Question: If RTU has integral fused disconnect and fed from panelboard B breaker1 then are conductors between breaker1 and fused disconnect feeders or branch circuit? I saw the definition of feeder and branch circuit NEC 2017 Article 100 but was not sure.
According to the NEC 2017 definitions in Article 100, the conductors between breaker 1 in panelboard B and the integral fused disconnect on the RTU would be considered feeders.Here's the breakdown: Branch Circuit
"The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s)." The outlet would be the RTU itself.
Feeder
"All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device."
Why Feeders?1. Overcurrent Protection
The overcurrent protection for the RTU's branch circuit is located inside the RTU's integral fused disconnect. The breaker in panelboard B is upstream of that final overcurrent device.2.
Feeding Multiple Loads (Potentially)
While this RTU might be the only load served, a feeder's function is to supply power from the source to the final overcurrent device that then feeds the load (or loads). The conductors before are called feeders.
In short, the conductors from breaker 1 to the fused disconnect are feeding the protected branch circuit within the RTU.Important Considerations
Fused Disconnect's Role
The integral fused disconnect serves as both a disconnecting means and the final overcurrent protection for the RTU's internal circuitry (e.g., the compressor motor, fan motor, controls). Without that fused disconnect, the breaker in panelboard B could be considered the final overcurrent device, and the conductors would be a branch circuit.
RTU as a Listed Assembly
RTUs are typically listed assemblies. The manufacturer determines the required overcurrent protection within the unit.
In Summary
Because the fused disconnect in the RTU contains the final overcurrent protection for the RTU's branch circuit, the conductors from the panelboard breaker to the fused disconnect are
feeders.