Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Rtu integral disconnect

User: hhsting, Location: Glen bunie, md, us

Asked on: Tuesday, October 28, 2025 at 11:10 pm EDT
Answered on: Tuesday, October 28, 2025 at 11:10 pm EDT

Question: If RTU has integral fused disconnect and fed from panelboard B breaker1 then are conductors between breaker1 and fused disconnect feeders or branch circuit? I saw the definition of feeder and branch circuit NEC 2017 Article 100 but was not sure.

According to the NEC 2017 definitions in Article 100, the conductors between breaker 1 in panelboard B and the integral fused disconnect on the RTU would be considered feeders.Here's the breakdown: Branch Circuit

"The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s)." The outlet would be the RTU itself.


Feeder

"All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device."

Why Feeders?
1. Overcurrent Protection

The overcurrent protection for the RTU's branch circuit is located inside the RTU's integral fused disconnect. The breaker in panelboard B is upstream of that final overcurrent device.2.

Feeding Multiple Loads (Potentially)

While this RTU might be the only load served, a feeder's function is to supply power from the source to the final overcurrent device that then feeds the load (or loads). The conductors before are called feeders.

In short, the conductors from breaker 1 to the fused disconnect are feeding the protected branch circuit within the RTU.
Important Considerations



Fused Disconnect's Role

The integral fused disconnect serves as
both a disconnecting means and the final overcurrent protection for the RTU's internal circuitry (e.g., the compressor motor, fan motor, controls). Without that fused disconnect, the breaker in panelboard B could be considered the final overcurrent device, and the conductors would be a branch circuit.

RTU as a Listed Assembly

RTUs are typically listed assemblies. The manufacturer determines the required overcurrent protection within the unit.

In Summary

Because the fused disconnect in the RTU contains the final overcurrent protection for the RTU's branch circuit, the conductors from the panelboard breaker to the fused disconnect are

feeders
.

Disclaimer: Consult a licensed electrical professional for specific installations as local codes may change the definition. Flag for review

Previous Question Next Question