User: Alwayslearningelec, Location: NJ
Asked on: Thursday, October 30, 2025 at 7:42 am EDT
Answered on: Thursday, October 30, 2025 at 7:42 am EDT
Question: Questions about feeding these receptacles. Yellow highlights on column drawing are receptacle just for visual. These are existing columns with new furred out gyp board walls. The ceiling are exposed slab. We can use MC cable in wall but must use EMT on ceiling.The way I see it we can use mc cable in the walls but I will not be able to get around the column as it is concrete. So I am thinking I will need to drop down from ceiling with EMT and hit receptacle then run MC in between columns. Is my non electrician thinking correct? Thanks.
Okay, let's break down the receptacle feeding options given your situation
Understanding the Constraints:
Existing Concrete Columns
This is the biggest hurdle. You cannot easily run conduit (or MC) through concrete columns. You're essentially limited to going around them.
MC Cable Allowed in Walls
Great! This will be your workhorse for the horizontal runs within the furred-out wall space.
EMT Required on Ceiling
This means you must use EMT conduit for any runs exposed on the ceiling. This is common for aesthetic or protection reasons in exposed slab ceilings.
Your Proposed Solution (EMT Drop from Ceiling, MC Between Columns)
Yes, your thinking is generally correct and a common way to handle this scenario.Here's a more detailed breakdown and some considerations
EMT Drop from Ceiling
This is a standard and acceptable method. You'll run EMT from your junction box/panel on the ceiling down the column to a point just above the receptacle boxes.
Important
You'll need appropriate EMT connectors to transition from the EMT to the receptacle boxes. A common fitting is a set-screw connector on the end of the EMT into a standard metal box connector screwed into the knockout of the receptacle box. You will need to use straps to support the EMT.2.
MC Cable Between Columns
Once you're down the column with EMT, you can transition to MC cable within the wall cavity between the columns.
Important
Use proper MC cable connectors at both ends of the MC cable runs (where it connects to the receptacle boxes). These connectors clamp the MC cable securely and provide grounding. Secure the MC Cable: MC cable must be properly secured within the wall cavity. Use MC cable staples or straps to keep it in place and prevent it from being stressed.3.
Grounding
Critical
Ensure proper grounding throughout the system. The metal boxes will need to be grounded, usually through the ground wire in the MC cable and the bonding of the EMT conduit run. Check your local codes for specific grounding requirements.4.
Junction Boxes (if needed)
If the length of the run between the EMT drop and the last receptacle is too long for a single MC cable run (or if it's just more convenient), you can install a junction box (within the wall cavity) between columns. This allows you to splice the MC cable and extend the run. The junction box must be accessible (meaning you can't bury it behind the finished wall without an access panel).5.
Box Fill
Make sure that you are not exceeding box fill for the receptacle boxes and any junction boxes.6.
Height and Accessibility Ensure that the receptacle outlets are at the height required. Confirm that you are not blocking or covering any required access panels.7. EMT and MC Connections at the Receptacle Box
Ensure you have enough "slack" (extra wire length) in the boxes to make connections to the receptacles easily. Code usually requires a certain amount of free conductor length in each box. The connectors used to transition from EMT or MC into the boxes need to be suitable for the purpose and provide a secure mechanical and electrical connection.
Diagram (Simplified)Ceiling (Slab)
Within Wall Cavity| MC CableReceptacle Box------------------------------------------------------ Receptacle BoxEMT Conduit|EMT Connector to Box|Concrete Column ----------------------------------------------------- Concrete Column
Important Considerations Before Starting Work
Local Codes
Always verify your local electrical codes and ordinances. They may have specific requirements that differ from the general advice given here.
Permits
Check if you need an electrical permit for this work.
Professional Electrician (Highly Recommended): If you are not a qualified and licensed electrician, it is strongly recommended that you hire one to do this work. Electricity is dangerous, and improper wiring can create fire hazards or shock hazards. This is especially true when dealing with existing building infrastructure.In summary, your basic plan is sound. Just pay close attention to code compliance, grounding, proper connector usage, and wire management. Good luck! Flag for review