Topic: 208 three phase

User: 618electrician, Location: St. Louis

Asked on: Friday, October 24, 2025 at 6:19 pm EDT
Answered on: Friday, October 24, 2025 at 6:20 pm EDT

Question: 208 a phase A 10 amps phase B 5 amps neutral amps = ??????????????????????????????????????????????????????????????????????????????????????

To determine the neutral current in a three-phase system, we need more information about the system's configuration (e.g., wye or delta) and whether the load is balanced or unbalanced. However, we can estimate a maximum possible neutral current for an unbalanced wye system. The maximum neutral current would be the imbalance - that is, the largest single phase current when the others are zero. Worst-Case Scenario (Unbalanced Wye)

In the worst possible case, all the current from phase A (10 amps) and Phase B (5 amps) returns through the neutral.
Neutral Current = √(A^2 + B^2) = √(10^2 + 5^2) = √(100+25) = √125 ≈

11.18 Amps
Important Considerations



Balanced vs. Unbalanced

This calculation assumes an
unbalanced load. If the load were perfectly balanced (equal current in each phase, with a 120-degree phase shift), the neutral current would ideally be zero. In reality, loads are rarely perfectly balanced.

Phase Angle

The calculation above assumes that the A and B currents are in phase with each other. In a balanced three-phase system they would have a 120 degree phase difference. If the current in the phases are not in phase, the formula is more complex.*

Harmonics

Harmonic currents (multiples of the fundamental frequency, like 3rd, 5th, 7th harmonics) can also contribute significantly to the neutral current, especially the 3rd harmonic. The above calculation does not consider harmonics.

Without further information about the specific system, it's impossible to give a definitive answer. However, 11.18 amps is a reasonable upper bound for the neutral current.