User: rhy_fraser, Location: Woodward, OK, USA
Asked on: Friday, October 24, 2025 at 8:45 am EDT
Answered on: Friday, October 24, 2025 at 8:46 am EDT
Question: Need a little clarification for bonding jumper.... Our contractor ran a 4/0 bare ground from equipment to a plate which ties into the grounding grid. Since this was done in EMT they installed a #6 bonding jumper from the conduit to the plate as well. Our client has concern that this jumper will not provide sufficient protection if someone were around the conduit and a fault would occur. I can't find anywhere in the code concerning a bonding jumper for the raceway when bonding an EGC specifically, only thing I found deals with bonding conductors and equipment... I feel that #6 would be fine, but just want to be sure that workers are protected. Thoughts?
Okay, let's break down the scenario and address your client's concerns. You're correct that the NEC doesn't explicitly require a bonding jumper in this specific situation (EGC run in EMT), but the reason the jumper is there is important.
Understanding the Setup
4/0 Bare Ground (EGC)
This is your primary Equipment Grounding Conductor. Its purpose is to provide a low-impedance path back to the source for fault current, allowing the overcurrent protective device (circuit breaker or fuse) to trip quickly and clear the fault. It's bonded to the equipment enclosure and, ultimately, the grounding electrode system.
Grounding Plate
This is likely a connection point for the building's grounding electrode system (ground rods, Ufer ground, etc.). The 4/0 connects the equipment to this grounding system.
EMT Conduit
The EMT is serving as a raceway to protect the 4/0 EGC. However, EMT isn't considered part of the EGC in this scenario because you have a dedicated EGC.
#6 Bonding Jumper (from EMT to Plate)
This is where the confusion often arises. This jumper is intended to bond the EMT to the grounding system, preventing it from becoming energized in the event of a fault.
Addressing the Client's Concerns
Your client's concern is valid. While the 4/0 provides the main fault current path, the EMT could become energized if the 4/0 were to fail (cut, loose connection, etc.) and a fault occurred within the equipment and the EMT came into contact with the energized part.
Why the #6 Bonding Jumper is Likely Adequate (But Requires Verification)
Purpose of the Jumper
The #6 bonding jumper's primary purpose isn't to carry the entire fault current back to the source. It's to keep the EMT at the same potential as the grounding system and prevent a voltage difference that could cause a shock hazard.2.
NEC Table 250.102(C)(1)
This table is used to size bonding jumpers to the EGC, not the service conductors.3.
Fault Current Path
In most cases, even if the 4/0 EGC failed, the fault current would likely still have a path to ground through other means (building steel, other connected equipment, etc.). The #6 jumper provides an additional low-impedance path.4.
Coordination
The size of the bonding jumper is relative to the size of the circuit conductors feeding the equipment. The jumper helps ensure that the OCPD will clear the fault and that the equipment will not become energized.
However, here's what you need to do to confirm the #6 is adequate and provide assurance to your client
Verify the Size of the Circuit Conductors
Find the conductors that are feeding the equipment. The size of these conductors is critical.2.
Use Table 250.102(C)(1)
This table is a little tricky. It's for sizing the supply side bonding jumper based on the size of the supply conductors. The table lists the equivalent conductor to be used for bonding jumpers.3.
Examine the Fault Current Path
If you have any exposed metallic water lines, or other metallic items near the conduit, these may present a parallel fault current path to ground.4.
Consider a Ground Fault Detection System
For critical applications, a ground fault detection system can quickly detect and clear ground faults, minimizing the risk of shock hazards.5.
Document Your Analysis
The most important thing is to document your assessment. Show the calculations, the code references, and the reasoning behind your conclusion. This provides a record for your client and for future reference.
Example Scenario
Let's say the equipment is fed by 200 amp conductors. According to Table 250.102(C)(1), you need a 6 AWG copper or 4 AWG aluminum for the bonding jumper. So the #6 would be sufficient.
Key Takeaways: The #6 bonding jumper is likely adequate, but you must verify it based on the size of the circuit conductors using Table 250.102(C)(1). The jumper's purpose is to bond the EMT and prevent voltage differences, not to carry the entire fault current. Document your analysis and provide it to your client. Consider a ground fault detection system for enhanced safety in critical applications.By carefully analyzing the situation and documenting your findings, you can address your client's concerns and ensure a safe installation. Flag for review