User: snik96, Location: Lynnwood, WA
Asked on: Wednesday, October 22, 2025 at 12:38 pm EDT
Answered on: Wednesday, October 22, 2025 at 12:39 pm EDT
Question: I'm working on a high-rise building with pressurization fans / elevator control room on the rooftop. These are fed from a panel that's also on the rooftop, that is part of the Legally Required distribution system.There is not a dedicated shaft available to route the panel feeder through vertically from the first floor, and maintain code-required 2-hour rating for smoke control.I've heard of pressurization fan branch circuits being routed through fire-rated stairwells to maintain 2-hour rating. My question is, can the same be done for a panel feeder? If I run the conduit for the panel on the roof vertically through a 2-hour rated stairwell, is that an acceptable solution for the smoke control feeder?
This is a complex question involving both the National Electrical Code (NEC) and local building codes. Here's a breakdown of the considerations and likely answers
Key Considerations:
NEC Requirements for Legally Required Standby Systems (LRSS) and Emergency Systems
These systems (which include smoke control) have stringent wiring requirements in NEC Article 700 and 701.
Local Building Code Requirements
Fire resistance ratings and allowed materials are often dictated by the building code (e.g., IBC) and local amendments.
Fire-Rated Construction
The definition of what constitutes "fire-rated" and the specific performance requirements vary.
Dedicated Space/Raceway
The NEC typically requires dedicated spaces or raceways for emergency and legally required standby systems. This is meant to protect the system from damage during a fire.
Integrity of the Fire-Rated Assembly
Any penetration of a fire-rated wall or floor (like a stairwell enclosure) must maintain the fire rating.
Likely Answer and Explanation
It's possible but highly depends on local interpretations and requires rigorous documentation and approval. It is not automatically acceptable.
Here's why:1. NEC 700.10(D) & 701.10(D): Wiring, Emergency System (700) and Legally Required (701): These sections generally require wiring for emergency and legally required standby systems to be installed in raceways that are either: Approved for the purpose
Meaning it is UL listed for fire-rated systems.
Encased in 2 inches (50.8 mm) of concrete
This provides physical protection and thermal insulation.
Fire-rated cable system
There are specific cable systems that are UL classified for 2-hour fire resistance.
Located in a fire-rated assembly
This is the key part. The stairwell is a fire-rated assembly, but the question is whether simply being in it is sufficient.2.
Interpretation of "Located in a Fire-Rated Assembly"
Strict Interpretation (Less Likely to be Accepted)
A strict interpretation of the NEC would suggest that "located in" means the raceway itself must contribute to the fire rating (e.g., be part of a UL-listed fire-rated assembly). This would likely require a specific fire-rated conduit system.
More Flexible Interpretation (Possible, but Requires Approval)
A more flexible interpretation is that the stairwell's fire rating provides adequate protection. This could be acceptable if:
Stairwell Design
The stairwell's fire rating is demonstrably sufficient to protect the conductors for the required duration (2 hours).
Physical Protection
The conduit run is physically protected from damage within the stairwell (e.g., surface-mounted high up, recessed, or protected by bollards).
Penetrations
Any penetrations of the stairwell enclosure (where the conduit enters/exits) are properly sealed with fire-stopping materials rated for at least 2 hours, maintaining the integrity of the fire-rated assembly.
Mechanical Damage Protection
The wiring within the stairwell must be protected from mechanical damage as well.3.
AHJ Approval is Crucial
You must get this approved by the Authority Having Jurisdiction (AHJ), which is the local electrical inspector and building official. Present a detailed proposal showing how you will meet the intent of the code and maintain the fire rating.4.
Documentation
Thorough documentation is essential. This includes: Detailed drawings showing the conduit route and fire-stopping details. Product data sheets for the conduit, fittings, and fire-stopping materials. Analysis of the stairwell's fire rating and ability to protect the conductors.5.
Fire-Rated Cable Systems
Consider using a fire-rated cable system specifically listed for 2-hour fire resistance. These systems are designed and tested to maintain circuit integrity during a fire. This is often the easiest and most reliable solution.
In summary
It's not a slam dunk. You can't just assume you can run the feeder through the stairwell. Consult with the AHJ early. Get their feedback on your proposed solution before proceeding with the design. Prioritize a fire-rated cable system or other explicitly approved method. These are typically easier to get approved. Ensure all penetrations are properly fire-stopped. Document everything thoroughly.Recommendation
First
Explore all other options. Is there any possible route, even a circuitous one, that could be dedicated? Can you upsize conductors and reduce voltage drop to allow for a longer but dedicated route? Can you locate the panel closer to the source?
Second
If routing through the stairwell is the only viable option, use a listed fire-rated cable system. It will be the most straightforward to get approved.
Third: If a fire-rated cable system isn't feasible, develop a detailed proposal for the AHJ outlining how you will maintain the fire rating and protect the conductors. Be prepared to provide substantial documentation and be flexible to accommodate their requirements.Good luck! This can be a tricky issue to navigate. Flag for review