Question: Let me start with, the manufacturers instruction arent clear!So we have a newly installed air handler with a total of 15kW of electric heat strips in it. They are factory split 2 stages, with stage 1 is 10kW, and stage 2 is 5kW. Onstage 1 is the control transformer, and the blower of about 3 amps.The unit came with 2 circuit breakers ( yes I checked they truly are breakers not just disconnects. Stage 1 is a 60, and stage 2 is the same. MOCP is 60 for stage 1, and 25 for stage 2. Obviously without swapping the stage 2 breaker I cannot use the "tap rule" to feed both stages from a 125 amp feeder. the main breaker panel is in the same room as the air handler and within sight. Anyone have a problem with removing the existing #1 THW conductors, and replacing them with 2 #6 (on the 60), and 2 #10 (on the 25) with the breakers in the main panel, and the air handler labeled to indicate that there are multiple branch circuits feeding it and which circuits they are?Howard
Okay, Howard, let's break this down to ensure a safe and code-compliant installation. Your frustration with unclear instructions is understandable; HVAC electrical can be tricky.
Understanding the Situation Air Handler
15kW total electric heat, split into two stages (10kW and 5kW).
Existing Wiring
Two separate circuits with dedicated breakers at the air handler: Stage 1 (10kW): 60A breaker, likely using larger conductors than necessary (your #1 THW) Stage 2 (5kW): 25A breaker, also likely using larger conductors than necessary (your #1 THW)
Proposed Change
Remove existing conductors and run two new circuits from the main panel to the air handler. Stage 1 (10kW): #6 AWG conductors, 60A breaker in the main panel. Stage 2 (5kW): #10 AWG conductors, 25A breaker in the main panel.
Main Panel Location
Same room and within sight of the air handler.
NEC Considerations & Concerns1. Nameplate MOCP
You've correctly identified the MOCP (Maximum Overcurrent Protection) for each stage. These values MUST be adhered to.2.
Multiple Branch Circuits
This is the core of your question. Section 424.22(C) of the NEC permits multiple branch circuits to supply a single fixed electric space-heating appliance like your air handler under specific conditions. You are on the right track by identifying that you will need to follow those specific conditions.
424.22 Overcurrent Protection. Electric space-heating equipment, other than such motor-operated equipment as required by Parts VII, VIII, and IX of Article 430, shall be protected as provided in (A) and (B). (C) Electric Space-Heating Appliances Using Two or More Branch Circuits. Electric space-heating appliances using two or more branch circuits shall be protected as specified in (1) and (2). (1) Individual Branch Circuits. Each circuit shall be protected individually by overcurrent devices rated or set at not more than the ampacity of the circuit conductors. (2) Marking Required. Space-heating appliances employing two or more branch circuits shall be legibly marked to indicate (a) the amount of current to be permitted to be employed by each circuit and (b) the number of branch circuits required.3.
Conductor Ampacity
Ensure your proposed conductor sizes (#6 and #10) are adequate for the load and the overcurrent protection you're using, considering ampacity derating for ambient temperature and conductor bundling (if applicable).
#6 AWG THHN/THWN
Typically rated for 55 amps at 75°C. With a 60A breaker, this is technically not compliant, but it is very close. Consider a conductor with a higher rating that would comply with 60 amps. For example #6 AWG THHN/THWN-2 or #6 AWG XHHW-2.
#10 AWG THHN/THWN
Typically rated for 30 amps at 75°C. This is fine for a 25A breaker.4.
Termination Ratings
Verify that the breakers and the air handler's connection points are rated for the size and type of conductors you plan to use. Many breakers and devices are only rated for a limited range of conductor sizes.5.
Grounding
Ensure proper grounding of the air handler and the branch circuits. Usually, this means a separate grounding conductor (equipment grounding conductor, EGC) run with each circuit.6.
Disconnecting Means
Even with the breakers in sight, you'll likely still need a disconnecting means at or within sight of the air handler for servicing. Your existing breakers at the air handler appear to meet this requirement, but it is crucial to be sure of it.
Steps to Take1.
Load Calculation
Double-check your load calculations for each stage (10kW and 5kW) at the supply voltage to determine the actual current draw. `Amps = Watts / Volts` (Remember to use line-to-line voltage for a 240V system, not 120V).2.
Conductor Selection
Choose the appropriate conductor size based on the calculated load, ampacity ratings, derating factors, and termination ratings. As noted above, #6 THHN may be cutting it close with a 60A breaker; upgrading to #6 THHN-2 or XHHW-2 is probably the right call.3.
Overcurrent Protection
The breakers in your main panel MUST match the MOCP ratings for each stage (60A and 25A, respectively).4.
Labeling
This is absolutely critical. The air handler MUST be clearly and permanently labeled to indicate that it is supplied by multiple branch circuits, stating the required current and number of branch circuits. An example label would be:
"CAUTION: This equipment is supplied by TWO branch circuits.CIRCUIT 1: 60 Amps Max.
CIRCUIT 2: 25 Amps Max."5.
Wiring Method
Use an approved wiring method (e.g., conduit, cable) from the main panel to the air handler. Secure and support the conductors properly.6.
Professional Inspection
Highly recommended. Electrical work, especially involving heating equipment, is best done or at least reviewed by a qualified electrician. They can ensure that your installation meets all applicable codes and safety standards.
Addressing Your Specific ProposalYour proposal is generally sound, assuming the conductors and terminations are properly sized and rated, and the labeling is clear. However, I have one concern: #6 AWG and 60A Breaker
As mentioned above, I'd suggest confirming the rating for #6 AWG THHN you intend to install is above 60 amps and can be terminated. It would be better to size up to #6 AWG THHN-2 or XHHW-2.
In summary, yes, what you're proposing is likely acceptable under the NEC as long as you strictly adhere to the MOCP ratings, use appropriately sized conductors, provide clear labeling, and follow all other applicable code requirements.* Get an electrician involved to confirm your work and verify local code interpretations. This will give you peace of mind and ensure a safe and compliant installation. Flag for review