Question: I understand that emt rmc and imc are considered egc and no egc of the wire type is required. How come the NEC hasn’t extended that requirement to say that in places where these conduits are subject to physical damage and or accessible like in attics roofs and claw spaces an egc of the wire type should be installed
You've hit upon a point that's debated and understood differently by many electricians and inspectors. Here's a breakdown of why the NEC handles metallic conduit systems as grounding conductors and why your suggestion about supplemental EGCs in certain environments isn't explicitly a requirement
Why Metallic Conduits are Considered EGCs:
Low Impedance Path
EMT, RMC, and IMC, when properly installed with listed fittings, create a low-impedance path back to the source. This low impedance is crucial for quickly clearing ground faults, tripping the overcurrent protection (circuit breaker or fuse).
Continuous Electrical Connection
The key to relying on conduit as an EGC is maintaining a continuous, electrically conductive connection throughout the entire raceway system. This is achieved through listed fittings designed for grounding and bonding.
NEC Recognition
The NEC recognizes metallic raceways as acceptable grounding conductors in various sections, including Article 250.118.
Established History
The practice of using metallic conduit as the EGC has a long history and has proven effective in preventing electrical shock and fire hazards when properly implemented.
Why Supplemental EGCs Are Not Always Required (Despite Concerns)
NEC Emphasizes Proper Installation
The NEC places a strong emphasis on proper installation and maintenance of the metallic raceway system. This includes: Using listed fittings specifically designed for grounding. Tightening all connections securely. Protecting the raceway system from corrosion. Ensuring continuous metallic continuity.
Risk Assessment
The NEC is a consensus-based document, and the decision to not mandate supplemental EGCs across the board reflects a complex balance of factors:
Cost
Requiring a separate EGC in every circuit adds significant cost to installations.
Labor
Installing a separate EGC adds time and labor.
Material
Extra copper wire use.
Practicality
In many installations, a properly installed metallic raceway system provides a robust and reliable grounding path.
Observed Failure Rates
The NEC committee weighs the actual observed failure rates of metallic raceway systems serving as EGCs against the cost and burden of requiring supplemental conductors. While failures can occur, they are often attributed to improper installation or maintenance, not inherent flaws in the system itself.
Specific Requirements Exist
While a blanket requirement for supplemental EGCs isn't in place, the NEC does have specific requirements for supplemental grounding in certain situations, which suggests the committee understands the added layer of safety it can bring in certain applications.
Redundancy
In many systems, other metal parts, such as enclosures and junction boxes, are bonded to the raceway system. This creates redundant grounding paths.
Addressing Your Concerns (Physical Damage, Accessibility, Attics, Roofs, Crawlspaces)
Your concerns about physical damage, accessibility, attics, roofs, and crawl spaces are valid. Here's how the NEC and best practices often address them:1.
Protection from Physical Damage (300.4 and specific Articles)
The NEC requires raceways and cables to be protected from physical damage. This can involve: Using heavier-gauge conduit (e.g., RMC) in areas prone to impact. Installing raceways in protected locations. Using guards or barriers to shield the raceway.2.
Corrosion Protection (300.6)
The NEC requires raceways to be suitable for the environment. This is especially important in damp or corrosive environments (e.g., some crawl spaces, coastal areas): Using corrosion-resistant materials (e.g., PVC-coated RMC, stainless steel). Applying protective coatings.3.
Bonding Jumpers (250.92, 250.96, etc.)
Bonding jumpers are often required around expansion joints, couplings, or other discontinuities in the raceway system to maintain electrical continuity.4.
Local Amendments/Jurisdictional Interpretations
Some local jurisdictions do amend the NEC to require supplemental EGCs in specific situations they deem warrant it. It's crucial to check your local electrical codes.5.
Professional Judgment & Risk Assessment
Electricians and engineers are expected to exercise professional judgment and consider the specific conditions of each installation. If they believe that a supplemental EGC is necessary to ensure safety and reliability, they should recommend and install one, even if it's not strictly required by the NEC.
Why Not Explicitly Mandate Supplemental EGCs in Those Locations? Subjectivity
Defining "subject to physical damage" and "accessible" is subjective and difficult to write into code without creating overly broad and burdensome requirements.
Cost-Benefit Analysis
The NEC committee has likely determined that the cost of mandating supplemental EGCs in all attics, roofs, and crawl spaces outweighs the potential benefits, given the existing requirements for proper installation and protection of raceways.
Potential for Misinterpretation
A blanket requirement could be misinterpreted, leading to unnecessary installations in some situations and inadequate installations in others.
Important Considerations and Recommendations
Always Follow Manufacturer's Instructions
Use fittings that are listed for grounding.
Tighten Connections Properly
Loose connections are a major cause of grounding failures. Use the proper torque.
Visually Inspect
When possible, visually inspect the raceway system to ensure it is intact and free from damage or corrosion.
Consider Supplemental EGCs
In harsh environments, critical applications, or situations where you have concerns about the integrity of the raceway system, consider installing a supplemental EGC for added safety and peace of mind. This is often the best approach.
Test the Grounding Path
Use a low-resistance ohmmeter to test the grounding path between the furthest point on the circuit and the main panel. This can help identify any discontinuities or high-resistance connections.*
Stay Updated with Code Changes: The NEC is updated every three years. Stay informed about any changes that may affect your work.In conclusion, the NEC's reliance on metallic conduits as EGCs is based on the principle that a properly installed and maintained system provides a low-impedance fault current path. While concerns about physical damage and accessibility are valid, the NEC addresses these concerns through requirements for protection, corrosion resistance, and proper installation practices. Electrical professionals are encouraged to use their judgment and consider supplemental EGCs when necessary to ensure the safety and reliability of the electrical system. Remember to always consult the latest edition of the NEC and local amendments for specific requirements. Flag for review