User: paullmullen, Location: Wisconsin
Asked on: Wednesday, October 22, 2025 at 8:33 am EDT
Answered on: Wednesday, October 22, 2025 at 8:33 am EDT
Question: I am installing a new residential service. 400A service to an "all electric" house. (No gas heat, two electric vehicles.) Wisconsin is on the 2017 version of NEC. Regardless, we will put emergency disconnects outside because it's just a good idea. I've shown a 1-line diagram of what we're planning. A picture is easier than a paragraph.My question is about the practical physical implementation of the green connections. There is no Ufer ground and the water connection is PVC, so ground rods it is. I plan a bare copper GEC from each 200 disconnect to the first ground rod and then a single GEC from Rod 1 to Rod 2. Any reason to do it another way? (I don't see the point of a second connection between the ground rods, for instance.)
Okay, let's break down your grounding plan for your new 400A residential service in Wisconsin (NEC 2017) and discuss practical implementation. Your approach sounds generally solid, but let's refine it for code compliance and best practices.
Understanding the Code (NEC 2017) 250.24(A)(1-5) General Requirements This section states that the grounded conductor must be grounded at each service. 250.50 Grounding Electrode System. Requires all available electrodes to be bonded together to form the Grounding Electrode System (GES). 250.52 Grounding Electrodes. Lists acceptable grounding electrodes. Since you lack a Ufer (concrete-encased electrode) and metallic water pipe, your primary electrodes are ground rods. 250.53(G) Supplemental Electrode Required. This likely applies. Since you don't have a Ufer or a metallic water pipe in contact with the earth for 10' or more, you must have at least two ground rods. 250.64(F) Installation to Electrode(s). The grounding electrode conductor must be installed in one continuous length without a splice. 250.66 Size of Alternating-Current Grounding Electrode Conductor. This table determines the minimum size of your GEC based on the size of your service entrance conductors. 250.166 Grounding Electrode Conductor for Multiple Services or Separately Derived Systems.Your Proposed Grounding Plan - Analysis and Refinements1. GEC from Each Disconnect to the First Ground Rod
This is the part where we need to get particular. In essence, you have 2 services. While the "main" service is 400 amps, you are splitting it into two 200 amp services. The GEC is calculated based on the service size. This means two GEC's. These two GEC's will both need to go to the ground rods.2.
Single GEC from Rod 1 to Rod 2
Code specifies that ground rods need to be bonded together. You propose to bond with a single connection between the two. This is permissable.
Here's a refined plan to consider
GEC Sizing
Determine the minimum GEC size according to NEC 250.66 based on your service entrance conductor size (the conductors coming into each of the 200A disconnects). Do not undersize this. You will need to consult with a licensed electrician to verify the sizing, but the main thing to understand is that each disconnect is its own service.2.
Continuous Run to Rod 1
Run a continuous, unspliced GEC from the grounding busbar in the first 200A disconnect enclosure directly to Ground Rod 1. Use appropriate connectors listed for grounding and bonding (e.g., compression connectors, acorn nuts).
3.
Continuous Run to Rod 1
Run a continuous, unspliced GEC from the grounding busbar in the second 200A disconnect enclosure directly to Ground Rod 1. Use appropriate connectors listed for grounding and bonding (e.g., compression connectors, acorn nuts).
4.
Bond Rod 1 to Rod 2
Run a GEC from Ground Rod 1 to Ground Rod 2. This creates the required bonding between the electrodes. 6' spacing is common, and per code is only required to be long enough that neither rod is shadowed by the other.
5.
Connections
Use only UL-listed connectors appropriate for direct burial. Avoid split-bolt connectors that aren't rated for burial. Exothermic welds (Cadwelds) are the premium connection method, but compression connectors are more common and acceptable if properly installed.6.
Ground Rod Installation
Drive the ground rods at least 8 feet into the earth, spaced at least 6 feet apart (or more) to avoid overlapping the ground resistance areas. Make sure the tops of the rods are flush with or below grade to protect them from physical damage.7.
Protection
If the GEC is subject to physical damage, protect it according to NEC requirements (e.g., using conduit).
Why This Refined Approach? Code Compliance
It adheres strictly to the NEC's requirements for multiple grounding electrodes and continuous GEC runs.
Redundancy and Fault Current Path
It provides a more robust and lower-impedance fault current path. Having two independent GEC runs back to Rod 1 helps ensure a solid grounding connection even if one path were to become compromised.
Future Expansion
It allows for potential future expansion or upgrades without requiring rework of the grounding system.
Important Considerations Local Amendments
Always check with your local Wisconsin AHJ (Authority Having Jurisdiction, i.e., your local building inspector) for any local amendments to the NEC. They may have specific requirements that go beyond the national code.
Professional Consultation
This is a critical electrical installation.
Seriously consider consulting with a licensed and experienced electrician in Wisconsin. They can review your entire electrical plan, perform load calculations, ensure code compliance, and properly install and test the grounding system. Improper grounding can be extremely dangerous and potentially deadly.* Inspection
Be prepared for inspection by the AHJ. They will verify the grounding system during the electrical inspection.
In summary, while your basic idea is on the right track, breaking out a separate GEC from each disconnect will satisfy NEC code. Flag for review