Question: What is the biggest hole i can a 2x4 stud for wire ? (2017 nec) ?????????????????????????????????????????????????????????????????????????????????????????????????????
According to the 2017 NEC (National Electrical Code), Section 300.4(A)(1) addresses this. Here's the gist: Holes in wood framing members (like 2x4 studs) for cables or raceways must be drilled so that the edge of the hole is not less than 1 1/4 inches from the nearest edge of the wood member. This means, in a standard 2x4 stud, you can drill a hole up to a maximum diameter of 1 3/4" (One and Three Quarters Inches).The 1 1/4" rule is important for safety and to avoid weakening the stud.It's always a good idea to consult with a qualified electrician or local building inspector to ensure your wiring is done safely and in accordance with all applicable codes. Flag for review