amps) (This formula is actually using single phase voltage and current, a more complex formula is needed for 3 phase)Therefore: If you decrease voltage, you MUST increase current to maintain the same power.So, your calculation: 13,200 volts 380 amps = 5,016,000 VA (5016 kVA) 480 volts 10,450 amps = 5,016,000 VA (5016 kVA)So, mathematically, it's correct. The kVA remains constant.
Real-World Scenario - Understanding Availability
Now, the big question: Is that 10,450 amps at 480V truly "available" to be divvied up across your campus transformers?
The answer is: It depends. Here's why:1. Transformer kVA Ratings are the Key Limiter
Each transformer has a kVA rating. This is its maximum capacity. You can't pull more kVA (and therefore current) from a transformer than it's designed for. If each of your 22 transformers is rated at, say, 225 kVA (a common size), then you're limited to how much current each individual transformer can provide. To calculate the maximum current at 480V, use: Amps = kVA / Voltage. Since we are using single phase current in the example calculations, a correction for 3 phase current should be applied here. This example is also neglecting the voltage correction factor that is needed when calculating FLA, or full load amps. A more accurate formula to use would be: Amps = kVA / Voltage / 1.7322.
Source Capacity (The Loop)
The 380 amps at 13,200V is a potential bottleneck. Your campus loop (the 13.2kV distribution system) has a limited capacity. The loop's capacity (often dictated by the utility company) must be able to supply the total kVA of all your transformers. This is why it is important to understand the available kVA and current capacity of the 13.2kV feed.
3.
Feeder and Transformer Protection
You mentioned fuses. Fuses (or circuit breakers) are in place to protect the equipment from overloads and faults. They limit the amount of current that can be drawn. The fuses (or breakers) on the primary (13.2kV) side of the transformer are chosen based on the transformer's kVA rating and the inrush current it experiences when energized. The fuses on the secondary (480V) side protect the downstream equipment and wiring. The protection should be carefully coordinated to ensure that the smallest overcurrent situation opens only the necessary overcurrent device.
4.
Voltage Drop
As current flows through conductors (wires), there's a voltage drop. Excessive current draw can lead to significant voltage drops, which can negatively impact equipment performance (motors may struggle to start, lights dim, etc.). This is why conductor sizes are chosen based on the anticipated load.5.
Diversity and Load Factors
In reality, not all of your 22 transformers will be loaded to their maximum capacity simultaneously. This is where "diversity" comes in. A diversity factor is a ratio of the maximum non-coincident demand to the sum of the individual demands. If your diversity factor is, say, 0.7, it means that the peak demand of the entire campus is only 70% of the sum of the individual maximum loads. This is factored into design calculations.* Example: Each transformer is rated at 225 kVA. 22 Transformers x 225 kVA = 4950 kVA. But the actual peak demand on the system is only 4950 kVA x 0.7 = 3465 kVA.
6.
Conductor Ampacity
The wires connecting the 480V side of the transformers to the loads also have ampacity limits. You can't exceed the ampacity of the conductors without risking overheating and fire.
To determine what's truly "available" on your campus loop, you need to consider
The capacity of the 13.2kV loop
Contact your utility company. They can tell you the maximum available power (kVA or MVA) and the fault current levels at your point of connection.2.
The kVA ratings of each transformer.3. The fuse/breaker ratings on both the primary and secondary sides of each transformer.4. A load study
This involves measuring the actual current draw on each transformer over a period of time (typically a week or more) to determine peak demand and diversity factors. This will give you a realistic picture of how the system is being utilized.5.
Conductor sizes and ampacities of the 480V distribution system.6. Voltage drop calculations to ensure adequate voltage at the furthest points of the distribution system.In summary:
While the 380 amps at 13,200V equating to 10,450 amps at 480V is mathematically correct, you can't simply assume that you have 10,450 amps "available" at 480V to divide up. The actual capacity is limited by the transformer kVA ratings, the 13.2kV loop capacity, conductor ampacities, protection devices, and the diversity of your loads. A proper engineering study is needed to determine the true available capacity of your system. Flag for review