User: Seven-Delta-FortyOne, Location: Humboldt
Asked on: Thursday, October 23, 2025 at 9:59 am EDT
Answered on: Thursday, October 23, 2025 at 9:59 am EDT
Question: This is inside the water tank, its purpose is to activate 2 water wells.Almost always they are wired into a contactor at the pump control.I have an in ground pull box where the branch circuits from the panel split to the two different wells. The pull box is right next to the water tank that is getting the float switch.Is there any reason that I can’t wire the float switch in series with the branch circuit conductors in the pull box? I can’t think of any reason not to, I just haven’t seen it done like that that I can remember.Each well pump has its own 20A branch circuit, so I would need 2 float switches of course.
You're thinking about wiring the float switch directly in series with the 20A branch circuit conductors feeding each well pump, before the contactor in the pump control panel. While technically it might work (with the right switch rating), it's a very bad idea and likely a code violation. Here's why
Why it's a Bad Idea and Likely a Code Violation:
1. Switch Rating
Standard float switches are not typically rated for 20A, continuous duty, at the voltages used for well pumps (usually 120V or 240V). Even if they momentarily interrupt the starting current, the constant current draw of the well pump would quickly overheat and destroy them. Using a switch outside its rated capacity is a safety hazard and violates electrical codes.2.
Arcing and Contact Wear
Interruption of current, especially inductive loads like motors, causes arcing. A low-rated float switch will quickly develop pitted, burned contacts, leading to switch failure and unreliable operation.3.
Safety
Putting a low-rated, water-exposed switch directly in the high-current path of a well pump circuit creates a significant electrocution hazard. If the switch fails or develops a leak, you could have 240V directly exposed to the water.4.
Loss of Motor Protection
The existing well pump control panel (with the contactor) likely provides overload protection for the motor. Bypassing this with your in-line float switch setup removes that critical safety feature. The motor could burn out from overload without tripping a breaker.5.
Unintended Consequences
If one of your in-line float switches fails open, that well pump will be permanently disabled. A properly wired float switch system (using a contactor) is designed to gracefully shut down both pumps based on water level, not disable them individually.6.
Control Philosophy
You're attempting to use the float switch as a power disconnect for the pump, which is not its intended function. Float switches are designed as control signals.
The Correct Way to Wire It (Using a Contactor)
The correct way to wire this is to use the float switch to control the coil of a contactor in the existing well pump control panel. Here's how:
Float Switch Signal
The float switch becomes a low-current control signal to the contactor coil.
Contactor Provides Power
The contactor, properly sized for the well pump's current draw, provides the actual switching of the well pump's power.
Safe, Low-Voltage Control
The float switch operates at a low voltage (typically 24V or 120V, depending on the contactor coil voltage), making it much safer.
Connecting to the Existing Pump Control Panel
The best approach is to locate the well pump control panel for each pump. There are likely control wires already ran to the well pump, that are used to control the contactor. You will likely need to run a new low voltage control wire from the tank to the pump control panel, in order to connect the float switch. The exact method to do this depends on the existing control panel wiring.
Important Safety Note: Working with electrical systems, especially well pumps and water, is dangerous. If you're not completely comfortable and knowledgeable about electrical wiring and safety procedures, hire a qualified electrician.In summary, wiring the float switch in series with the 20A branch circuit conductors is a hazardous and incorrect approach. The proper method is to use the float switch as a control signal* for a contactor, ensuring safe and reliable operation of your well pumps. Flag for review