Question: We have disconnect switch after Service meter of 480 V service. Is additional disconnect is required before service meter? as per NEC230.71(C)
NEC 230.71(C) addresses the number of disconnects permitted for each service. It's important to understand its context and how it relates to your specific situation.Here's a breakdown of NEC 230.71(C) and how it applies to your situation: NEC 230.71(C): Maximum Number of Disconnects. This section states that the service disconnecting means for each service permitted by 230.2 shall consist of not more than six switches or six sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, or in a group of separate enclosures.Now, let's address your question: Scenario
You have a disconnect switch after the service meter. You're asking if you need an additional disconnect before the service meter.
Analysis
Your disconnect after the meter is your service disconnect. The utility owns the meter. The wiring and equipment before the meter are typically under the exclusive control of the utility company, not the building owner or electrician. They are responsible for overcurrent protection up to the meter. NEC typically doesn't apply to the utility's side. The NEC primarily governs the electrical installations on the customer's side of the service point (which is often the meter, but not always). The utility may or may not have a disconnect before the meter. This is their decision, based on their standards and practices. You generally don't get to install one. Article 230.71(C) applies to the customer's service disconnects. The rule about a maximum of six disconnects applies to the service disconnecting means provided for your service. Since you already have one disconnect (after the meter), and it's serving as the main service disconnect for your building or portion of a building, you likely don't need another.
Therefore, generally speaking, you do NOT need an additional disconnect switch before the service meter. The utility will have their own equipment to disconnect the service.
Important Considerations and Caveats
Local Utility Requirements
Always check with your local utility company. They may have specific requirements for service disconnects, even before the meter. These requirements often supersede the NEC in the utility's domain. They may even require a visible, lockable disconnect on the customer side ahead of the meter.
Specific Circumstances
There might be unusual situations where an additional disconnect is necessary, based on the specific design of the electrical system, local amendments to the NEC, or the requirements of the Authority Having Jurisdiction (AHJ). For example, a large multi-tenant building could have multiple services, each requiring its own disconnecting means.
AHJ
Always consult with your local electrical inspector (AHJ) to ensure your installation complies with all applicable codes and regulations.
Emergency Disconnects
If the disconnect after the meter serves as an emergency disconnect, it must comply with the additional requirements for emergency disconnects.*
Working Space
Sufficient working space is required per NEC 110.26 for all electrical equipment.
In summary, the utility is generally responsible for the equipment before the meter, and you don't need an additional disconnect before the meter unless the utility or AHJ specifically requires it. Always consult with the utility and the AHJ to confirm. Flag for review