User: ADELECTRICWORKS, Location: New York
Asked on: Saturday, October 25, 2025 at 12:30 pm EDT
Answered on: Saturday, October 25, 2025 at 12:39 pm EDT
Question: hi, I have job in medical clinic to contact shunt trip breaker with disconnect switch.I don’t have any diagram as it’s old breaker. Qj23b200.It has 4 wires 1 white and 3 black. Blacks are marked as A, S and T.I am attaching photos for the breaker and switch.Thank you
Okay, I've reviewed the photos you've provided. Here's a breakdown of how a shunt trip breaker works, what those terminals likely are, and how to likely interface it with a disconnect switch for remote tripping, along with important warnings
Understanding Shunt Trip Breakers
Purpose
A shunt trip breaker is a circuit breaker that can be tripped (turned off) remotely by applying a voltage signal to a dedicated coil within the breaker. This is used for emergency shutdowns, fire alarm systems, or other situations where you need to de-energize a circuit from a distance.
How it Works
The shunt trip coil is energized by a separate control circuit (often low voltage, like 24VDC, 120VAC, or 240VAC). When the correct voltage is applied to the shunt trip coil, it mechanically releases the breaker's latching mechanism, causing it to trip.
Identifying the Terminals (Based on Common Practice and Your Markings)
Given the markings on your wires (A, S, T) and the common configurations, here's my best guess. THIS IS NOT A GUARANTEE. VERIFY WITH THE MANUFACTURER OR A QUALIFIED ELECTRICIAN. S & T (or A & T)
These are very likely the terminals for the shunt trip coil. You apply voltage between these terminals to trip the breaker. The specific voltage depends on the coil's rating. This is the most critical to determine.
A (or S)
This could be a common or neutral for the shunt trip coil, but it could also be something else entirely (like a test point - highly unlikely but theoretically possible).
White
This is likely a neutral or ground associated with the shunt trip circuit itself. It is NOT necessarily the neutral or ground for the main breaker power supply. Do not assume it connects to the building's neutral.
WARNINGS: EXTREMELY IMPORTANT1. VOLTAGE HAZARD
Working with electrical equipment is dangerous. Voltages present in that breaker can be lethal. If you do not have experience and expertise, contact a qualified electrician immediately.2.
IDENTIFICATION IS CRITICAL
Incorrectly wiring the shunt trip can damage the breaker, create a fire hazard, or prevent it from working in an emergency. You MUST positively identify the voltage rating of the shunt trip coil before applying any voltage. Contact the breaker manufacturer (or search online for the QJ23B200 datasheet and specific shunt trip option details) to confirm the voltage required for tripping.3.
TESTING
After any wiring changes, test the shunt trip function CAREFULLY. Make sure the breaker trips reliably and that the control circuit voltage is appropriate.4.
LOCKOUT/TAGOUT
Before doing any work on the breaker, ALWAYS de-energize the circuit, lock out the disconnect switch, and tag it properly. Verify the circuit is de-energized with a voltage meter.5.
ASSUME NOTHING
Do not assume wire colors or terminal markings are correct. Verify everything with testing and documentation.6.
THE PICTURE IS ONLY FOR THE SWITCH. PLEASE BE CAREFUL ABOUT WORKING WITH HIGH VOLTAGES.How to Integrate with the Disconnect Switch
The typical goal is to use the disconnect switch to interrupt the shunt trip circuit, thereby causing the breaker to trip. Here's the general idea:1. Identify the Shunt Trip Voltage
As emphasized above, this is the most important step. Determine the voltage required to activate the shunt trip (e.g., 24VDC, 120VAC, 240VAC).2.
Create a Control Circuit
You'll need a power supply that provides the correct voltage for the shunt trip coil. This power supply needs to be protected with a fuse of the correct rating for the load.3.
Wire the Disconnect Switch in Series
The disconnect switch needs to be wired in series with the shunt trip coil's power supply. Here's the concept: Power Supply (+) ----> Disconnect Switch (Normally Closed Contacts) ----> Shunt Trip Terminal (e.g., "S") Shunt Trip Terminal (e.g., "T") ----> Power Supply (-)When the disconnect switch is CLOSED (normal operation), the circuit is complete, and the shunt trip is ready to trip the breaker if the circuit were energized. When the disconnect switch is OPENED, it breaks the circuit, de-energizes the shunt trip coil, and the breaker trips.
Example Scenario (Illustrative - You MUST Verify Voltages)
Let's assume (for this example only*) that the shunt trip requires 120VAC.1. You would use a 120VAC power supply.
2. You would run one wire from the 120VAC supply's hot (line) terminal to one of the normally closed contacts of your disconnect switch.3. You would run the wire from the other normally closed contact to the shunt trip terminal you identified as the voltage input (e.g., "S").
4. You would run a wire from the shunt trip terminal identified as the neutral or return (e.g., "T") back to the 120VAC power supply's neutral terminal.
NEXT STEPS (Before You Do Anything)1. Find the Breaker's Documentation
Search online for "QJ23B200 datasheet" or "QJ23B200 shunt trip." Look for manufacturer specifications, wiring diagrams, and voltage ratings. Include information about the specific shunt trip option installed in the breaker.2.
Contact the Manufacturer
If you can't find documentation, contact the breaker manufacturer directly. Provide the model number (QJ23B200) and any other identifying information on the breaker. Ask for the wiring diagram for the shunt trip option.3.
Engage a Qualified Electrician
If you are not 100% confident in your ability to safely and correctly wire this shunt trip, hire a qualified electrician who is familiar with industrial controls and shunt trip breakers.4.
TEST, TEST, TEST
After any wiring, test the shunt trip functionality with the breaker disconnected from any load. Verify that the correct voltage is present at the shunt trip terminals when the disconnect switch is closed, and that the breaker trips reliably when the switch is opened.
In summary, proceed with extreme caution. Verify the voltage requirements of the shunt trip coil before applying any power. If in doubt, consult a qualified electrician.
Good luck, and please be safe. Flag for review