Topic: Manual says 8 AWG for a 30 A dryer?

User: marmathsen, Location: Seattle, Washington ...ish

Asked on: Monday, October 27, 2025 at 4:13 pm EDT
Answered on: Monday, October 27, 2025 at 4:13 pm EDT

Question: Just curious if any one else has run across this?I have a client who needs me to run a circuit for an electric dryer in a residence. LG model DLEX4000B.I was sent a link to the electrical requirements portion of the instructions by the general contractor and was surprised to see the statement:If the branch circuit to appliance is 15 ft. (4.5 m) or less in length, use UL (Underwriters Laboratories) listed No.-10 AWG wire (copper wire only), or as required by local codes. If over 15 ft. (4.5 m), use UL-listed No.-8 AWG wire (copper wire only), or as required by local codes.

Yes, that's an unusual and, frankly, concerning electrical requirement from LG for their DLEX4000B dryer. You're right to be surprised. Here's a breakdown of why it's unusual and what you should do

Why it's Unexpected and Potentially Problematic:
Standard Practice

The National Electrical Code (NEC) and common electrical practice dictate wire size based on the circuit's ampacity (the amount of current it's designed to carry) and the length of the run
only when voltage drop is a concern. Typically, a 30-amp dryer circuit uses 10 AWG copper wire, regardless of length, unless the run is exceptionally long and voltage drop calculations show a need for larger wire.

Voltage Drop Concern?
Their specification heavily implies a voltage drop issue. However, needing to jump to 8 AWG copper after only 15 feet is extremely aggressive and suggests either a very poorly designed appliance that is extremely sensitive to voltage fluctuations, or an overabundance of caution on LG's part. "Copper Wire Only" Emphasis

This is standard and correct. Aluminum is not permitted for this particular application.


Local Codes Always Prevail

Their disclaimer that local codes take precedence is important.

What You Should Do (in order of importance)


Check the Dryer's Nameplate

The MOST important thing is to verify the dryer's nameplate amperage. The nameplate, usually located on the back of the dryer, states the maximum amperage draw of the appliance. This trumps anything in the manual. It will say something like "Rated Current: 24 Amps" or "Maximum Circuit Amperage: 30 Amps".2.

Consult Your Local Electrical Inspector

This is your best course of action. Show the inspector the LG manual's wire sizing requirement and the dryer's nameplate information. They will have the final say on what is acceptable in your jurisdiction and have the most practical experience with local conditions. Explain your concerns and ask for their guidance. Be prepared to provide the length of the circuit run.3.

Voltage Drop Calculation (If Necessary)

If the inspector isn't immediately definitive, or if the circuit run is exceptionally long (e.g., over 75 feet), perform a voltage drop calculation. The NEC recommends a maximum voltage drop of 3% for branch circuits. You can use online voltage drop calculators or consult an electrical engineer. This calculation will take into account the amperage, wire gauge, circuit length, and voltage to determine if voltage drop is excessive.4.

Contact LG Technical Support

Call LG's technical support and ask them to explain the reasoning behind their wire sizing requirement. Specifically, ask about the potential for voltage drop issues and the voltage sensitivity of the dryer. Get the name and employee number of the person you speak with, and document the conversation.5.

Comply with the Inspector's Decision

Whatever the local inspector dictates, you must follow. They have the authority to approve or reject the installation.

Important Considerations



Liability

As the electrician, you are responsible for ensuring the installation is safe and code-compliant. If you deviate from accepted practices (like using 8 AWG for a short run) without a solid justification (like voltage drop calculations or the inspector's approval), you could be liable if problems arise later.


Cost

8 AWG copper wire is significantly more expensive than 10 AWG.

Overkill vs. Safety

While using larger wire than
necessary isn't unsafe (it can be more difficult to work with), it's generally considered a waste of resources. However, under-sizing wire is extremely dangerous.

Permitting

Ensure you obtain the necessary electrical permits for the dryer circuit installation. The inspector will be reviewing your work during the inspection process.

In Summary:


LG's recommendation is unusual. Do not proceed without: Verifying the dryer's nameplate amperage. Consulting with your local electrical inspector first.* Potentially contacting LG's technical support.Prioritize safety and compliance with local codes above all else. Good luck! Let me know what you find out from the inspector. Flag for review