User: PanelGuy1315, Location: Louisville
Asked on: Monday, October 27, 2025 at 9:02 am EDT
Answered on: Monday, October 27, 2025 at 9:03 am EDT
Question: Hi all,I'm designing a control panel that will contain (3) 480v 3ph input to 24vdc Power supplies. I'm accustomed to having a breaker for each load (power supply), but in this case I'm wondering if I can just have a single 10A Allen Bradley 140UT MCCB (UL489) with through the door disconnect operator that will protect all 3 power supplies. The input current of the power supplies is (1.3A + 1.3A + 0.65A = 3.25A) and the wire size would be #14 to all supplies.Do I need individual protection for each PS?Thanks for your time!
Okay, let's break down the code requirements and best practices for protecting these power supplies in your control panel.
Code Considerations (Primarily NEC/NFPA 70) 110.3(B) - Listing and Labeling
You must use equipment that is listed and labeled for its intended purpose. This is fundamental.
110.14 - Electrical Connections
Pay attention to the temperature ratings of your conductors and termination points (breakers, power supply terminals, etc.). Make sure the conductors are sized appropriately for the ampacity AND the termination temperature rating.
240.4(D) - Small Conductor Protection
This is a critical section. It limits the overcurrent protection for smaller conductors. Specifically, for #14 AWG copper, the overcurrent protection device shall not exceed 15 amps unless a specific exception applies. This is the most significant hurdle to your plan.
240.21 - Location in Circuit. Addresses where overcurrent protection is allowed in a circuit, and generally must occur where conductors receive their supply. 409 - Industrial Control Panels
This is the main article covering industrial control panels. It references other articles, including those mentioned above. It will also address short-circuit current ratings (SCCR) for the panel.
670 - Industrial Machinery
If this panel is supplying power to an industrial machine, Article 670 may apply.
Arguments for and Against a Single BreakerArguments FOR a Single Breaker (Potentially, but with Challenges)
Total Load
Your total load is 3.25A, which is well below the 10A rating of the breaker. From a purely load perspective, the breaker has ample capacity.
Convenience
A single disconnect/breaker is simpler and potentially less expensive.
Arguments AGAINST a Single Breaker (More Likely the Correct Approach)
Small Conductor Protection (NEC 240.4(D))
This is the BIGGEST issue. While your total load is low, you're using #14 AWG.
NEC 240.4(D) generally requires that #14 AWG be protected by a 15A or smaller overcurrent device. Your 10A breaker is smaller than 15A, so on the surface it seems okay, BUT...2. Power Supply Listing and Instructions
This is critical.
You MUST consult the power supply manufacturer's documentation. The power supply's UL listing (or other applicable listing) will specify the required overcurrent protection. The manufacturer may require individual fusing or circuit breakers per power supply. It's very common for power supplies to require individual branch circuit protection. If the manufacturer's instructions conflict with other code requirements, it can create a tricky situation that requires careful evaluation. The manufacturers information will supercede some of the general rules, especially if those general rules are there to protect equipment in a general sense, and not necessarily personnel.3. Selective Coordination
If you have a single breaker protecting all three power supplies, a fault in one power supply will trip the main breaker, shutting down all three. This may or may not be acceptable from an operational standpoint. Individual breakers or fuses offer better selective coordination, isolating the fault to the affected power supply and minimizing downtime.4.
SCCR
Your control panel needs a Short-Circuit Current Rating (SCCR). This is the maximum fault current the panel can safely withstand. The SCCR is determined by the lowest rated component in the panel. Individual breakers might help you achieve a higher SCCR than relying on a single breaker, particularly if the power supplies themselves have low SCCR ratings. This is less of a concern with a 10A breaker, but it's something to consider.5.
Cost is Negligible
The cost difference to use (3) appropriately sized breakers as compared to one is generally not significant.
Best Practice and Recommendation
Given the code requirements, the power supply manufacturer's instructions, and best practices for reliability, here's what I recommend:1.
Consult Power Supply Documentation
This is the absolute first step. Read the power supply manuals and look for specific overcurrent protection requirements. They may specify a particular type of fuse or circuit breaker and its maximum rating.2.
Individual Protection
The safest and most code-compliant approach is generally to provide individual overcurrent protection for each power supply. This is almost certainly what you'll need to do based on the fact that this is best practice, and the manufacturers recommendation.3. Breaker or Fuse Sizing
Base the breaker or fuse size on the power supply documentation. If the power supply documentation does not specify, use the table in NEC 430.52.
4.
Consider In-Rush Current
Power supplies have an inrush current when they are first energized. You might need to use a breaker or fuse with a time-delay characteristic (e.g., a "D" curve breaker) to prevent nuisance tripping.
Example Scenario
Let's say your power supply documentation specifies a maximum 6A fast-acting fuse for input protection. In that case, you would: Use #14 AWG wire from the main disconnect to three individual fuse holders (or miniature circuit breakers - MCBs). Install 6A fuses (or 6A MCBs) in each fuse holder.
Revised Wiring Diagram (Conceptual)480V 3PH Input ----> 10A Main Breaker (w/ Disconnect) ----> Terminal BlockTerminal Block ----> #14 AWG ----> 6A Fuse/MCB ----> Power Supply 1Terminal Block ----> #14 AWG ----> 6A Fuse/MCB ----> Power Supply 2Terminal Block ----> #14 AWG ----> 6A Fuse/MCB ----> Power Supply 3(Power Supplies Output 24VDC)
Important Considerations
Short-Circuit Current Rating (SCCR)
Make sure the components you choose (breakers, fuses, power supplies) have an adequate SCCR for your application. The SCCR of the entire panel must be clearly labeled. The lowest rated part is the overall rating, and there are methods to increase it, but the easiest way to is to ensure the SCCR rating of the lowest rated part is greater than the available fault current.
UL 508A
If you are building an industrial control panel, UL 508A is the standard that provides specific requirements for the design, construction, and testing of these panels.
Local Codes and AHJ
Always check with your local electrical codes and the Authority Having Jurisdiction (AHJ) for any specific requirements in your area. They have the final say.
Professional Engineer: For complex installations or if you're unsure about any aspect of the design, it's always a good idea to consult with a qualified professional engineer.In summary, while a single breaker might seem simpler initially, the code requirements for small conductor protection and, most importantly, the power supply manufacturer's instructions strongly suggest using individual overcurrent protection for each power supply. This approach offers better safety, reliability, and compliance. Always consult the power supply documentation! Flag for review