User: Primarycontractinginc., Location: Massachusetts
Asked on: Thursday, October 23, 2025 at 11:27 am EDT
Answered on: Thursday, October 23, 2025 at 11:47 am EDT
Question: Electrical Inspector is telling me I must use 350KCMIL for Parallel feeders to the 400amp meter feeding 2 -200amp services (2 family House) for the over head service? I have pulled 300's Aluminum in Parallel ?
Okay, let's break down the electrical inspector's requirement and see if the 300 kcmil aluminum conductors you've installed meet the code. This involves understanding ampacity, conductor sizing, and relevant sections of the National Electrical Code (NEC).
Understanding the Inspector's Reasoning
The inspector is likely focusing on several factors:1. Total Load and Ampacity
Even though you have two 200 amp services, the feeder to the meter must be sized to handle the potential total load of both services simultaneously. While it's unlikely both services will draw their maximum 200 amps at the same instant, the feeder must have sufficient ampacity to handle a significant portion of that load. The NEC typically allows for demand factors, but the starting point is still based on the sum of the service ratings.2.
Overcurrent Protection
The feeder conductors must be protected by an overcurrent device (the main breaker at the meter). The size of this overcurrent device dictates the minimum ampacity required of the conductors.3.
Conductor Ampacity Tables
The NEC has specific tables (NEC Table 310.16, adjusted for derating factors if applicable) that list the allowable ampacities of different conductors based on their size, insulation type, and installation conditions (e.g., temperature rating of terminations, ambient temperature, number of current-carrying conductors in a raceway).
4.
Parallel Conductors
When using parallel conductors (two or more conductors connected together to serve as a single conductor), each conductor must be sized to handle its proportionate share of the total load. (NEC 310.10(H)5.
Voltage Drop
Long runs of conductors can experience significant voltage drop, which can affect the performance of electrical equipment. The inspector may be considering voltage drop in addition to ampacity. (Informative Annex D provides examples)6.
Local Amendments
It's crucial to remember that local jurisdictions can amend the NEC. The inspector may be enforcing a local amendment that specifically requires a minimum conductor size for service feeders of this capacity.
Analyzing Your Situation (300 kcmil Aluminum)1. Ampacity of 300 kcmil Aluminum
According to NEC Table 310.16, the ampacity of 300 kcmil aluminum conductors with a 75°C insulation rating (a common rating) is typically around
255 amps. Always refer to the actual table for the specific insulation type you used (THHN, XHHW, etc.). Make sure the terminals are rated to at least 75°C, otherwise you must use the 60°C ampacity.2. Parallel Conductors
You are using two 300 kcmil aluminum conductors in parallel per phase. This means the combined ampacity of each phase conductor is 255 amps x 2 =
510 amps (assuming 75°C).3. 400 Amp Service Meter
The 400 amp meter base means the upstream conductors must be rated for 400 amps, minimum.4.
Demand Factors
With only 2-200 amp services, a demand factor can be used (NEC 220.82).
5.
350 KCMIL Aluminum Ampacity: According to NEC Table 310.16, the ampacity of 350 kcmil aluminum conductors with a 75°C insulation rating (a common rating) is typically around 280 amps.
Why the Inspector Wants 350 kcmil The 400 amp meter requires 400 amp conductors before you take any demand factors. The inspector may be following a local requirement that dictates a minimum wire size or has calculated the load with a different method. The inspector could be concerned with voltage drop over your 300-foot run, a 350kcmil conductor has less resistance, therefore, less voltage drop.
What You Need to Do1. Communicate with the Inspector
The most important step is to politely and professionally discuss the situation with the inspector. Ask specifically why they are requiring 350 kcmil aluminum. Ask them to cite the specific NEC section or local amendment they are using as justification.2.
Review Your Load Calculation
Double-check your load calculation for the entire two-family dwelling. Ensure you've considered all potential loads (lighting, appliances, heating/cooling, etc.) and applied any applicable demand factors.3.
Provide Documentation
Prepare a clear and concise load calculation to present to the inspector. Include all assumptions and references to relevant NEC sections. Also, provide the conductor specifications (insulation type, temperature rating) to show the ampacity you calculated.4.
Consider Voltage Drop Calculations
Perform voltage drop calculations for your 300-foot run. This can be done using online voltage drop calculators or formulas from the NEC (Informative Annex D). If voltage drop is excessive with 300 kcmil, it could justify the inspector's requirement for larger conductors.5.
Review Local Amendments
Check your local electrical code for any amendments that might affect conductor sizing.6.
Consider Options
If the inspector is firm on the 350 kcmil requirement and you believe it's not justified by the NEC or a valid local amendment, you have a few options:
Appeal the Decision
Most jurisdictions have an appeals process for electrical inspections.
Consult with a Licensed Electrical Engineer
A professional engineer can review the situation, perform load calculations, and provide an expert opinion to support your position.
Important Considerations Safety First
Always prioritize safety and follow the inspector's instructions if there's a concern about safety.
Documentation is Key
Keep accurate records of all communications with the inspector, load calculations, and conductor specifications.
Professionalism
Maintain a professional and respectful attitude throughout the process.
In summary:
Your 300 kcmil may be sufficient. It really boils down to what the inspector is basing his decision on. Most likely its the total ampacity of the conductors. Talk with the inspector and understand exactly what the issue is. Then refer to the appropriate section in the NEC and local requirements.Disclaimer: I am an AI chatbot and cannot provide electrical advice. Consult with a qualified electrician or electrical engineer for all electrical work. Flag for review