Topic: NEC article 215.3 Vs. 430.62

User: Ashu, Location: Hunt Valley, USA

Asked on: Tuesday, October 28, 2025 at 3:24 pm EDT
Answered on: Tuesday, October 28, 2025 at 3:24 pm EDT

Question: I have applied NEC article 430.62 to calculate the size of the Main circuit breaker as a feeder (Pleas see attached picture) then I came across article 215.3 which suggests a different calculation. Now I am little confused which one of these two codes to follow. Motors shown in the attached picture are going to be running all the times but the load may vary slightly based on the product running through the machine. I will appreciate any help clarifying this. Thank you!NEC 215.3Overcurrent Protection. Feeders shall be protectedagainst overcurrent in accordance with the provisions ofPart I of Article 240. Where a feeder supplies continuousloads or any combination of continuous and noncontinuousloads, the rating of the overcurrent device shall not be lessthan the noncontinuous load plus 125 percent of the continuousload.NEC 430.62 Rating or Setting — Motor Load.(A) Specific Load. A feeder supplying a specific fixed motorload(s) and consisting of conductor sizes based on430.24 shall be provided with a protective device having arating or setting not greater than the largest rating or settingof the branch-circuit short-circuit and ground-fault protectivedevice for any motor supplied by the feeder [based onthe maximum permitted value for the specific type of aprotective device in accordance with 430.52, or 440.22(A)for hermetic refrigerant motor-compressors], plus the sumof the full-load currents of the other motors of the group.Where the same rating or setting of the branch-circuitshort-circuit and ground-fault protective device is used ontwo or more of the branch circuits supplied by the feeder,one of the protective devices shall be considered the largestfor the above calculations.

Okay, let's break down the NEC articles you're looking at and clarify which one applies to your situation. The key here is understanding the differences between feeder calculations for general loads versus motor-specific loads.

Understanding the Articles NEC 215.3 (Overcurrent Protection for Feeders)

This article applies to
general feeders supplying a mix of loads, including continuous and non-continuous loads. Its primary purpose is to ensure the feeder is adequately protected against overcurrent due to sustained loads. The 125% calculation for continuous loads is crucial because continuous loads can cause a feeder to overheat if the overcurrent protection is sized too close to the actual load. A continuous load is defined in Article 100 as a load where the maximum current is expected to continue for 3 hours or more.

NEC 430.62 (Rating or Setting - Motor Load)

This article is specifically for feeders that supply motor loads. It takes into account the unique characteristics of motors, particularly their inrush current during starting. It allows for a higher overcurrent protection rating than might otherwise be allowed based on the continuous load, recognizing that motors draw significantly more current during startup than during normal operation.

Which Article Applies to Your Situation?


Based on your description, you should use NEC 430.62 to calculate the size of your main circuit breaker. Here's why:1. Specific, Fixed Motor Load

You explicitly state that the feeder supplies specific, fixed motor loads. This puts you squarely in the scope of Article 430.2.

Article 430 Takes Precedence

When a feeder supplies only motor loads, Article 430 takes precedence over the general feeder rules in Article 215. Article 215 is a general rule and is subject to the specific rules within Article 430.
3.


Motors Running Continuously, but Load Varying

The fact that your motors run "all the time" does not automatically make 215.3 the correct choice. Your motors are still the only load. Article 430 accounts for the motors' operation. The slight variation in load will be covered in the motor calculations.

How to Apply NEC 430.62


Here's a step-by-step breakdown of how to apply NEC 430.62:1. Determine the Branch-Circuit Overcurrent Protection for Each Motor

For each motor, determine the maximum allowed size of the branch-circuit short-circuit and ground-fault protective device (circuit breaker or fuses). This is based on NEC 430.52 and the motor's Full Load Amps (FLA) from the motor nameplate and Table 430.
250. The type of protective device (inverse time circuit breaker, fuses, etc.) will affect the allowable multiplier.
This is a crucial step.


You cannot skip determining each motor's individual branch circuit protection.
2. Identify the Largest Branch-Circuit Overcurrent Device

Of all the motor branch-circuit protective devices you calculated in Step 1, identify the largest one.3.

Sum the Full-Load Amps (FLA) of the Remaining Motors

For all the motors except the one with the largest branch-circuit protective device, add up their individual Full Load Amps (FLA) as listed on their nameplates or from NEC Table 430.250.
4.


Calculate the Feeder Overcurrent Protection

Add the value of the largest branch-circuit protective device (from Step 2) to the sum of the FLA of the other motors (from Step 3). `Feeder Overcurrent Protection Size = (Largest Branch-Circuit Device) + (Sum of FLA of Other Motors)`

Important Considerations



Feeder Conductor Sizing (430.24)

You also need to ensure your feeder conductors are sized correctly according to NEC 430.24. This requires calculating the feeder's ampacity based on 125% of the largest motor's FLA plus the sum of the FLA's of all the other motors. This will then be used to select the proper wire size.

Voltage Drop

Always check for voltage drop, especially on longer feeder runs. Excessive voltage drop can negatively impact motor performance and life.


Safety Factor

It is permissible to size the breaker larger to account for future expansion, however, NEC 430.62 states that the breaker should "not be greater than" the calculation.

Example


Let's say you have three motors: Motor 1: 20 FLA, Branch Circuit OCPD = 60A Motor 2: 10 FLA, Branch Circuit OCPD = 30A* Motor 3: 5 FLA, Branch Circuit OCPD = 15A1. Largest Branch Circuit OCPD: 60A (Motor 1)2. Sum of FLA of Other Motors: 10 FLA (Motor 2) + 5 FLA (Motor 3) = 15 FLAFeeder Overcurrent Protection: 60A + 15A = 75ATherefore, you would use a 75A circuit breaker for the feeder.

In Summary

Use NEC 430.62 for your feeder calculation. It is designed specifically for motor loads and accounts for their unique operating characteristics. Make sure you properly determine the branch circuit protection for each motor first, and remember to size your feeder conductors according to NEC 430.24 as well. Flag for review