User: Ken_S, Location: NJ
Asked on: Wednesday, October 29, 2025 at 8:39 am EDT
Answered on: Wednesday, October 29, 2025 at 8:39 am EDT
Question: Given - Remote ground mounted array, micro inverters, disconnect and combiner panel at the array. Is a disconnect required to be installed at the house where the feeder conductors enter? I believe 225.31 would require a disconnect, however I'm questioning if it's needed. The feeder conductors would enter the rear of the home and be run to the front of the home to an exterior disconnect connected to the line side of the service.2020 NEC
You're on the right track. Let's break down the NEC requirements and considerations for your situation
Yes, a disconnect is generally required at the house where the feeder conductors enter.
Your assessment of 225.31 is the key.
Why 225.31 Applies 225.31 Disconnecting Means. "Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or other structure." In your scenario, the conductors from the remote array are supplying a building (the house).
Why the Array Disconnect Doesn't Change the Requirement at the House
Having a disconnect at the array doesn't negate the need for a disconnect at the building. The NEC requires a disconnecting means to disconnect the entire supply at the building.
Important Considerations & Code Sections to Review 225.32 Location. This section requires the disconnecting means to be at a "readily accessible location" either outside the building or nearest the point of entrance of the conductors. Your proposed location at the front of the house might be acceptable if it meets the "readily accessible" requirement. Readily Accessible. Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to actions such as to use tools, to climb over or remove obstacles, or to resort to portable ladders, and so forth. 690.13(E) & (F) - PV System Disconnect(s). These sections specify additional requirements regarding PV system disconnects, including the need for a directory and proper labeling. While you have a disconnect at the array, these sections emphasize the importance of having a means to safely isolate the PV system. 690.15 - Disconnecting Means for Ground-Mounted PV Arrays. This addresses the disconnect at the array specifically. 225.36 Suitable for Service Equipment. The disconnecting means you install at the house must be suitable for use as service equipment.
Your Specific Scenario Running the conductors from the rear of the house to the front for the disconnect. This can be compliant, provided: The disconnect at the front of the house is readily accessible. The disconnecting means is marked with a permanent sign indicating the location of the service disconnecting means for the premises.* You comply with all other applicable code requirements for the wiring method and protection of the conductors.
In Summary
Yes, a disconnect is generally required at the house in your scenario. Your proposed location at the front of the house could be acceptable if it's readily accessible, suitable for service equipment, and properly labeled. Ensure you comply with all applicable requirements of 225.31, 225.32, 690.13, 690.15, and any other relevant sections of the 2020 NEC. Always consult with your local AHJ for specific interpretations and requirements. Flag for review