User: kjroller, Location: Dawson Mn
Asked on: Wednesday, October 29, 2025 at 4:55 pm EDT
Answered on: Wednesday, October 29, 2025 at 4:55 pm EDT
Question: Does a Sub Panel have to follow Article 230.79? Or can you configure it however you want? I ask because I am wondering if since it is a panel if it is considered a service and since it would have 6 breakers if it would have to follow 230.79(D) for amperage.
No, a subpanel does not have to follow Article 230.79. Article 230 is for Services. A subpanel is part of a feeder or branch circuit, not a service.Here's a breakdown of why and what rules do apply: Service vs. Feeder
Service
The electrical supply from the utility company to the building. Article 230 deals with the requirements for this service entrance.
Feeder
Conductors from the service equipment to a subpanel or a branch circuit overcurrent device. A subpanel is fed by a feeder.
Article 230.79 Relevance
This article specifically deals with the minimum ampere rating of service disconnects. Since a subpanel is NOT a service disconnect, this article does not apply.
Subpanel Requirements (What does apply)
Feeder Size
The feeder conductors supplying the subpanel must be sized according to Article 215 (Feeders) to carry the calculated load of the subpanel. The overcurrent protection at the origin of the feeder (at the main panel) must protect these feeder conductors.
Overcurrent Protection
The subpanel itself needs overcurrent protection. This is usually the main breaker in the subpanel (if it has one) or the overcurrent device at the main panel feeding the subpanel. The overcurrent protection at the origin of the feeder must protect the subpanel's busbar rating.
Grounding and Bonding
Very important! The subpanel must have a separate equipment grounding conductor (EGC) run with the feeder conductors from the main panel. The neutral (grounded conductor) must be isolated in the subpanel. Do not bond the neutral to the enclosure in a subpanel. This avoids parallel neutral paths. Use a 4-wire feeder (two hots, neutral, and ground).
Panel Rating
The subpanel's busbar rating must be at least equal to the calculated load it will serve or the overcurrent protection it is feed with.
Working Space
You must provide adequate working space around the subpanel as required by Article 110.26.
Number of Circuits
While 230.79(D) might say that you can't have more than 6 hand movements, that is specifically for services. For a subpanel there is no limit to the number of circuits you can have.
In Summary
You design and install a subpanel based on:1.
Load Calculations
Determine the total load the subpanel will serve.2.
Feeder Sizing
Size the feeder conductors to carry that load.3.
Overcurrent Protection
Provide overcurrent protection for the feeder conductors.4.
Grounding/Bonding
Ensure proper grounding and bonding, with a separate EGC.5.
Panel Rating
The subpanel itself must be rated to handle the load.6.
Working Space: Adequate working space is required.Always consult the current edition of the National Electrical Code (NEC) and local codes for the most accurate and up-to-date requirements. When in doubt, consult a qualified electrician. Flag for review