User: mannyb, Location: Florida
Asked on: Tuesday, October 28, 2025 at 9:30 am EDT
Answered on: Tuesday, October 28, 2025 at 9:30 am EDT
Question: Customer has existing 4- 4 gang meter can banks same building same side of building. Each 4 gang bank has its own service lateral. Will all the services require to have common ground? Bond for Building steel also exist does these need to.also extend into.each service disconnect. The current situation is that they cut the wiring short behind the wall and its not accesible. Just trying to determine best approach for customer.
Okay, this is a complex situation with a lot of potential implications for safety and code compliance. Let's break down the issues and potential solutions.
Key Considerations & Code References (NEC 2023 unless otherwise noted)
Multiple Buildings vs. Single Building
The crucial point is whether these meter can banks serve one building or multiple buildings. Based on your description of being in the same building and same side of building this will require a common ground.
Multiple Services for a Single Building (NEC 230.2)
Generally, a building should only have one service. However, the NEC allows for multiple services under specific conditions (NEC 230.2(A) through (D)). These include:
Capacity Requirements
Where the capacity requirements exceed the capabilities of a single service.
Different Characteristics
For different voltages, frequencies, or phases.
Special Occupancy Conditions
Where required by law or permitted by the authority having jurisdiction (AHJ).
Fire Pumps
For fire pumps.
Emergency, Legally Required Standby, or Optional Standby Systems
Where independent services are required for these systems.If your customer's situation doesn't fit one of these exceptions, you might have a fundamental problem with the legality of the existing setup. You must consult with the AHJ for a determination.
Bonding and Grounding (NEC Article 250)
This is critical for safety. The goal is to create a low-impedance path for fault current to return to the source, tripping overcurrent devices quickly and preventing dangerous voltage on conductive parts.
Service Bonding Jumper (SBJ) and Grounding Electrode Conductor (GEC) (NEC 250.24)
Each service must have a GEC connecting the grounded conductor (typically the neutral) to a grounding electrode system. This electrode system must include:
Metal Underground Water Pipe (250.52(A)(1))
If available and meets the requirements.
Metal Frame of the Building (250.52(A)(2))
If effectively grounded.
Concrete-Encased Electrode (Rebar) (250.52(A)(3))
If available and meets the requirements.
Ground Ring (250.52(A)(4))
If available and meets the requirements.
Rod, Pipe, and Plate Electrodes (250.52(A)(5), (A)(6), (A)(7))
If the above aren't available or require supplementation.
Bonding of Building Steel (250.104(A))
The metal water piping system and exposed structural metal frame of a building must be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor, or the grounding electrodes.
Common Grounding Electrode System (NEC 250.58)
This is KEY for multiple services in a single building. All grounding electrodes used must be bonded together to form a single grounding electrode system.
Addressing Your Specific Questions
"Will all the services require to have a common ground?" YES, almost certainly. If these services are serving a single building, NEC 250.58 mandates a common grounding electrode system. All individual grounding electrodes associated with each service MUST be bonded together to form a single system.
2. "Bond for Building steel also exist does these need to.also extend into.each service disconnect?" YES, The building steel must be bonded to the grounding electrode system. The language in 250.104(A) indicates this bond can be made to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor, or the grounding electrodes. It does not necessarily require a separate bond directly from each service disconnect to the building steel. However, the important thing is to ensure the steel is part of the overall grounding electrode system. If it isn't clearly bonded effectively to the GEC or grounding electrodes, it's safest to add a bonding jumper from one of the service disconnects to the steel.3. "The current situation is that they cut the wiring short behind the wall and its not accesible." This is a major problem. The GECs and bonding jumpers are essential for safety. You need to find a way to make these connections. Here's a breakdown of how to approach this
Best Approach & Recommendations:
1. Consult with the AHJ (Authority Having Jurisdiction)
This is the most important step. Explain the situation and get their guidance before doing any work. They can provide interpretations of the code and approve alternative solutions.2.
Determine the Service Arrangement
Is it a single building? Do the multiple services meet the exceptions in NEC 230.2?3.
Assess the Existing Grounding Electrode System
What electrodes are currently being used (water pipe, building steel, ground rods, etc.)? Are the existing GECs properly sized (based on the size of the service conductors – see NEC Table 250.66)? Are they in good condition and properly connected?4.
Address the Inaccessible Wiring
Access is Paramount
You must gain access to the wiring behind the wall. This might involve: Carefully cutting access holes in the wall (patching later). Using fish tape or other tools to pull new conductors through existing conduit (if applicable). Installing junction boxes to extend the existing conductors. In extreme cases, you might need to replace sections of conduit or wiring.
Extending Conductors
If you can access the existing wires, you can use approved splicing methods (e.g., listed connectors) to extend them. Ensure the splices are accessible in a junction box.5.
Establish a Common Grounding Electrode System
Bond the Grounding Electrodes
Run a bonding jumper (sized according to NEC Table 250.66) between the grounding electrodes of each service. This creates the required common grounding electrode system. Consider using exothermic welding ("Cadwelding") for a reliable, permanent connection to the electrodes.
6.
Bond the Building Steel
If the building steel isn't demonstrably bonded to the GEC or grounding electrodes, run a bonding jumper from one of the service disconnects to the steel. Size this jumper according to NEC 250.104(A) and Table 250.
66.7.
Documentation
Take detailed pictures and document everything you do. This will be helpful for future maintenance and inspections.8.
Inspection
Have the work inspected by the AHJ.
Important Safety Considerations
De-energize all circuits before working on any electrical equipment. Use proper lockout/tagout procedures. Wear appropriate PPE (personal protective equipment), including safety glasses, gloves, and insulated tools.* Work safely and carefully. Electrical work can be dangerous. If you are not qualified, hire a licensed electrician.
In summary: The most likely answer is that these will need to be bonded to a common ground system. Because this is complex and potentially dangerous, involving the AHJ and a qualified electrician is critical. Do not proceed without their guidance. Flag for review