Topic: Coordination study dependent upon exact feeder cable length?

User: Isaiah, Location: Baton Rouge

Asked on: Friday, October 24, 2025 at 6:14 pm EDT
Answered on: Friday, October 24, 2025 at 6:15 pm EDT

Question: I was told today that the coordination study had not yet been done because they on didn’t have the exact cable length of 480V feeders.Yet the one lines have all been completed - from switchgear to MCCs, Panelboards and Transformers with CB sizes and trip settings assigned for protection.It seems odd that they were unable to perform the study.In the past I’ve seen estimated feeder lengths utilized to determine short circuit and CB/Fuse sizes and the studies were done well in advanceEnviado desde mi iPhone utilizando Tapatalk

You're right to find that situation odd. It's definitely possible to, and often preferred to, perform a preliminary coordination study with estimated cable lengths. Here's a breakdown of why, and what likely happened

Why it's odd to be completely stalled without feeder lengths:
Reasonable Estimates

Cable lengths can be estimated reasonably well, especially if one-line diagrams exist showing the routing of feeders. Walking the site, reviewing architectural/structural plans, and comparing to similar installations allows for a decent approximation. Even a rough estimate is better than no estimate.


Impact of Length

While cable length does affect fault current levels and arc flash energy, the difference between an estimated length and the final, exact length often doesn't drastically change the protective device settings needed for coordination and protection. Minor adjustments might be needed later, but the overall strategy is usually sound. The biggest impact of cable length is voltage drop, which is a separate calculation.

Coordination Strategy

Coordination studies establish the
relationships between protective devices. They determine how circuit breakers (or fuses) will selectively trip, isolating faults and minimizing outages. These relationships are built on relative current and time settings. While the exact settings might need tweaking with precise lengths, the strategy is established early on.

Early Detection of Problems

A preliminary coordination study can uncover potential issues like:

Insufficient available fault current

This is often a problem at the end of long feeders. If this is predicted early, you can address it with different equipment, paralleled conductors, etc.


Coordination conflicts

Discovering coordination problems early allows for more design flexibility to resolve them (e.g., changing transformer impedance, adjusting CT ratios, upgrading breakers).

Risk Mitigation

Waiting until the last minute to do the coordination study is risky. What if it reveals a major flaw requiring significant redesign or equipment changes? It's much easier to fix these problems early in the project.

Why
might they be waiting? Potential Explanations (and concerns)



Over-Reliance on Accuracy

The engineer performing the study might be overly focused on having perfectly accurate data. This could be due to inexperience, a rigid process, or fear of making mistakes. While accuracy is desirable, it shouldn't paralyze the project.

Poor Communication/Coordination

There might be a breakdown in communication between the electrical designer/installer and the engineer performing the study. The installer might not be providing the information (or updating it as needed).


Cost Concerns

Perhaps the scope of work was not appropriately defined and priced for the coordination study to allow for preliminary stages.

Specific Software Limitations

Some coordination software packages may require certain data input to allow for the modeling to occur - perhaps it must have these values for short circuit analysis calculations.


Potential Hidden Issues

Perhaps there are other unknowns in the system design that are affecting the ability to accurately model and perform the coordination study - for example, generator size or UPS capacity.

They plan to do it later anyway

Perhaps they performed a short circuit study to determine CB sizes and trip settings - without actually running a coordination study.

What you should do

1.

Inquire Directly

Ask the engineer performing the coordination study (or the project manager) directly:
"What specific challenges are you encountering that prevent you from doing a preliminary coordination study using estimated feeder lengths?" "What level of accuracy do you need in the feeder lengths to proceed?" "What are the potential risks of delaying the coordination study until after the exact feeder lengths are known?"* "Could we use 'typical' or 'conservative' cable length assumptions to get started?"2.

Review the Scope of Work

Check the contract or scope of work for the coordination study. Does it explicitly require exact cable lengths, or does it allow for preliminary work based on estimates?3.

Offer Solutions

If the issue is getting accurate estimates, offer to help. Suggest walking the site, reviewing plans, or contacting the electrical installer for preliminary lengths.4.

Escalate (if necessary)

If you're not getting satisfactory answers or if the delay is impacting the project schedule, escalate the issue to your project manager or the client. Explain the potential risks of waiting.5.

Consider a Second Opinion:
If you have serious concerns, consider getting a second opinion from another electrical engineer experienced in coordination studies.In summary, waiting for exact cable lengths to start a coordination study is unusual and potentially risky. A preliminary study using estimated lengths is a best practice that can save time, money, and prevent problems later in the project. You should investigate the reasons for the delay and push for a more proactive approach. Flag for review