User: JayBuud, Location: Minnesota
Asked on: Thursday, October 30, 2025 at 7:59 pm EDT
Answered on: Thursday, October 30, 2025 at 8:14 pm EDT
Question: I need to pull six 10AWG circuits from my panelboard up to a 24x24 in one pipe and all circuits require an iso ground. Does each circuit need its own dedicated iso or can I get away with pulling only one and splicing off it in that 24x24 and would I have to upsize it? Can’t seem to find it in the code.
Okay, let's break down the NEC requirements and best practices for isolated grounding conductors, especially in your situation with multiple circuits in a single conduit.
Understanding Isolated Grounds (IGs) Purpose
Isolated grounds are used to minimize electrical noise and interference on sensitive equipment. They provide a dedicated grounding path back to the service equipment (main panel) that is electrically isolated from the regular equipment grounding conductor (EGC) system.
Key Difference
The key difference is that the isolated ground conductor is not connected to the metal conduit, junction boxes, or other metallic enclosures along its path. It's only connected at the service equipment (where the neutral and ground are bonded) and at the equipment being served.
Your Situation: Six 10 AWG Circuits with IGs in One Conduit
Here's the breakdown of the code and best practices:1. Individual Isolated Ground Conductors are generally required
The NEC (National Electrical Code) generally requires a separate isolated ground conductor for each circuit that requires an isolated ground. While there isn't a specific section that explicitly prohibits splicing IG conductors, it is against best practices for minimizing noise and interference, which is the entire purpose of the IG.
Reasoning
The idea behind an isolated ground is to create a dedicated, low-noise grounding path. Splicing IG conductors together compromises this isolation, as any noise on one circuit's ground can then be coupled onto the other circuits sharing the spliced IG.2.
NEC 250.146(D) Receptacles, Equipment, and Enclosures:This section covers requirements when using isolated ground receptacles, but it highlights the overall intent: "Where installed for the reduction of electrical noise (electromagnetic interference) on the grounding circuit, an insulated equipment grounding conductor shall be installed from the branch-circuit panelboard to the grounding terminal of the receptacle or equipment. This equipment grounding conductor shall be identified as an insulated equipment grounding conductor." Important Implication
This strongly implies a dedicated conductor for each receptacle/circuit requiring isolation.3.
Why Not Splicing? Compromised Isolation
Splicing the isolated ground conductors within the 24x24 box defeats the purpose of having isolated grounds. Any noise or interference on one circuit's ground will be coupled onto the other circuits sharing the spliced ground.
Increased Impedance
Splicing can introduce additional impedance (resistance to AC current) in the grounding path, potentially reducing the effectiveness of the isolated ground.
Potential for Ground Loops
Splicing, especially if not done perfectly, can create ground loops, which can introduce even more noise and interference.4.
Conduit Fill
You'll need to calculate the conduit fill to ensure you're not exceeding the maximum allowable fill percentage. With six 10 AWG conductors plus six 10 AWG isolated ground conductors, you will also need to include the 10 AWG EGC that is required to be pulled with the circuit. You'll also need to include the conductors for your neutrals. This will add up to 19 conductors so you will need to run your calculations to see what size conduit will be required. Use Chapter 9, Table 1 and Table 4 for your calculations.
Conclusion
To adhere to best practices and maintain the integrity of the isolated grounding system, you should run a separate 10 AWG insulated isolated ground conductor for each* of the six circuits from the panelboard to the 24x24 box, and then to each piece of equipment served. You cannot splice them together. Flag for review