Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Test busway after splashed water

User: sssss, Location: VA

Asked on: Wednesday, October 22, 2025 at 11:01 am EDT
Answered on: Wednesday, October 22, 2025 at 11:01 am EDT

Question: There was an incident that water splashed to starline open channel busway. Would like to hear the recommendation of test procedure after moisture has been removed. Thanks.

Okay, water splashing onto a Starline Open Channel Busway is a serious incident that requires a thorough investigation and testing regime after the moisture has been removed. Here's a recommended test procedure, broken down into logical steps. Safety is paramount. De-energize and lockout/tagout the entire busway section affected before any inspection or testing.I. Immediate Actions & Inspection (After De-Energizing & Lockout/Tagout)


Documentation

Immediately document the incident. Include: Date and time of the incident. Precise location of the splash. Source of the water (e.g., rain, sprinkler, leak, etc.). Estimated amount of water. Direction of the splash. How long the water was present. Any initial observations (e.g., visible corrosion, pooling water). Photographs and/or video of the affected area. Names of personnel involved in the investigation. Record the model number and serial number of the busway segment(s) affected. Consult Starline documentation (installation manuals, specifications) for specific recommendations related to water exposure.2.

Visual Inspection



Detailed examination of the entire affected section of the busway



Busway Housing

Look for any signs of water ingress into the housing. Check for cracks, damage to seals, or areas where water may have penetrated.

Insulation

Inspect the insulation around the busbars for any discoloration, swelling, or signs of degradation.


Busbars

Look for any signs of corrosion, oxidation, or water stains on the busbars themselves. Pay close attention to joints and connections.

Plug-in Units/Tap Boxes

Carefully inspect any plug-in units or tap boxes that were connected to the busway in the affected area. Open them (after ensuring they are de-energized) and look for water ingress, corrosion, or damage.


Support Hangers

Check the support hangers for any signs of corrosion or damage.

Grounding

Inspect grounding connections for corrosion.


Use a flashlight and magnifying glass to aid in the inspection.
Document all findings with photos.3. Water Removal



Thorough drying

Use fans, heaters (low heat), and/or desiccant dehumidifiers to thoroughly dry the affected area. Ensure good ventilation to prevent moisture from being trapped. Avoid using high heat, which can damage insulation.

Consider using a vacuum cleaner with a narrow nozzle to remove any standing water.
Be patient! Drying can take several days, depending on the humidity and the amount of water. Monitor humidity levels with a hygrometer. Aim for a relative humidity below 50% before proceeding to the next steps.

II. Insulation Resistance Testing (Megger Testing)

This is crucial to determine if the insulation has been compromised.1.

Preparation

Ensure the busway section is completely dry. Verify with a hygrometer. Clean the busbars and insulation with a clean, dry cloth to remove any residual dirt or contaminants. Use a contact cleaner specifically designed for electrical components if necessary (follow manufacturer instructions). Disconnect any connected equipment (plug-in units, tap boxes, etc.) to isolate the busway for testing. Short all the phases together at one end of the busway section being tested. This will ensure that you are testing the insulation to ground.2.

Megger Testing Procedure



Use a calibrated megohmmeter (insulation resistance tester) with an appropriate voltage rating for the busway system.
(Consult Starline documentation for recommended test voltage - usually 500V or 1000V DC). Test each phase-to-ground and phase-to-phase. This means: Connect one lead of the megger to the shorted phases. Connect the other lead to the busway housing (ground). Apply the test voltage for a specified duration (usually 1 minute). Record the megohm reading. Repeat for each phase combination (A-B, A-C, B-C). To do this you need to remove the short that you installed earlier. Record all readings. Include the date, time, temperature, humidity, megger model, and test voltage. Compare the readings to the manufacturer's specifications or baseline readings (if available). Starline should have minimum acceptable insulation resistance values. Generally, a reading of 1 megohm or higher is considered acceptable, but always refer to the manufacturer's recommendations.3. Interpretation



Low Insulation Resistance

A low reading (below the manufacturer's specified minimum) indicates that the insulation has been compromised and is likely contaminated or damaged.
Do not energize the busway. Further investigation and possible replacement of the affected section are required.

Fluctuating Readings

Unstable or fluctuating readings can also indicate insulation problems.

Acceptable Readings

If the insulation resistance readings are within the acceptable range, proceed to the next step.

III. Hi-Pot Testing (Dielectric Withstand Test) -
Proceed with Extreme Caution and ONLY if Megger Testing is Acceptable



This test is more stressful to the insulation and should only be performed if the insulation resistance test passes and if recommended by Starline or a qualified electrical engineer.
It's designed to verify the dielectric strength of the insulation.1. Preparation

Ensure the busway section is completely dry and clean. Disconnect all connected equipment. Follow all safety precautions for high-voltage testing. Use appropriate PPE (insulating gloves, safety glasses, etc.). Have a second qualified person present during the test. Establish a clear communication protocol. Use a calibrated high-potential tester (hi-pot).

Ground the busway housing securely.
2. Hi-Pot Testing Procedure



Apply a voltage that is typically 75% of the factory test voltage.
Contact Starline for the exact factory test voltage for your busway model. Ramp up the voltage slowly. Maintain the test voltage for a specified duration (usually 1 minute). Monitor the current leakage. Excessive leakage current indicates insulation breakdown. Reduce the voltage slowly after the test duration. Record the test voltage, duration, and leakage current.3. Interpretation



Failure

If the insulation breaks down (excessive leakage current or voltage collapse), do not energize the busway. The insulation is damaged and must be repaired or the busway section replaced.

Pass

If the busway withstands the test voltage for the specified duration with acceptable leakage current, the insulation is considered to be in good condition.

IV. Ground Continuity Testing


Verify the integrity of the grounding system.
Use a low-resistance ohmmeter to measure the resistance between the busway housing and the grounding conductor. The resistance should be very low (typically less than 1 ohm). Check along the run, at the ends and any joints to insure proper continuity.

V. Torque Checks1. Check the torque on all connection points, including plug in units, joints etc. using a calibrated torque wrench to be sure the connections are tight.

VI. Re-Assembly & Functional Testing


Reassemble the busway system.
Carefully reconnect all plug-in units and tap boxes.2. Perform a visual inspection of all connections. Ensure that they are properly seated and tightened.3. Energize the busway system.4. Monitor the busway for any signs of overheating, vibration, or unusual noise.5. Measure the voltage and current at various points along the busway to ensure proper operation.6. Test each plug-in unit or tap box to verify that it is functioning correctly.7. Monitor the busway system for an extended period (e.g., 24-48 hours) to ensure that it is operating reliably.VII. Reporting & Documentation


Prepare a comprehensive report documenting all aspects of the incident, inspection, testing, and repairs.
Include:
Detailed description of the incident. Photographs and/or video. Inspection findings. Test procedures and results (including megger and hi-pot data). Any repairs or replacements made. Date and time of re-energization. Name and qualifications of personnel involved.2. Retain the report for future reference.Important Considerations



Consult Starline Directly

Contact Starline (Universal Electric Corporation) directly for their specific recommendations for testing and repair procedures following water exposure. They may have specific guidelines or requirements for their products.


Qualified Personnel

All testing and repairs should be performed by qualified and experienced electrical personnel who are familiar with busway systems and high-voltage testing procedures.

Safety

Strict adherence to safety precautions is essential when working with electrical equipment, especially after a water incident.


Replacement

In some cases, depending on the severity of the water damage, it may be necessary to replace the affected section of the busway.

Insurance

Notify your insurance carrier about the incident.


Preventative Measures

Consider implementing preventative measures to prevent future water incidents, such as improving drainage, installing barriers, or relocating sensitive equipment.

Disclaimer:
This information is for general guidance only. Always consult with qualified electrical professionals and follow the manufacturer's recommendations for testing and repair procedures. I am an AI and cannot provide professional electrical engineering advice. Flag for review

Previous Question Next Question