Topic: SqD I-Line Meter CT connections

User: solarken, Location: Hudson, OH, USA

Asked on: Thursday, October 30, 2025 at 5:00 pm EDT
Answered on: Thursday, October 30, 2025 at 5:00 pm EDT

Question: Is anyone familiar with this PM5563 power meter and Smart Cell surge protector combination? I have a customer where the CTs secondary leads look to have their polarity reversed and need to correct it. It was installed by a different electrical contractor, and I am configuring the meter and integrating it with their BAS. I It is not clear to me if I can remove the meter or a cover on the unit while the SPD is installed into the panelboard bus, to get access to the CT lead terminals. There are 800A:5A CT's installed in the i-line and the orientation of those on the service conductors looks correct, and I cannot get to them to flip the CT orientation either. Getting negative power readings on this thing and I think the CT lead polarity is reversed. Do I need to remove the whole unit?

You're dealing with a common (and frustrating) issue: reversed CT polarity leading to negative power readings. Let's break down your situation with the PM5563/Smart Cell combo and how to address the CT polarity.

Understanding the PM5563 and Smart Cell Combination PM5563 Power Meter

This meter measures voltage and current to calculate various power parameters (kW, kVAR, kVA, power factor, etc.). It relies on the CTs to accurately measure current flow.


Smart Cell Surge Protector

The SPD protects the panel and connected equipment from voltage surges. It's designed to be installed directly on the bus bars of the panelboard.

Integrated Unit

The key point is whether these are
truly integrated or simply physically close in the panel. If they are integrated, accessing the meter's wiring might be complicated by the SPD's bus connection. If they are not integrated, the meter is likely installed and wired as any other meter is.

Troubleshooting Steps and Considerations
1. Confirm the Reversed Polarity

Before physically touching anything, double-check that reversed CT polarity is definitively the cause of the negative power readings. Here are some things to consider:

Check All Phases

Verify that
all phases are showing negative power. If only one phase is negative, the issue is almost certainly a reversed CT on that phase. If all phases are negative, there could be a system-wide wiring issue or configuration error.

Load Test

Apply a known, substantial load (e.g., turning on a large motor or heating element). If the power readings become more negative, that strongly suggests reversed CT polarity.

Configuration Check

Access the PM5563's configuration software (using whatever communication method it supports – likely Modbus TCP or RTU). Ensure the CT ratio is correct (800:5 in your case). Also, check if there's a setting for CT polarity that might have been accidentally inverted. Some meters have a software-based polarity reversal option. Look for an option to reverse the CT or the phase polarity.


Current Direction

If possible, use a clamp-on ammeter to verify the direction of current flow on the conductors. Current should be flowing "into" the load and "out" from the source. You can then compare that to the CT orientation.2.

Safety First!
De-energize

This is the most important step!

Completely de-energize the panelboard before attempting to access any wiring.
Lockout/Tagout procedures are mandatory. This means disconnecting the power source at the upstream breaker/disconnect and verifying the panel is de-energized with a reliable voltage tester.
Never work on energized equipment unless absolutely necessary, and then only with proper training and PPE. Qualified Electrician

If you are not a qualified electrician comfortable working inside a live panel (after verifying it is de-energized) and understanding the risks, do not proceed. Call a qualified professional.

Read the Manuals

Locate the installation manuals for both the PM5563 and the Smart Cell. These manuals will provide specific safety instructions and wiring diagrams.
Especially consult the manuals for installation and maintenance procedures, as these documents will describe how to disassemble parts without damaging the units.3.

Accessing the CT Terminals



Visual Inspection

Carefully examine the PM5563 and Smart Cell combination. Look for any removable panels, access covers, or terminal blocks that might allow you to reach the CT wiring.

Identify Terminal Blocks

Trace the CT wires from the CTs themselves to the terminals on the PM5563. These terminals will likely be screw terminals or spring clamp terminals.


Smart Cell Obstruction

This is the tricky part. If the Smart Cell's physical connection to the bus bars is blocking access to the meter's CT terminals, you might need to temporarily remove the Smart Cell. However, proceed with extreme caution! Removing the Smart Cell requires carefully disconnecting it from the bus bars. Do not force anything. Take clear pictures of the unit and the bus before disassembly to ensure that you can put it back together properly.

Integrated Unit

If they are truly integrated, then the disassembly may involve removing the meter with the SPD, or removing panels on the meter to expose the CT terminals.4.

Correcting the CT Polarity



Reversing CT Leads

Once you have access to the CT terminals on the PM5563, swap the two leads for the affected phase(s). The leads are often labelled S1 and S2, or H1 and H2, and are sometimes represented by a dot and a line. Swap the wire on the dot with the wire on the line.

CT Orientation

If you can access the CTs themselves (which you said you can't, but double-check), reversing the CT's physical orientation on the conductor is another way to correct the polarity.5.

Testing and Verification



De-energize

Reconnect the power to the panel.

Monitor Readings

Observe the power readings on the PM5563. The power readings should now be positive and consistent with the load.


Load Test

Repeat the load test from step 1 to ensure the readings are accurate under varying load conditions.

Important Considerations



Warranty

Check the warranty status of both the PM5563 and the Smart Cell. Disassembling the unit might void the warranty.


Documentation

Keep detailed records of everything you do, including photos of the wiring before and after making changes.

Do you need to remove the whole unit?


Probably not, but possibly. Ideally, you should be able to access the CT terminals on the PM5563 without completely removing the Smart Cell or the entire assembly. But it depends on the physical design and how tightly integrated they are. First try to find a way to remove access panels on the PM5563 only The last resort is to remove the whole unit.Recommendations


Get the Manuals

This is your top priority.2.

Photograph Everything

Before you touch anything, take detailed photos of the entire installation, including the wiring, terminal blocks, and any labels.3.

Proceed Methodically

Follow the steps outlined above, and don't hesitate to stop and consult with a qualified electrician if you are unsure about anything.4.

Double-Check Everything:
Before re-energizing the panel, carefully double-check all wiring connections to ensure they are secure and correct.By following these steps and prioritizing safety, you should be able to resolve the reversed CT polarity and get the PM5563 reading accurate power values. Good luck! Flag for review