Question: John Guys, I just had an inspection, and the inspector told me to derating my wire because my entire race way is over 24”My understanding is that I have one 12” conduit from panel#1 running into a gutter and have another 12” conduit from gutter to panel#2, and the total CCC is 24 counts, I should be ok with the “shout conduit rule”, am i right? Or as the inspector says, the total raceway is over the limits?Thanks
Okay, let's break this down and address your question about conductor derating due to conduit fill and the "short conduit rule."Understanding the Inspector's Concern
The inspector is likely concerned with NEC (National Electrical Code) Article 310.15(C)(1) and Table 310.15(C)(1). This section deals with adjustment factors for more than three current-carrying conductors (CCCs) in a raceway or cable. When you have more than three CCCs, the ampacity of the conductors needs to be reduced (derated) to prevent overheating.
Key Concepts Current-Carrying Conductors (CCCs)
Wires that carry current under normal operating conditions (e.g., ungrounded [hot] conductors and neutral conductors if carrying significant harmonic current). Grounding conductors (equipment grounds) and, in most cases, neutral conductors in a balanced system are not counted as CCCs.
Raceway
A channel designed expressly for holding wires, cables, or busbars (e.g., conduit, tubing, wireways, etc.).
Ampacity
The current, in amperes, that a conductor can carry continuously under the conditions of use without exceeding its temperature rating.
Derating
Reducing the ampacity of a conductor based on various factors, such as the number of CCCs in a raceway.
The "Short Conduit Rule" (NEC 310.15(C)(1)(a) Exception No. 2)
This is the exception you're referring to, and it's crucial. It says that adjustment factors for multiple CCCs do not apply if:1. The adjustment factors are not applied to conductors in a raceway having a length not exceeding 24 inches (610 mm).2. The raceway is used to protect conductors from physical damage or support conductors.
Analyzing Your Situation
You have: 12" conduit from Panel #1 to gutter 12" conduit from gutter to Panel #2 24 total CCCsHere's where the interpretation is critical: The Inspector's Argument
The inspector is likely seeing the entire run (Panel #1 to Gutter to Panel #2) as one raceway that is longer than 24 inches. Therefore, they are saying the derating rules apply because you have 24 CCCs in that combined raceway.
Your Argument (and where you might be correct)
You're arguing that each individual conduit run (Panel #1 to Gutter, and Gutter to Panel #2) is 12 inches and therefore qualifies for the exception. This means the derating rules do not apply within each of those 12-inch sections.
Who is Right?
The correct interpretation depends on how the inspector views the system and how the Code is applied. Here's what to consider:1. Definition of Raceway
The NEC defines a "raceway" as "an enclosed channel of metal or nonmetallic materials designed expressly for holding wires, cables, or busbars, with additional functions as permitted in this Code." The key here is the enclosed channel.2.
Is the Gutter Part of the Raceway? If the gutter is properly sized and designed as a wiring trough or auxiliary gutter according to Article 376, it could be argued that the entire run (conduit-gutter-conduit) is a single raceway. If it's not a properly installed and sized gutter, then you have two separate raceways connected by a junction point (the gutter itself).
Here's a breakdown of potential scenarios and how to handle them
Scenario 1: Gutter is a Proper Auxiliary Gutter (Well-Sized, Meets NEC 376 Requirements) In this case, the inspector likely has a stronger argument. The Code could be interpreted to mean the entire length is one raceway. Therefore, derating would be required for 24 CCCs based on Table 310.15(C)(1). Scenario 2: Gutter is NOT a Proper Auxiliary Gutter In this case, you have a stronger argument. The gutter is essentially a junction box, and you have two separate 12-inch raceways. The "short conduit rule" should apply to each raceway individually. Therefore, no derating is required within each 12-inch conduit run. However, the gutter itself will need to have sufficient room to handle all conductors and splices following the rules in Article 314.
How to Proceed1. Review NEC Article 376 (Auxiliary Gutters)
Determine if your gutter meets the requirements for a proper auxiliary gutter (size, construction, labeling, fill limitations).2.
Clarify with the Inspector
Politely ask the inspector for the specific section of the NEC they are citing for the derating requirement. Ask them to explain why they view the entire run as one raceway.3.
Document Everything
Keep detailed notes of your conversation with the inspector. Take pictures of the installation.4.
Consider a Second Opinion
If you disagree with the inspector's interpretation, consider consulting with a qualified electrical engineer or another experienced electrician for a second opinion. A letter from a licensed engineer supporting your interpretation can be very helpful.5.
Offer Alternatives
If the inspector insists on derating, explore alternative solutions. Can you: Increase the size of the conduit and conductors to reduce the number of CCCs in each conduit? Use conductors with a higher temperature rating (e.g., THHN/THWN-2) to allow for a higher ampacity after derating? Modify the system to reduce the total number of CCCs? Properly convert your gutter to a Auxiliary gutter per the NEC table.
Important Considerations Safety First
Always prioritize safety. Even if you technically comply with the Code, ensure the installation is safe and won't cause overheating or other problems.
Local Amendments
Be aware that local jurisdictions may have amendments to the NEC that could affect the interpretation of these rules. Check with your local building department.
Inspector's Authority
While you have the right to question an inspector's interpretation, remember that they have the authority to enforce the Code. It's often easier to work with them to find a mutually acceptable solution.
In summary, whether you need to derate or not depends on whether the entire conduit-gutter-conduit run is considered one raceway or two separate raceways. This hinges on whether the gutter meets the requirements for an auxiliary gutter per NEC Article 376. Gather information, communicate with the inspector, and be prepared to offer alternative solutions if necessary. Flag for review