Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Short Circuit Current

User: Zyb, Location: Maine

Asked on: Wednesday, October 29, 2025 at 12:52 pm EDT
Answered on: Wednesday, October 29, 2025 at 12:52 pm EDT

Question: Do I need a fusible switch, if a typical non fusible is only 10kAIC. 39kA and 18kA are available fault currents?

Yes, you likely need a fusible switch if your available fault currents exceed the AIC (Ampere Interrupting Capacity) rating of your non-fusible switch. Let's break down why: AIC (Ampere Interrupting Capacity)

This is the maximum fault current a switch can safely interrupt without failing catastrophically (e.g., exploding, melting, welding closed).


Available Fault Current

This is the magnitude of fault current that could flow at a particular point in the electrical system during a short circuit or ground fault. It depends on the utility supply, transformer size, conductor impedance, and other factors.

In your scenario

Your non-fusible switch is rated for 10kAIC. You have available fault currents of 39kA and 18kA.

The Problem

Both 39kA and 18kA are significantly higher than the 10kAIC rating of your non-fusible switch. If a fault occurs and the current exceeds 10kA, the switch is likely to fail, potentially causing:

Equipment Damage

Extensive damage to the switch itself and surrounding equipment.


Fire Hazard

The failure could create arcs and sparks, igniting nearby materials.

Personnel Injury

Arc flash and explosions can cause serious burns and other injuries.

Why a Fusible Switch is Needed

A fusible switch combines a switch mechanism with fuses. The fuses are designed to:


Interrupt High Fault Currents

Fuses have very high AIC ratings, often 200kA or more. They are designed to quickly interrupt fault currents before they can damage the switch or other equipment.

Provide Overcurrent Protection

Fuses also protect against overloads.

What to do


Confirm Available Fault Current

Verify the 39kA and 18kA values through a proper fault current study. These calculations are crucial.2.

Select a Fusible Switch with Adequate AIC

Choose a fusible switch where the fuses' AIC rating
exceeds the highest available fault current. In your case, it must be higher than 39kA. Standard fusible switches are rated for 200kAIC, which will meet your need.3.

Proper Fuse Selection

Select fuses with appropriate amp ratings to protect the connected circuit and equipment from overload and short circuit conditions.4.

Installation and Maintenance

Ensure the fusible switch is properly installed and maintained according to manufacturer's instructions and applicable electrical codes (NEC in the US).

Important Considerations



Coordination

Ensure proper selective coordination between fuses, other overcurrent protective devices to minimize nuisance tripping.

NEC (National Electrical Code)

The NEC requires that equipment be rated to interrupt the available fault current. Violating this is a serious safety hazard and code violation.


Qualified Personnel

Always consult with a qualified electrician or electrical engineer for fault current studies, equipment selection, and installation. Dealing with high fault currents is dangerous and requires expertise.

In short, if your available fault current exceeds the AIC rating of your switch, you need to use a fusible switch with appropriately rated fuses to ensure safety and code compliance.
Flag for review

Previous Question Next Question