User: SlackJawedYokel, Location: Washington
Asked on: Thursday, October 23, 2025 at 11:25 pm EDT
Answered on: Friday, October 24, 2025 at 12:01 am EDT
Question: I have RTU that has a rating of 52 amps with an MCA of 52 amps. Going by the code it looks like I can use #6 thhn dual rated because the 75 degree rating is 65 amps and for a continuous load of 52 amps it meets the 80% correction factor. Is there something I am missing or does this work out just perfectly?
You're close, but there are a few crucial points to consider to ensure you're fully compliant with the National Electrical Code (NEC)
Here's a breakdown of why #6 THHN might work, and the critical areas to double-check:
MCA (Minimum Circuit Ampacity)
The MCA is the minimum ampacity required for the circuit conductors supplying the RTU. You cannot go smaller than this value. In your case, MCA is 52A.
Conductor Ampacity
You're planning to use #6 THHN, which has an ampacity of 65 amps at 75°C according to NEC Table 310.16. (Assuming it is copper)
125% of Continuous Load
Because RTUs are generally considered continuous loads, you must size the conductors to at least 125% of the RTU's rated current. In your case, 52 amps 1.25 = 65 amps This means your conductors must be rated for at least 65 amps, which #6 thhn can do.
However, here's where you need to be extra careful
Termination Temperature Ratings
This is the most common point of failure.
Check the RTU's Nameplate and Breaker
The equipment's nameplate (RTU) and the circuit breaker feeding the RTU will specify the maximum temperature rating for the conductor terminations (usually 60°C or 75°C).
NEC 110.14(C)(1)
This section of the NEC is absolutely critical. It states that the conductor ampacity used in calculations can't exceed the temperature rating of the weakest link in the system (terminals, devices, etc.). So, even if your #6 THHN is rated for 75°C, if the RTU's terminals are rated for only 60°C, you must use the 60°C ampacity rating for your calculations.
Example
If your RTU is only rated for 60°C, #6 THHN is only rated for 55 amps. In this case, your wire is too small.2.
Ambient Temperature Correction
NEC Table 310.15(B)(1)
If the ambient temperature where the conductors are installed is higher than 30°C (86°F), you must apply a correction factor to the ampacity of the conductors. Hot attics, rooftops, and areas near the RTU itself are common places where ambient temperatures exceed 30°C.
Example
If your ambient temperature requires a 0.88 correction factor, a 65A #6 THHN conductor is now only rated for 57.2A. This is still big enough since we only need 52A but it is important to consider.
3.
Number of Conductors in a Raceway or Cable (Adjustment Factors)
NEC Table 310.15(B)(3)(a)
If you have more than three current-carrying conductors in the same raceway or cable, you may need to apply an adjustment factor to the conductor ampacity. This reduces the allowable ampacity to prevent overheating.
Typically not an issue for RTUs
Most RTU circuits consist of three current-carrying conductors (L1, L2, L3) and a ground. However, if you're running multiple RTU circuits in the same conduit, this becomes a factor.
Summary and Recommendation
Check the RTU's nameplate and breaker for the termination temperature rating. This is the most important step.2. Determine the ambient temperature where the conductors will be installed. If it's above 30°C, apply the correction factor.3. Verify the number of current-carrying conductors in the raceway or cable. If there are more than three, apply the adjustment factor.
In conclusion, #6 THHN might* work for your 52A MCA RTU if the termination temperature is 75°C and you do not need to apply ampacity correction/adjustment factors. However, it's absolutely essential to check the factors mentioned above to ensure you're fully compliant with the NEC and maintaining a safe installation. If you're unsure, it's always best to err on the side of caution and upsize the conductors.
When in doubt, consult a qualified electrician. They can perform the necessary calculations and ensure your installation meets all applicable codes and regulations. Flag for review