Topic: Flicker Pst and Plt Caculations in EAF - How does affect X/R relation and how to calculate it

User: Joao, Location: portugal

Asked on: Monday, October 27, 2025 at 9:26 am EDT
Answered on: Monday, October 27, 2025 at 9:26 am EDT

Question: As per IEC 61000-3-7 the equation is the following:However X/ relation is not shown in that equation. How does X/R affect it? How to calculate with that variable?

You're right, the simplified formula for Pst in IEC 61000-3-7 doesn't explicitly show X/R. This is because the simplified formula is often based on assumptions or simplifications to make calculations easier for quick estimations. The X/R ratio (reactance to resistance ratio) does impact flicker severity and should be considered for more accurate assessments, particularly in systems with a significant inductive component.Here's how X/R affects flicker and how you can incorporate it into calculations

Why X/R Matters for Flicker:
Voltage Drop Phase Angle

The X/R ratio influences the phase angle of the voltage drop caused by load changes. A high X/R ratio (predominantly inductive circuit) means the voltage drop will have a larger reactive component (voltage lagging current by a significant angle). This affects the way the voltage fluctuates and, consequently, the flicker perception. A purely resistive load (low X/R) causes a voltage drop that's mostly in phase with the current.


Resonance

High X/R can be associated with potential resonant conditions, which can amplify voltage fluctuations and worsen flicker.

System Impedance

X/R is a key parameter characterizing the impedance of the supply network. The network impedance plays a direct role in determining the voltage drop caused by load changes. A higher impedance (especially inductive) leads to greater voltage fluctuations and increased flicker.

How to Incorporate X/R into Flicker Calculations (Beyond the Simplified Formula)

1.

Complex Impedance Calculations

The most accurate approach is to calculate the

complex impedance
of the supply network at the point of common coupling (PCC) where the fluctuating load is connected. This requires knowing both the resistance (R) and reactance (X) of the network. Impedance (Z) = √(R² + X²) Phase angle (Φ) = arctan(X/R) The complex impedance is then Z∠Φ.You can often find R and X information from utility company data, system studies, or by estimation based on the type and length of cables/conductors, transformer ratings, etc.2. Using More Complete Flicker Calculation Methods (Software Simulations)

Specialized power system analysis software (e.g., DIgSILENT PowerFactory, ETAP, PSS/E, ATP) is designed to accurately model flicker. These programs allow you to input the complete network impedance (R and X) and the characteristics of the fluctuating load (amplitude, frequency, waveform) and then simulate the resulting voltage fluctuations and calculate Pst. This is the most reliable method for complex systems.3.

Approximations and Correction Factors

If you don't have detailed network data, you can use approximate methods or correction factors. For example:

Typical X/R Values

For a low-voltage system, you might assume an X/R ratio of around 0.5 to 1.
0. For medium-voltage systems, the X/R ratio could be higher (e.g., 2 to 5). High-voltage systems can have even higher X/R ratios. Use these as a very rough estimate, and err on the side of caution (higher X/R).


Crucially, understand that these are generalizations and may not be suitable for your specific situation.
Sensitivity Analysis

If you have a range of possible X/R values, perform a sensitivity analysis. Calculate Pst using the simplified formula but then repeat the calculation with different assumed X/R values (e.g., the lowest and highest plausible X/R). This will help you understand how sensitive the flicker levels are to variations in X/R.4.

Empirical Data and Measurement

If possible, measure the voltage fluctuations at the PCC directly using a flicker meter compliant with IEC 61000-4-15. This is the most accurate way to determine Pst. Measurements automatically account for the system's actual impedance and the characteristics of the fluctuating load.

Modifying the Simplified Formula (Carefully)

It's difficult to directly incorporate X/R into the simplified Pst formula without making some potentially inaccurate assumptions. The simplified formula is often based on a specific network impedance angle. However, you might be able to use a correction factor, but this requires careful consideration:

Calculate Pst using the simplified formula.
This is your baseline. Estimate the voltage drop at the PCC due to the fluctuating load. This requires calculating the current change caused by the load and using the network impedance (Z∠Φ) to determine the resulting voltage drop (ΔV∠θ). Determine the Phase Angle Difference

Calculate the phase angle difference (θ) between the voltage drop and the supply voltage. A purely resistive load would have θ = 0. A highly inductive load would have θ close to 90 degrees.


Consider a "Worst-Case" Correction

A large θ can make flicker worse (depending on the frequency and waveform of the fluctuations). A conservative (but potentially overly cautious) approach is to assume the worst-case phase angle. However,

be very careful with this approach
, as it's easy to over-estimate flicker levels.

Example of a Conceptual (but simplified) Correction (Use with Caution)

This is a highly simplified and potentially inaccurate example for illustrative purposes only:1.

Calculate Pst (base) using the original simplified formula.
2. Estimate ΔV (voltage drop) at the PCC and the phase angle θ between the voltage drop and the supply voltage. (From complex impedance calculations).3. A very rough "correction factor" could be based on cos(θ)

Pst (corrected) = Pst (base) / cos(θ) (if cos(θ) is close to 0, this correction blows up and is invalid)

Important Cautions



Simplifications

The simplified formula for Pst is a simplification. Using it with a naive correction factor can introduce significant errors.

Network Complexity

Real-world power systems are complex. Impedances change with frequency and operating conditions. Simplified calculations can miss important effects.


Regulation and Standards

Always adhere to local regulations and standards regarding flicker limits. Contact your utility company for specific requirements and data.*

Consult an Expert

For critical applications or if you are unsure about the accuracy of your calculations, consult with a qualified power system engineer.

In summary:


While the simplified Pst formula doesn't explicitly show X/R, it's implicitly present through the network impedance. For accurate flicker assessment, especially in systems with significant inductance, use more sophisticated methods like complex impedance calculations, power system simulation software, or direct measurement. Avoid relying on overly simplistic corrections to the basic Pst formula unless you fully understand the potential inaccuracies. Always prioritize compliance with relevant standards and regulations. Flag for review