User: Necnerd, Location: colorado
Asked on: Thursday, October 23, 2025 at 7:16 pm EDT
Answered on: Thursday, October 23, 2025 at 7:16 pm EDT
Question: I don't do much residential anymore and I'm trying to understand how to label and do my grounding/bonding for my the electrical system emergency disconnect for a single family dwelling fed by feeders.This is a farm house. the utility supplies a meter and service disconnect at a pole about 75 ft from the house.there is a 200amp main lug panel fed with four wires from the service disconnect on the utility pole.this main lug panel feeds another 100amp panel on the outside of the house.since the house is fed with feeders I would use 225.41 and label the 100 amp panel on the outside of the dwelling emergency disconnect.does the service disconnect at the pole also need to be labled emergency disconnect, service disconnect?im assuming my grounding and bonding would all be the same.the poco provided meter/ service disconnect would need to have a gec connected to two ground rods and have the grounded/ grounding conductors bondedthe 200a main lug panel on the back side of utility pole fed with four wires would have grounded and grounding conductors isolatedthe 100a main disconnect panel on the outside of the dwelling fed with four wires would have grounded and grounding conductors isolated. Because this is a seperate structure i would require one more ground rod at this location.the dwelling has a metal undergroundwater piping system where the main line comes in. can i bond this anywhere on the metal water pipe back to the sub panel ground bar? 250.104(3) i would size the bonding jumper using 250.102(c) looks like if the panel is fed with 1/0 i can get away with running #6 copper to the water pipe?I really appreciate all of you in this forum and would like to thank anyone in advance who replies or offers any input! hopefully I'm understanding the nec correctly and have a solid plan... thanks again!
Okay, let's break down the grounding, bonding, and labeling requirements for your farmhouse electrical system, based on the NEC (specifically the 2023 edition, which is what I'll assume unless otherwise noted).1. Labeling Disconnects 100A Disconnect at the House
You are correct. The 100A disconnect on the exterior of the house MUST be labeled as the Emergency Disconnect. The exact wording should follow 225.41: "EMERGENCY DISCONNECT, SERVICE DISCONNECT"
The Label Must be Legible and Durable The Label must be on the outside of the Panel
Service Disconnect at the Pole
This is also important and frequently missed. While the pole-mounted disconnect IS the service disconnect, labeling is still important. You should label this disconnect as "SERVICE DISCONNECT." Consider including the address it serves to avoid any confusion.
2. Grounding and Bonding Considerations
Utility Pole Service Disconnect (Meter/Disconnect)
Grounding Electrode System (GES)
You're right, this needs a GES. Two ground rods are typically required (250.53(A)(3)). If soil resistance is > 25 ohms after the first rod you'll need a second. A single rod can be used if supplemented by additional grounding such as concrete encased electrode.
GEC (Grounding Electrode Conductor)
Connect the GEC from the equipment grounding bar in the disconnect to the ground rods. Size the GEC per 250.66 based on the size of the ungrounded service conductors.
Bonding
The grounded (neutral) conductor MUST be bonded to the enclosure/equipment grounding bar at this location. This is your service point.
200A Main Lug Panel (MLP) on the Pole (Fed with Feeders)
Grounding and Bonding Separation
You're correct again. The grounded (neutral) and grounding (equipment grounding) conductors MUST be kept SEPARATE in this panel.
No Bonding Jumper
Do NOT bond the neutral conductor to the enclosure.
Equipment Grounding Conductor (EGC)
Run a properly sized EGC (equipment grounding conductor) with the feeder conductors from the service disconnect at the pole to this 200A MLP. The size is based on the overcurrent protection for the feeder (250.122).
100A Emergency Disconnect Panel at the House (Fed with Feeders)
Grounding and Bonding Separation
As this is a separate structure, the grounded (neutral) and grounding (equipment grounding) conductors MUST be kept SEPARATE.
Grounding Electrode System (GES)
This panel REQUIRES its own grounding electrode system (250.32). This can be one ground rod, or other electrodes. If using a ground rod, it generally requires two, unless you can demonstrate low resistance to ground per 250.53(A)(3).
GEC (Grounding Electrode Conductor)
Connect the GEC from the equipment grounding bar to the ground rod(s). Size this GEC per 250.66 based on the size of the feeder conductors.
Equipment Grounding Conductor (EGC)
Run a properly sized EGC with the feeder conductors from the 200A MLP on the pole to the 100A disconnect at the house.
No Bonding Jumper
Do NOT bond the neutral conductor to the enclosure in this panel.
3. Water Pipe Bonding
Bonding Location
You can bond the metal water piping system to the grounding busbar in the 100A emergency disconnect panel (250.104(A)). The goal is to create a low-impedance path to ground.
Sizing the Bonding Jumper
Correct! Use 250.102(C) to size the bonding jumper. The size is based on the size of the service conductors. If your feeder conductors from the 200A MLP to the 100A disconnect are 1/0 AWG copper, then a #6 AWG copper bonding jumper is sufficient for bonding the water pipe. Make sure the bonding clamp is listed for grounding.
Bonding to the Nearest Available Point
You can bond to the water pipe at the nearest accessible point where the pipe enters the dwelling.
Important Considerations and Potential Issues
Feeder Conductor Size
Make sure your feeder conductors between the pole-mounted disconnect and the 200A MLP, and between the 200A MLP and the 100A disconnect, are properly sized for the load and overcurrent protection. Voltage drop is also a key factor due to the distance involved.
Overcurrent Protection
Verify that the overcurrent protection devices (breakers) are sized appropriately for the conductors and equipment they are protecting.
Load Calculation
It's crucial to perform a thorough load calculation to ensure that your 200A and 100A panels have sufficient capacity. Farms often have unique load requirements.
Agricultural Buildings
Be mindful of Article 547 (Agricultural Buildings). This could impact your wiring methods and equipment choices, especially if the farmhouse is used for agricultural purposes (even partially). This article can have very stringent requirements.
Local Amendments
Always check with your local electrical inspector for any local amendments to the NEC that may apply in your area. Some jurisdictions have specific requirements for grounding and bonding farm buildings.
Documentation
Keep good records of your grounding and bonding connections, including the location of ground rods, the size and type of conductors used, and any test results. This will be helpful for future maintenance and troubleshooting.
In SummaryYou're on the right track! Just remember to meticulously follow the NEC requirements for grounding, bonding, and separation of neutral and ground at feeder-fed panels. The labeling is essential. Focus on creating a safe and reliable electrical system for the farmhouse. Always consult with your local electrical inspector to ensure compliance with all applicable codes and regulations. Flag for review