Question: I am working on relocation of lab equipment. Below is an excerpt from an email received relative to equipment connections required for a chiller and UPS unit. Given both are fed by e-pwr on normal circumstances, I'm unsure how the UPS feeds in the chiller.Chiller #137A01 has a UPS backupUPS resides on furniture dolly to allow ease of movement out of way for servicing rear of chillerChiller needs a e-pwr NEMA L15-30R on 208V 20A breakerUPS needs a e-pwr NEMA 6-50R on 208V 50A breaker
Okay, let's break down the situation and how the UPS likely connects to the chiller, based on the information you provided.
Understanding the Setup Chiller
This is your temperature-regulating unit. It requires a dedicated 208V, 20A circuit with an L15-30R receptacle (locking, 3-phase).
UPS (Uninterruptible Power Supply)
This provides backup power in case of a power outage. It requires a 208V, 50A circuit with a 6-50R receptacle (non-locking, single-phase or three phase depending on actual config.). It's on a dolly for mobility.
"e-pwr": This likely refers to "electrical power" coming from the building's electrical system (normal grid power).
The Likely Connection Scenario (Based on Common Practices)
The most common and logical way the UPS feeds the chiller is this:1. UPS Input
The UPS is plugged into the wall outlet with the NEMA 6-50R. This is its normal power source.2.
UPS Output
The UPS has one or more output receptacles. One of these outputs will be a NEMA L15-30R. The chiller is plugged into this output receptacle on the UPS.
In other words
`Wall Power (NEMA 6-50R) --> UPS Input --> UPS Output (NEMA L15-30R) --> Chiller`
Why This Arrangement Makes Sense Uninterrupted Power
When the wall power fails, the UPS automatically switches to its internal battery and continues to supply power to the chiller through its L15-30R output.
Voltage Compatibility
The UPS steps in and provides a controlled 208V to the chiller, even during a power outage.
Mobility
Putting the UPS on a dolly allows it to be moved out of the way when you need to access the back of the chiller.
Important Considerations and Questions to Verify
UPS Output Receptacles
Crucially, confirm that the UPS actually has a NEMA L15-30R output receptacle. This is essential for the setup described above to work. Look at the back panel of the UPS.
UPS Capacity
Verify that the UPS is adequately sized to handle the chiller's power requirements (20A at 208V). Overloading the UPS could damage it or cause it to fail. Check the UPS's VA (Volt-Ampere) rating. The chiller's VA can be approximated by: `VA = Voltage Amperage sqrt(3) = 208V 20A 1.732 ≈ 7200 VA` The UPS should have a VA rating significantly higher than this, perhaps 10kVA or more.
UPS Phase Configuration
Clarify whether the UPS is single-phase or three-phase. While the input connector is a 6-50R (which could be either single or three-phase), the output connector (L15-30R) is three-phase. The UPS must be a three-phase unit to properly power the chiller.
Wiring Integrity
Ensure that all cords and receptacles are in good condition and properly rated for the voltage and amperage involved.
Grounding
Proper grounding is essential for safety. Verify that the UPS and chiller are properly grounded according to local electrical codes.
Documentation
Consult the manuals for both the chiller and the UPS for specific connection instructions and safety precautions.
Before Moving or Reconnecting Anything
Inspect
Carefully inspect the existing wiring and connections. Take photos if possible.2.
Identify
Clearly label all cords and receptacles before disconnecting anything.3.
Consult: If you are unsure about any aspect of the connections, consult with a qualified electrician. Improper electrical connections can be dangerous.By clarifying these details, you can ensure a safe and reliable connection between the chiller and the UPS. Flag for review