Question: Looking for Advice on 100A → 200A Service Upgrade + Panel RelocationHey everyone, ive lurked on here for a while but first post. Looking for some guidance from those with more experience in service upgrades and panel relocation.I’ve done a fair amount of residential electrical work including panel upgrades, however I don't have experience with the outside work of panel upgrades, like weather heads, meter bases, etc.Current SetupHouse has 100A serviceMain panel: old Square D QO (QOBW20M100), located in a bedroom closet, has about 14 circuitsSubpanel: 40A Murray fuse box located in the garageHouse is about 60 ft across (panel-to-panel distance)Existing loads: pool pump, normal household circuits, multiple window/wall ACs, air compressor.Future loads: potential hot tub + EV charger/chargers.Service drop could enter from either side of house (same distance from pole) no obstructions/height issues.Planned UpgradeThe plan is to upgrade the service to 200A, but I’m debating the smartest way to manage the panel locations.Main QuestionWhich approach would you take?Option AMove service drop to the garage where a service entrance actually makes senseInstall new 200A panel in the garageConvert the existing 100A panel in the bedroom closet into a subpanelOption BUpgrade existing service location (still in closet — I believe this is not compliant with current code for panel location) and a larger physical panel would not fit.Make the garage panel a larger 100A or 200A subpanelI previously had a licensed electrician quote the job (about $3,000). He claimed he had utility approval for the meter relocation, but then ghosted me after a couple calls.What I’ve Already DoneI decided to get some of the prep work done myself:Purchased 100 ft of 1-1-1-3 SER Al and a 100 amp QO breakerPicked up a brand new Homeline 200A convertible panel value pack (Marketplace score: $90)My thought was to replace the 40A fuse subpanel in the garage with the new panel but keep it fed as a subpanel for nowThe existing subpanel is fed with what looks like #6 or #8 copper MC — I planned to remove and repurpose that and run the 1-1-1-3 SER in its placeQuestions for the Pros Is Option A (moving service to garage) the best long-term and most code-compliant solution?Any issues or things to think about with temporarily installing the new 200A panel as a subpanel besides the obvious like operate grounds and neutral bars?Thanks in advance — appreciate any thoughts, code references, or advice before I move forward.
Okay, this is a good rundown of the situation. Let's break down the options and address your questions.
Analysis of Options A and B Option A (Move Service to Garage)
Pros
Best Long-Term Solution
This is generally the preferred approach. It gets the service entrance where it should be (in a garage or utility area) and provides ample space for future expansion.
Code Compliance
This is the most likely to be code-compliant, especially regarding working clearances around the panel and the accessibility of the main disconnect. (I'll emphasize this later, but you MUST confirm with your local AHJ about panel location requirements)
Future-Proofing
You'll have a 200A panel in the garage, which is ideal for your future hot tub, EV chargers, and air compressor.
Subpanel Conversion
Converting the existing 100A panel to a subpanel is straightforward.
Cons
More Complex Installation
Relocating the meter base and service entrance conductors is more work than a straight upgrade. This is likely why the electrician you contacted ghosted you; it requires more coordination with the utility company and more specialized skills.
Potential Permit Issues
Meter relocation can sometimes be more scrutinized by the AHJ (Authority Having Jurisdiction, i.e., your local building department).
Option B (Upgrade Existing Service Location)
Pros
Simpler Installation
Less work involved in the service entrance upgrade itself.
Potentially Less Costly (Initially)
If you ignore long term costs and future planning.
Cons
Code Violations Likely
Installing a 200A service in a bedroom closet is almost certainly a code violation. There are strict rules about working clearances, accessibility, and the types of locations where panels can be installed.
DO NOT DO THIS WITHOUT A LOCAL ELECTRICIAN EVALUATING YOUR OPTIONS. Limited Future Expansion
Fitting a larger panel into the closet space will be difficult or impossible.
Potential Safety Issues
A panel in a bedroom closet is a potential fire hazard and makes it difficult to access in an emergency.
Subpanel Limitation
Even with a 100A subpanel in the garage, you might still be limited by the 100A service to the house.
The Verdict: Option A is almost always the better choice. The upfront hassle is worth the long-term benefits of code compliance, safety, and future expansion capabilities.
Addressing Your Specific Questions1. "Is Option A (moving service to garage) the best long-term and most code-compliant solution?" Yes, almost certainly. It's the most logical and forward-thinking approach.2. "Any issues or things to think about with temporarily installing the new 200A panel as a subpanel besides the obvious like operate grounds and neutral bars?" Yes, several
Neutral-Ground Bonding
Make absolutely sure the neutral and ground bars are separated in the 200A panel when it's being used as a subpanel. The neutral and ground should only be bonded at the main service panel. This is critical for safety.
Wire Size Adequacy
Is the #6 or #8 copper MC really adequate for a 40A fuse box? It seems undersized. Confirm its ampacity and replace it if necessary. Remember, you're planning to use 1-1-1-3 SER, which is good.
Overcurrent Protection
Ensure the breaker feeding the "temporary" subpanel is properly sized to protect the feeder conductors. You don't want a 100A breaker feeding undersized wire.
Inspection
While you might think this is temporary, it's best to have it inspected. This gives you peace of mind and makes the eventual service upgrade smoother.
Important Considerations Before Moving Forward1. PERMITS ARE REQUIRED! This is not a small DIY project. You absolutely need a permit from your local building department. This protects you, your home, and your neighbors.2. UTILITY COMPANY
You must contact your utility company before you do anything involving the service entrance. They have specific requirements for meter base location, service entrance cable size, and grounding. They are the ones who will disconnect and reconnect the power.3.
LOCAL ELECTRICAL INSPECTOR
Talk to your local electrical inspector before you do anything. They are the ultimate authority on what is allowed in your area. Panel location requirements can vary significantly from one jurisdiction to another.4.
LICENSED ELECTRICIAN (Again)
Seriously consider hiring a licensed electrician, especially for the service entrance upgrade. This is not just about knowing how to wire; it's about understanding code, dealing with the utility company, and ensuring a safe and reliable installation. The $3,000 quote you got previously may have been a fair price for the scope of work. Prices are inflated now; expect to pay closer to $5,000-8,000 if you hired out now.5.
Bonding and Grounding
Service entrance bonding and grounding are critical for safety. Make sure you understand the requirements for grounding electrodes (ground rods, water pipe, etc.) and bonding all metal parts of the electrical system.6.
Trenching (if applicable)
If you're running service entrance conductors underground, you'll need to dig a trench to the proper depth, and you'll need to use the correct type of conduit.7.
Load Calculation
Although you are going to 200A, perform a load calculation before upgrading. This is required by code and ensures that the 200A service is adequate for your existing and future loads.8.
Panel Location Considerations: Check your local and National Electrical Code (NEC) for rules about panel clearance and accessibility. This includes minimum heights, distances from flammable materials, and required working space in front of the panel. In general, panels should be readily accessible and not located in bathrooms, closets, or over stairs. You mentioned a closet; while that's not ideal, it might be grandfathered in IF you keep the panel in the same location. Moving it somewhere else may trigger the new location needing to comply with current code, making it more of a headache.
Action Plan1. Contact the Utility Company
Inquire about their requirements for a 200A service upgrade and meter relocation.2.
Contact the Local Building Department
Discuss your plans with the electrical inspector.3.
Re-evaluate Electrician Quotes
Get multiple bids from qualified, licensed electricians after you've talked to the utility company and the building department.4.
Load Calculation
Perform a thorough load calculation.5.
Start with Permits
Once you have a solid plan, get the necessary permits.6.
Safety First
If you decide to do some of the work yourself, be extremely cautious and follow all safety precautions. Disconnect the power before working on any electrical circuits.
Regarding the Materials You've Already Purchased The 1-1-1-3 SER aluminum cable is a good choice for a 200A service. The 200A Homeline panel is a good starting point. Make sure it's rated for service entrance use (most are).* Repurposing the existing #6 or #8 MC cable is questionable. Verify its ampacity and replace it with adequately sized conductors if necessary.Good luck with your project! Take your time, do your research, and prioritize safety. This is a significant electrical upgrade, and it's worth doing it right. Flag for review