Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Finding Resistance in Chapter 9 Table 8

User: nbabcock03, Location: Des Moines, Iowa

Asked on: Tuesday, October 28, 2025 at 11:12 pm EDT
Answered on: Tuesday, October 28, 2025 at 11:18 pm EDT

Question: When finding resistance for a problem like voltage drop, and the conductor type is unspecified, which column of Chapter 9 Table 8 is to be used when searching for ohm/kFT. I assume copper unless otherwise specified to be aluminum. I am unsure whether to use uncoated/coated and solid/stranded when the conductor is not specified in the problem.For example, when solving;What's the voltage drop of two 12 AWG conductors that supply a 10A, 120V, single-phase load located 100 ft from the power supply?With VD = I x RHow would I find the resistance of my 12 AWG conductors?

You're right to be specific about the details in finding the resistance. Here's how to approach this problem when conductor type isn't fully specified

1. Default to Copper:
Unless the problem explicitly states the conductor is aluminum, always assume it's copper. Copper is the most common conductor in most electrical installations.2. Coated vs. Uncoated



Always assume coated
. Almost all modern building wire is coated with insulation. The uncoated values are for bare conductors.3. Solid vs. Stranded



Assume
stranded
for general wiring applications. While solid wire can be used, stranded wire is much more common, especially for anything other than short runs and specific applications (like inside some luminaires). Stranded wire is easier to pull and bend, especially in larger sizes.

Therefore, in your example, you would look at the values for
Coated Stranded Copper in Chapter 9, Table 8 of the NEC.Solving the Voltage Drop Problem


Resistance

Look up the resistance of 12 AWG coated stranded copper in Chapter 9, Table 8 of the NEC. You'll find a value in ohms per 1000 feet (Ω/kft). The exact value may depend on the temperature rating of the insulation (e.g., 60°C, 75°C, or 90°C), but for this type of problem, using the 75°C column is usually a safe bet, unless the problem gives you a specific temperature rating. Let's assume you find a value of

1.98 ohms/kft
.2. Adjust for Length

You have 100 feet of wire, but the table gives resistance per 1000 feet. So, divide the table value by 10:
1.98 Ω/kft / 10 = 0.198 Ω/100ft3.

Account for Two Conductors

The 100ft represents the distance to the load. However, the current has to travel to the load and back. This means you have 200 feet of conductor in the circuit. Since we have already calculated the ohms per 100ft, we multiply our answer by 2. 0. 198 Ω/100ft x 2 = 0.396Ω4.

Calculate Voltage Drop

Use Ohm's Law (VD = I x R):
VD = 10 amps 0.396 ohms VD = 3.96 volts

Answer

The voltage drop would be 3.96 volts.

Important Considerations



NEC (National Electrical Code)

Always refer to the most recent edition of the NEC. Values in tables can change between editions.


Temperature Correction

In precise calculations, you might need to adjust the resistance based on the operating temperature of the conductor. The NEC has tables and formulas for this. For a simple voltage drop calculation, it's usually not critical.

Reactance

For longer runs, especially at higher currents, you
might need to consider the reactance of the conductors. However, for a relatively short run of 100 feet, it is usually negligible.

Problem Specifics

Always pay close attention to the wording of the problem. If it provides any clues about the conductor type, use that information.

Safety:
This is just a calculation. In a real-world electrical installation, voltage drop is just one* factor to consider. You also need to ensure proper wire sizing for ampacity (current-carrying capacity) and overcurrent protection. Always consult a qualified electrician for any electrical work. Flag for review

Previous Question Next Question